Phase Near Overload everyday at the same time

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Phase Near Overload everyday at the same time
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-09 03:47 AM . Last Modified: ‎2024-02-14 11:18 PM

0 Likes
3
3779
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 03:47 AM . Last Modified: ‎2024-02-14 11:18 PM

Phase Near Overload everyday at the same time

Hi all,

We've been experiencing this problem recently in the past month where one of our PDUs (AP8941) in a data center give us "Switched Rack PDU: Phase near overload on phase #1." and 1 minute later we recieve "Switched Rack PDU: Phase near overload cleared on phase #1.".

We have Dell PowerEdge servers running Windows Server 2008 R2 and Server 2012 and 1 KVM utilizing this PDU.

This happens at the same time every morning, at 7:00 AM, but at no other point during the day.

We have not changed anything, or plugged any new device into any outlet.

Can confirm that no servers have restarted during this time (They are only scheduled to restart once a week on Sunday)

Any ideas as to what might cause what seems to be a "Scheduled" increase in amperage?

 

 07/19/2015 06:18:04 Switched Rack PDU: Phase near overload on phase #1.
 07/19/2015 06:18:01 Switched Rack PDU: Phase near overload cleared on phase #1.
 07/19/2015 06:17:56 Switched Rack PDU: Phase near overload on phase #1.
 07/19/2015 06:17:39 Switched Rack PDU: Phase near overload cleared on phase #1.
 07/19/2015 06:17:35 Switched Rack PDU: Phase near overload on phase #1.
 07/19/2015 06:16:25 Switched Rack PDU: Phase near overload cleared on phase #1.
 07/19/2015 06:16:23 Switched Rack PDU: Phase near overload on phase #1.
 07/19/2015 06:16:21 Switched Rack PDU: Phase near overload cleared on phase #1.
 07/19/2015 06:16:16 Switched Rack PDU: Phase near overload on phase #1.
 07/19/2015 06:16:15 Switched Rack PDU: Phase near overload cleared on phase #1.
 07/19/2015 06:16:12 Switched Rack PDU: Phase near overload on phase #1.
 07/19/2015 06:16:03 Switched Rack PDU: Phase near overload cleared on phase #1.

 

 

 

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • daily
  • everyday
  • near
  • overload
  • phase
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
rnauert_apc
Crewman rnauert_apc
Crewman

Posted: ‎2021-07-09 03:48 AM . Last Modified: ‎2024-02-14 11:18 PM

0 Likes
0
3779
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 03:48 AM . Last Modified: ‎2024-02-14 11:18 PM

Angela-  I am having the same problem that was listed in this thread.  Mine has been going on for some time on this device.  We have two of these and the 2nd unit is not having this problem.  Both are being used as redundant power supplies to my server rack.  I have even moved several 5-15Ps off of this device and moved to a separate multi outlet to troubleshoot.  I have the data and event txt files if you need to review them.  Thanks.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 03:48 AM . Last Modified: ‎2024-02-14 11:18 PM

0 Likes
0
3779
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 03:48 AM . Last Modified: ‎2024-02-14 11:18 PM

I have the same issue.  I have two AP8959EU3 switched RPDU in the same server rack as all the devices have redundant power supplies.  Both RPDU have the same number of connections yet one of the RPDU's is showing a Phase Near Overload all the time.  The other RPDU is showing a phase load of .66 KW and but the RPDU in question is showing a  load of 3.25 KW.  As I mentioned both have the exact same number of connections from different redundant power supplies.  All of the devices power supplies have green status lights and are all running ok.  I am getting a change request submitted to update the firmware from 6.3.3 to 6.4.4 but am not confident that this will resolve this issue.  Any ideas?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 03:48 AM . Last Modified: ‎2024-02-14 11:18 PM

0 Likes
0
3779
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 03:48 AM . Last Modified: ‎2024-02-14 11:18 PM

Can you share the full event.txt, data.txt, and config.ini files? (Instructions here if you need them -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156131) I'd have to guest this is a legitimate increase/site issue unless there is a threshold set really low that shouldn't be? Maybe something on the same circuit causing this as an effect that kicks on at the same time every day?

Are all of those devices connected to the same bank of outlets as well? I have never seen a PDU erroneously do something like this before.

Reply

Link copied. Please paste this link to share this article on your social media post.

rnauert_apc
Crewman rnauert_apc
Crewman

Posted: ‎2021-07-09 03:48 AM . Last Modified: ‎2024-02-14 11:18 PM

0 Likes
0
3780
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 03:48 AM . Last Modified: ‎2024-02-14 11:18 PM

Angela-  I am having the same problem that was listed in this thread.  Mine has been going on for some time on this device.  We have two of these and the 2nd unit is not having this problem.  Both are being used as redundant power supplies to my server rack.  I have even moved several 5-15Ps off of this device and moved to a separate multi outlet to troubleshoot.  I have the data and event txt files if you need to review them.  Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 03:48 AM . Last Modified: ‎2024-02-14 11:18 PM

0 Likes
0
3780
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 03:48 AM . Last Modified: ‎2024-02-14 11:18 PM

I have the same issue.  I have two AP8959EU3 switched RPDU in the same server rack as all the devices have redundant power supplies.  Both RPDU have the same number of connections yet one of the RPDU's is showing a Phase Near Overload all the time.  The other RPDU is showing a phase load of .66 KW and but the RPDU in question is showing a  load of 3.25 KW.  As I mentioned both have the exact same number of connections from different redundant power supplies.  All of the devices power supplies have green status lights and are all running ok.  I am getting a change request submitted to update the firmware from 6.3.3 to 6.4.4 but am not confident that this will resolve this issue.  Any ideas?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore