Wondering if someone can explain how a slightly higher rated UPS model has a lower run time capability vs. a lower rated model. Tried asking a couple of my peers but none of them seemed to know.
[APC Smart-UPS - SUA5000R5TXFMR|http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SUA5000R5TXFMR]
4000 Watts / 5000 VA
Battery VAh Capacity: 816
[APC Smart-UPS RT - SURT6KRMXL3U-TF5|http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SURT6KRMXL3U%2DTF5]
4200 Watts / 6000 VA
Battery VAh Capacity: 960
Say we use 1kW/1.4kVA as an example. According to the run-time charts:
SUA5000R5TXFMR - 1hr 3min
SURT6KRMXL3U-TF5 - 39min
Pretty big difference of ~62%. If I recall, online UPS units are usually less efficient but a difference of ~62%!? Seems like something's off to me. Guessing the answer probably is something obvious but can't seem to figure it out here. ๐
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2021-06-28 10:33 PM . Last Modified: โ2024-03-14 04:22 AM
The SUA5000R5TXFMR has a larger battery. If you look in the manual for the UPS it has 108lbs of batteries (4 batts 27lbs each). The SURT6KRMXL3U-TF5 has a 74lb battery(both batt packs =74lbs). So in terms of back up time with UPS lead = run time. The SUA 5000 has more lead paired with a slightly lower amount of output power and you get your large diffrence in stated run time.
Hope this answers your question.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2021-06-28 10:33 PM . Last Modified: โ2024-03-14 04:22 AM
The SUA5000R5TXFMR has a larger battery. If you look in the manual for the UPS it has 108lbs of batteries (4 batts 27lbs each). The SURT6KRMXL3U-TF5 has a 74lb battery(both batt packs =74lbs). So in terms of back up time with UPS lead = run time. The SUA 5000 has more lead paired with a slightly lower amount of output power and you get your large diffrence in stated run time.
Hope this answers your question.