Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Phase Near Overload everyday at the same time

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: Phase Near Overload everyday at the same time
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5027
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
tandetit_apc
tandetit_apc
Cadet

Posted: ‎2021-07-09 03:47 AM

0 Likes
3
813
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-09 03:47 AM

Phase Near Overload everyday at the same time

This was originally posted on APC forums on 7/21/2015


Hi all,

We've been experiencing this problem recently in the past month where one of our PDUs (AP8941) in a data center give us "Switched Rack PDU: Phase near overload on phase #1." and 1 minute later we recieve "Switched Rack PDU: Phase near overload cleared on phase #1.".

We have Dell PowerEdge servers running Windows Server 2008 R2 and Server 2012 and 1 KVM utilizing this PDU.

This happens at the same time every morning, at 7:00 AM, but at no other point during the day.

We have not changed anything, or plugged any new device into any outlet.

Can confirm that no servers have restarted during this time (They are only scheduled to restart once a week on Sunday)

Any ideas as to what might cause what seems to be a "Scheduled" increase in amperage?

 

 07/19/2015 06:18:04 Switched Rack PDU: Phase near overload on phase #1.
 07/19/2015 06:18:01 Switched Rack PDU: Phase near overload cleared on phase #1.
 07/19/2015 06:17:56 Switched Rack PDU: Phase near overload on phase #1.
 07/19/2015 06:17:39 Switched Rack PDU: Phase near overload cleared on phase #1.
 07/19/2015 06:17:35 Switched Rack PDU: Phase near overload on phase #1.
 07/19/2015 06:16:25 Switched Rack PDU: Phase near overload cleared on phase #1.
 07/19/2015 06:16:23 Switched Rack PDU: Phase near overload on phase #1.
 07/19/2015 06:16:21 Switched Rack PDU: Phase near overload cleared on phase #1.
 07/19/2015 06:16:16 Switched Rack PDU: Phase near overload on phase #1.
 07/19/2015 06:16:15 Switched Rack PDU: Phase near overload cleared on phase #1.
 07/19/2015 06:16:12 Switched Rack PDU: Phase near overload on phase #1.
 07/19/2015 06:16:03 Switched Rack PDU: Phase near overload cleared on phase #1.

 

 

 

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • daily
  • everyday
  • near
  • overload
  • phase
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
rnauert_apc
Crewman rnauert_apc
Crewman

Posted: ‎2021-07-09 03:48 AM

0 Likes
0
813
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-09 03:48 AM

This was originally posted on APC forums on 4/26/2016


Angela-  I am having the same problem that was listed in this thread.  Mine has been going on for some time on this device.  We have two of these and the 2nd unit is not having this problem.  Both are being used as redundant power supplies to my server rack.  I have even moved several 5-15Ps off of this device and moved to a separate multi outlet to troubleshoot.  I have the data and event txt files if you need to review them.  Thanks.

See Answer In Context

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 03:48 AM

0 Likes
0
813
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-09 03:48 AM

This reply was originally posted by Ron on APC forums on 10/20/2017


I have the same issue.  I have two AP8959EU3 switched RPDU in the same server rack as all the devices have redundant power supplies.  Both RPDU have the same number of connections yet one of the RPDU's is showing a Phase Near Overload all the time.  The other RPDU is showing a phase load of .66 KW and but the RPDU in question is showing a  load of 3.25 KW.  As I mentioned both have the exact same number of connections from different redundant power supplies.  All of the devices power supplies have green status lights and are all running ok.  I am getting a change request submitted to update the firmware from 6.3.3 to 6.4.4 but am not confident that this will resolve this issue.  Any ideas?

See Answer In Context

Reply
Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 03:48 AM

0 Likes
0
813
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-09 03:48 AM

This reply was originally posted by Angela on APC forums on 7/21/2015


Can you share the full event.txt, data.txt, and config.ini files? (Instructions here if you need them -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156131) I'd have to guest this is a legitimate increase/site issue unless there is a threshold set really low that shouldn't be? Maybe something on the same circuit causing this as an effect that kicks on at the same time every day?

Are all of those devices connected to the same bank of outlets as well? I have never seen a PDU erroneously do something like this before.

Reply
rnauert_apc
Crewman rnauert_apc
Crewman

Posted: ‎2021-07-09 03:48 AM

0 Likes
0
814
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-09 03:48 AM

This was originally posted on APC forums on 4/26/2016


Angela-  I am having the same problem that was listed in this thread.  Mine has been going on for some time on this device.  We have two of these and the 2nd unit is not having this problem.  Both are being used as redundant power supplies to my server rack.  I have even moved several 5-15Ps off of this device and moved to a separate multi outlet to troubleshoot.  I have the data and event txt files if you need to review them.  Thanks.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 03:48 AM

0 Likes
0
814
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-09 03:48 AM

This reply was originally posted by Ron on APC forums on 10/20/2017


I have the same issue.  I have two AP8959EU3 switched RPDU in the same server rack as all the devices have redundant power supplies.  Both RPDU have the same number of connections yet one of the RPDU's is showing a Phase Near Overload all the time.  The other RPDU is showing a phase load of .66 KW and but the RPDU in question is showing a  load of 3.25 KW.  As I mentioned both have the exact same number of connections from different redundant power supplies.  All of the devices power supplies have green status lights and are all running ok.  I am getting a change request submitted to update the firmware from 6.3.3 to 6.4.4 but am not confident that this will resolve this issue.  Any ideas?

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc