Using Network Shutdown with VMWare Server

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Using Network Shutdown with VMWare Server
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
itdweeb999_apc
Crewman itdweeb999_apc
Crewman

Posted: ‎2021-07-09 03:13 AM . Last Modified: ‎2024-02-14 11:22 PM

0 Likes
7
3945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 03:13 AM . Last Modified: ‎2024-02-14 11:22 PM

Using Network Shutdown with VMWare Server

I have a very simple setup. I have 1 esxi 6.0 server which hosts 1 windows 2012 virtual machine. I need my Network Management Card to shutdown the virtual machine and the esxi server. I'm confused on how to do this. I assume that I need to install PCNS agent on my 2012 server. However, when I go to install the agent on my virtual machine, I'm a little confused because it asks if I want to enable vmware support and then at the end, it launches a wizard that is asking me for all of my vmware host information. I don't understand why it is asking for the vmware host information. Also, I found the link below which seems to be the information on how to configure for vmware. I'm just a little confused by this document though - do I really need to setup an appliance on my vmware server in order to properly shutdown esxi host? I'm just all sorts of confused.

http://www.apcmedia.com/salestools/PMAR-9HBK44/PMAR-9HBK44_R3_EN.pdf?sdirect=true

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 03:13 AM . Last Modified: ‎2024-02-14 11:22 PM

0 Likes
0
3944
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 03:13 AM . Last Modified: ‎2024-02-14 11:22 PM

Jeff,

Install PowerChute on the Windows system and when asked select enable VMware support. Then when running the configuration wizard select Standalone VMware host and enter the host information. Once PowerChute has been configured you will need to verify that VMWare tools is installed on each VM and follow the instruction in Knowledge Base document FA159688 to configure the ESXi host to power down the VMs. You should review VMware knowledge base document 1008182 for assistance with shutdown of the VMs. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 03:13 AM . Last Modified: ‎2024-02-14 11:22 PM

0 Likes
0
3944
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 03:13 AM . Last Modified: ‎2024-02-14 11:22 PM

Hi,

You should not install PowerChute on the Server 2012 VM. You should install PowerChute Network Shutdown Appliance on the ESXi host. Once installed configure for standalone host and add the host information. PowerChute will shutdown the host and the host will be responsible for powering down the VMs. Knowledge Base document FA159688 will help you with configuring the host to power down the VMs. You should also review PowerChute Network Shutdown VMware User's Guide. Help configuring Standalone VMware host begins on page 14 of the User's Guide.

Reply

Link copied. Please paste this link to share this article on your social media post.

itdweeb999_apc
Crewman itdweeb999_apc
Crewman

Posted: ‎2021-07-09 03:13 AM . Last Modified: ‎2024-02-14 11:22 PM

0 Likes
0
3944
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 03:13 AM . Last Modified: ‎2024-02-14 11:22 PM

Thank you for the response. So, it sounds like nothing at all is installed on the actual virtual machine? Instead, I need to create the network shutdown appliance on the esxi server? I did review the vmware User's guide but it seems to assume that I have vcenter which I don't so I don't really know how much of this guide applies to my situation. The guide keeps showing screenshots of what looks to be a powerchute agent (green screenshots). That confuses me a little as I have no idea where they are even accessing this screen. Seems like they forgot to mention an entire step.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 03:13 AM . Last Modified: ‎2024-02-14 11:22 PM

0 Likes
0
3945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 03:13 AM . Last Modified: ‎2024-02-14 11:22 PM

Hi,

Once you install the Appliance on the host (See the installation guide for assistance page 51) you access the PowerChute configuration wizard to configure PowerChute to communicate with the host. To access the wizard open a web browser and enter https://IP address of the appliance:6547 The wizard will launch and walk you through configuring PowerChute. 

Reply

Link copied. Please paste this link to share this article on your social media post.

itdweeb999_apc
Crewman itdweeb999_apc
Crewman

Posted: ‎2021-07-09 03:13 AM . Last Modified: ‎2024-02-14 11:22 PM

0 Likes
0
3945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 03:13 AM . Last Modified: ‎2024-02-14 11:22 PM

OK, as I'm reading through this guide, I am seeing that there are actually 3 options to that allow you to monitor a VM host.

Installing on Windows to Monitor VMware Hosts
Deploying the PowerChute Virtual Appliance
Installing on vSphere Management Assistant (vMA)
I actually realized that there is another physical server running windows at the location so I guess option 1 would be possible as well. However, out of these three options, which would be recommended?
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 03:13 AM . Last Modified: ‎2024-02-14 11:22 PM

0 Likes
0
3945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 03:13 AM . Last Modified: ‎2024-02-14 11:22 PM

Hi,

If the Windows system is connected to (plugged into) the UPS that the ESXi host is connected to I suggest the Windows option since most people prefer to work with Windows OS. If the Windows system is not connected to the UPS then I recommend using the Appliance. 

My personal preference is the Appliance. I prefer working with a Linux VM. 

Reply

Link copied. Please paste this link to share this article on your social media post.

itdweeb999_apc
Crewman itdweeb999_apc
Crewman

Posted: ‎2021-07-09 03:13 AM . Last Modified: ‎2024-02-14 11:22 PM

0 Likes
0
3945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 03:13 AM . Last Modified: ‎2024-02-14 11:22 PM

Great. Thanks for all of the input and help. I will likely go the windows route since I am more knowledgeable with windows. So just to clarify, I install nothing (no agent) on the actuallyVMWare virtual server as long as I've followed the article for

Configure virtual machine shutdown on standalone VMware ESX and ESXi hosts protected by PowerChute.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 03:13 AM . Last Modified: ‎2024-02-14 11:22 PM

0 Likes
0
3945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 03:13 AM . Last Modified: ‎2024-02-14 11:22 PM

Jeff,

Install PowerChute on the Windows system and when asked select enable VMware support. Then when running the configuration wizard select Standalone VMware host and enter the host information. Once PowerChute has been configured you will need to verify that VMWare tools is installed on each VM and follow the instruction in Knowledge Base document FA159688 to configure the ESXi host to power down the VMs. You should review VMware knowledge base document 1008182 for assistance with shutdown of the VMs. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.