Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
Options
  • Mark all as New
  • Mark all as Read
  • Float this item to the top
  • Subscribe
  • Bookmark
  • Invite a Friend
  • Threaded format
  • Linear Format
  • Sort by Topic Start Date
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Labels
Top Labels
  • Alphabetical
  • Smart-UPS & Symmetra LX | RM 4,611
  • UPS Management Devices & PowerChute Software 2,913
  • Racks, Rack Accessories, & Cooling 955
  • Data Center & Facility 3 Phase UPS 605
  • General Questions & Suggestions 240
  • Getting Started 166
  • Datacenter UPS 131
  • Server Room & Data Center Design Best Practices 106
  • Smart-UPS & Symmetra LX-RM 97
  • Other Environmental Monitoring Products & Questions 48
  • Business Power UPS 36
  • Datacenter Racks & Cooling 28
  • Rack Accessories & Cooling 16
  • Business Power Software & NMC 15
  • Home & Office - UPS & Software 15
  • Datacenter Accessories 15
  • Datacenter Netbotz & Monitoring 9
  • Network Management Card 6
  • Data Center Expert 6
  • Racks 6
  • power monitoring expert 5
  • IT Expert 5
  • Data Center Operation 4
  • Back-UPS & Surge Protectors 3
  • DCIM Support 2
  • apc 2
  • firmware 2
  • UPS 2
  • Home & Office - Accessories 2
  • Product Feedback 2
  • UPS Network Management Card 2
  • SMARTCONNECT 2
  • NetBotz 2
  • EcoStruxure IT Design CFD 1
  • Smart-750 1
  • Smart Design & Engineering 1
  • srt5000 1
  • detected 1
  • AP9210 1
  • Legacy Gateways & Energy Servers 1
  • symmetra 1
  • AP9619 1
  • 240v 1
  • spit phase 1
  • Certicate 1
  • AP7750A 1
  • Datacenter Forum 1
  • managedservices 1
  • dedicatedserver 1
  • managedserver 1
  • Electrical Calculation Tools 1
  • Tips and ideas 1
  • Building Operations 1
  • DDF 1
  • IT Advisor 1
  • Battery life 1
  • Safety 1
  • ssl 1
  • SERVER 1
  • Previous
  • 1 of 6
  • Next
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All
Related Products
Thumbnail of EcoStruxure™ IT SmartConnect
Schneider Electric
EcoStruxure™ IT SmartConnect
32
Thumbnail of Smart-UPS
Schneider Electric
Smart-UPS
29
Thumbnail of Uninterruptible Power Supply (UPS)
Schneider Electric
Uninterruptible Power Supply (UPS)
25
Load more

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

APC UPS Data Center & Enterprise Solutions Forum

Start a Topic
  • All
  • Solved
  • Unsolved
  • Unanswered
Solved
Anonymous user
Anonymous user

Phase Near Overload everyday at the same time

Hi all, We've been experiencing this problem recently in the past month where one of our PDUs (AP8941) in a data center give us "Switched Rack PDU: Phase near overload on phase #1." and 1 minute later ...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
3772 0 3
Latest Reply: BillP

Solved
Anonymous user
Anonymous user

AP7900 - Switched Rack Power - Will Not Come Up

Hello, I recently acuqired an AP7900 from one of our labs and am looking to start using it in a new test environment. I was able to determine the IP address (hold grey button for 5 secs), and log...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
6644 0 5
Latest Reply: BillP

Solved
BillP
Administrator BillP Administrator

AR3150 CONTACT LOCK SYSTEM

Hi, System works with the APC door open dual contact system. 1. contact on, 2. contact off. With 3th party fingerprint sensor is also able to open a single contact, but do not shut down. Because this ...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
1262 0 1
Latest Reply: BillP

Solved
Anonymous user
Anonymous user

AP9630 with SmartUPS 5000 - Garbled Characters

Hello, We recently moved our SmartUPS 5000 (with an AP9630 NMC2) to our new location. I need to connect to it to update the IP address, as it is still configured for the old space on a subnet that no l...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
2921 0 2
Latest Reply: Anonymous user

Solved
BillP
Administrator BillP Administrator

PowerChute Personal Edition 3.0.2 won't install on Windows 10

I have BR1500G and Windows 10 Pro 64-bit and can't get PCPEInstaller.exe (fresh download of v. 3.0.2) to install -- it won't get past installing .net 2.0* .net 2.0 won't install on Windows 10, so can't...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
19078 0 32
Latest Reply: pjzzz_apc

Solved
Anonymous user
Anonymous user

Powerchute and physcal servers

Hello, Does network shutdown allow managing of physical servers connected to the APC? I have configured it to shutdown my VM but I don't see anyplace in Network Shutdown to specify physical servers. t...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
1911 0 3
Latest Reply: BillP

Solved
BillP
Administrator BillP Administrator

PowerChute keep send shutdown command to client

I have configured APC Network Management card and truing to shutdown server before it drain out. one of Linux server i have added to PowerChute client and configure shutdown time. after first time te...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
918 0 1
Latest Reply: BillP

Solved
Anonymous user
Anonymous user

PCBE Compatibility Issue.

Hi Team, Greetings. We would like to seek your advice on the PCBE compatibility issue. From the compatibility chart, the PCBE only compatible to Oracle Linux 6.5. How about client with Oracle Linux 6.7...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
1589 0 1
Latest Reply: BillP

Solved
Anonymous user
Anonymous user

UPS is not recognised on my SBS 2011 server and not communicate

Hello I have APC Back-UP Pro 900VA connected via USB to HP Proliant server with SBS2011 OS My operating system - Windows Small Business Server 2011 The model and UPS cable - APC Back-UP Pro 900VA ...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
3058 0 2
Latest Reply: Anonymous user

Solved
itdweeb999_apc
Crewman itdweeb999_apc

Using Network Shutdown with VMWare Server

I have a very simple setup. I have 1 esxi 6.0 server which hosts 1 windows 2012 virtual machine. I need my Network Management Card to shutdown the virtual machine and the esxi server. I'm confused on h...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
3949 0 7
Latest Reply: BillP

Solved
Anonymous user
Anonymous user

AP9617 and DLA2200RM2U issue

I have a DLA2200RM2U 2u rack mount UPS and I bought a AP9617 management card for it. However the under the device manager menu there are no devices listed it is just blank. The card currently has AOS...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
882 0 2
Latest Reply: Anonymous user

  • « Previous
    • 1
    • …
    • 271
    • 272
    • 273
    • …
    • 1078
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore