IT Expert - Device communication failure

ITE Configuration

Detailed instructions for how to configure EcoStruxure IT Expert

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • IT Expert
  • Configuration
  • ITE Configuration
  • IT Expert - Device communication failure
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Service contract information in IT Expert
  • Service visit information in IT Expert
  • Device warranty information in IT Expert
  • Create locations in IT Expert
  • Create an alarm severity policy in IT Expert
  • Custom properties in IT Expert
  • Single device configuration
  • Outlet control in IT Expert
  • EcoStruxure IT authentication method
  • SMS authentication
  • Google, Duo, Auth0, or other authentication
  • Setting up call priority for Asset Advisor in IT E...
  • Configure EcoStruxure IT mobile app push notificat...
  • Rack ATS firmware update can cause permanent damag...
  • Configure event actions for APC SNMP devices in IT...
  • IT Expert - Device communication failure
  • IT Expert - Device is offline
  • IT Expert - Device not recognized
  • Service contract information in IT Expert
  • Service visit information in IT Expert
  • Device warranty information in IT Expert
  • Create locations in IT Expert
  • Create an alarm severity policy in IT Expert
  • Custom properties in IT Expert
  • Single device configuration
  • Outlet control in IT Expert
  • EcoStruxure IT authentication method
  • SMS authentication
  • Google, Duo, Auth0, or other authentication
  • Setting up call priority for Asset Advisor in IT E...
  • Configure EcoStruxure IT mobile app push notificat...
  • Rack ATS firmware update can cause permanent damag...
  • Configure event actions for APC SNMP devices in IT...
  • IT Expert - Device communication failure
  • IT Expert - Device is offline
  • IT Expert - Device not recognized

Related Forums

  • EcoStruxure IT Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

EcoStruxure IT Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to ITE Configuration
Start a Topic
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
22576 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

IT Expert - Device communication failure

Picard EcoStruxureIT
‎2022-09-21 07:02 AM

Last Updated: Sisko JLehr Sisko ‎2024-09-03 06:58 AM

When a device communication failure occurs in IT Expert, it is usually because the FTP/SCP credentials are not configured properly on the APC Network Management Card (NMC) or in the Gateway file transfer settings.

How to configure Gateway device file transfer settings

Need NMC help?

 

Common reasons for failure

Resolution

The device does not have FTP/SCP enabled and/or credentials configured.

To use FTP, the FTP server must be enabled on the NMC device.

To use SCP, SSH must be enabled on the NMC device.

 

  1. Log in to the NMC device.
  2. For FTP: Go to Configuration > Network > FTP server.
  3. For SSH: Go to Configuration > Network > Console > Access.

 

Make sure the Super User or Administrator is configured and enabled on the NMC device.

 

  1. Go to Configuration > Security > Local Users > Management to configure users.
The Gateway has incorrect NMC device credentials, or the device credentials provided do not have adequate privileges for FTP/SCP functions.

Make sure FTP and SSH are enabled on the NMC device.

 

Make sure the NMC device credentials you configure in the Gateway are for the device Super User or Administrator, and that they are correct.

The Gateway does not have FTP/SCP file transfer credentials configured.

Add file transfer settings to the Device Configuration and Firmware Update settings in the Gateway.

 

  1. Log in to the Gateway, and go to Settings > Device credentials > New file transfer credentials.

 

Make sure the Gateway is configured with the correct APC NMC device credentials. See how

The device is on the wrong port.

Make sure port settings are correct on the device and in the Gateway.

Network or firewall are not configured properly.

Make sure to check that your network and firewall are working properly and allowing devices to register.

 

IMPORTANT: If you make any changes on an NMC, make sure you log out to reboot the card.

After you make any changes to device credentials in the Gateway, you must rediscover the affected devices.

 

idea_icon_6893533639837.pngidea_icon_6893533639837.png To check the FTP/SCP settings on a device in IT Expert, go to Devices and select the device. Click Configuration and then Get latest.
 

See Single device configuration

 

If you can successfully retrieve the latest settings from the device, it is a good indication that device settings and Gateway settings are correct.

If you cannot retrieve settings from the device, review your settings again.

 

Note: When FTP/SCP credentials are not set up correctly, some EcoStruxure IT features are not available.

Was this article helpful? Yes No
0% helpful (0/3)

Link copied. Please paste this link to share this article on your social media post.

Comments
LarryK
Lt. Commander LarryK
Lt. Commander
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2024-11-22 07:18 AM

One site has 3 devices.

All three failed the update with the message: Download checksum mismatch

There is no description of how to recover from that failure in this documentation.

Also, ESIT now no longer presents the ability to update the devices - which means I must go back to working with them manually via a web browser, defeating the purported usefulness of ESIT...

 

Edited to say:  I attempted one device at the other sites and not one was capable of succeeding.

Ticket 113089185 has been created.

Turd_Ferguson
Turd_Ferguson
Cadet
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2024-11-22 09:55 AM

We have the same problem LarryK has.
Attempted to update multiple devices multiple times--and with two different Gateways.
Some UPSs had NMC2 going to 7.1.8, some had NMC3 going to 3.2.0.8. Same failure, regardless.
 checksum_mismatch.jpg

LarryK
Lt. Commander LarryK
Lt. Commander
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2024-11-25 10:36 AM

DCIM Technical Support reports:

We did have a platform issue with the checksum. A hotfix is in place and updates should work for you. If you're still experiencing issues please let me know.

 

Unfortunately, one site now has a new (also undocumented) problem:

 

Binary image version mismatch

 

Sigh...

ponzi
ponzi
Cadet
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2025-07-29 07:56 AM

Screenshot 2025-07-29 at 10.55.41 AM.png

On site, have multitude of these and through Eco I get this after eventually getting the config setup. HELP!

LarryK
Lt. Commander LarryK
Lt. Commander
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2025-12-03 04:04 AM

Newly found with SU v3.4.1.1 implementation.

2 successful, 1 [did not work] - and now no ability the only way to update the device - is to log off the account and log back on.

 

Requesting an enhancement that a screen refresh do this for me..

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore