Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Installing AP9512THBLK
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2810:34 PM. Last Modified: 2024-03-1404:21 AM
Installing AP9512THBLK
All
I have bought 2x AP9512THBLK sensors to replace the temperature only ones which came with out AP9619 Network Management Cards.
I assume i can just remove the old ones and plug the new ones in. This wont cause an auto shutdown of our servers as its lost communication will it? Is there anything else i need to be aware of for this?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2810:34 PM. Last Modified: 2024-03-1404:21 AM
Welcome to the APC Forum Robin.
Unplugging and removing environmental probes on the network management card should not cause any auto/unexpected shutdown. But to be more safe just in case there is a brief or false signal cause by the pins being loosened and replugged make sure that there are no PowerChute Network Shutdown settings set for anything environmental.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2810:34 PM. Last Modified: 2024-03-1404:21 AM
Welcome to the APC Forum Robin.
Unplugging and removing environmental probes on the network management card should not cause any auto/unexpected shutdown. But to be more safe just in case there is a brief or false signal cause by the pins being loosened and replugged make sure that there are no PowerChute Network Shutdown settings set for anything environmental.
Hope this helps.