Hello
I have APC Back-UP Pro 900VA connected via USB to HP Proliant server with SBS2011 OS
UPS doesn´t communicate with apcupsd - is not recognised










Is this UPS compatible with Powerchute ?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 03:14 AM . Last Modified: 2024-02-14 11:21 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 03:14 AM . Last Modified: 2024-02-14 11:21 PM
Hi Bill,
thank you for your reply, I will try. APCUPSD I was try before but no communicating too
I am going to try Personal edition of PowerChute
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 03:14 AM . Last Modified: 2024-02-14 11:21 PM
Hi,
PowerChute Business Edition is not compatible with a Back-UPS Pro. You need to uninstall PowerChute Business Edition and install PowerChute Personal Edition or install APCUPSD if you do not want to run PowerChute Personal Edition.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 03:14 AM . Last Modified: 2024-02-14 11:21 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 03:14 AM . Last Modified: 2024-02-14 11:21 PM
Hi Bill,
thank you for your reply, I will try. APCUPSD I was try before but no communicating too
I am going to try Personal edition of PowerChute