Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
Options
  • Mark all as New
  • Mark all as Read
  • Float this item to the top
  • Subscribe
  • Bookmark
  • Invite a Friend
  • Threaded format
  • Linear Format
  • Sort by Topic Start Date
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Labels
Top Labels
  • Alphabetical
  • Smart-UPS & Symmetra LX | RM 4,611
  • UPS Management Devices & PowerChute Software 2,913
  • Racks, Rack Accessories, & Cooling 955
  • Data Center & Facility 3 Phase UPS 605
  • General Questions & Suggestions 240
  • Getting Started 166
  • Datacenter UPS 131
  • Server Room & Data Center Design Best Practices 106
  • Smart-UPS & Symmetra LX-RM 97
  • Other Environmental Monitoring Products & Questions 48
  • Business Power UPS 36
  • Datacenter Racks & Cooling 28
  • Rack Accessories & Cooling 16
  • Business Power Software & NMC 15
  • Home & Office - UPS & Software 15
  • Datacenter Accessories 15
  • Datacenter Netbotz & Monitoring 9
  • Network Management Card 6
  • Data Center Expert 6
  • Racks 6
  • power monitoring expert 5
  • IT Expert 5
  • Data Center Operation 4
  • Back-UPS & Surge Protectors 3
  • DCIM Support 2
  • apc 2
  • firmware 2
  • UPS 2
  • Home & Office - Accessories 2
  • Product Feedback 2
  • UPS Network Management Card 2
  • SMARTCONNECT 2
  • NetBotz 2
  • EcoStruxure IT Design CFD 1
  • Smart-750 1
  • Smart Design & Engineering 1
  • srt5000 1
  • detected 1
  • AP9210 1
  • Legacy Gateways & Energy Servers 1
  • symmetra 1
  • AP9619 1
  • 240v 1
  • spit phase 1
  • Certicate 1
  • AP7750A 1
  • Datacenter Forum 1
  • managedservices 1
  • dedicatedserver 1
  • managedserver 1
  • Electrical Calculation Tools 1
  • Tips and ideas 1
  • Building Operations 1
  • DDF 1
  • IT Advisor 1
  • Battery life 1
  • Safety 1
  • ssl 1
  • SERVER 1
  • Previous
  • 1 of 6
  • Next
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All
Related Products
Thumbnail of EcoStruxure™ IT SmartConnect
Schneider Electric
EcoStruxure™ IT SmartConnect
32
Thumbnail of Smart-UPS
Schneider Electric
Smart-UPS
29
Thumbnail of Uninterruptible Power Supply (UPS)
Schneider Electric
Uninterruptible Power Supply (UPS)
25
Load more

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

APC UPS Data Center & Enterprise Solutions Forum

Start a Topic
  • All
  • Solved
  • Unsolved
  • Unanswered
Solved
Anonymous user
Anonymous user

"Lost communication with UPS" every few days

Hello. We have a number of SMT1500IC UPSes, connected via USB cables to HP PCs running PowerChute Business Edition 9.2.5 that came with them. USB cables are all OK and nobody touches them. We turn the ...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
1139 0 7
Latest Reply: Anonymous user

Solved
Anonymous user
Anonymous user

Help APC SURTD5000XLI error (red X led)

Hi AllI just have problem with my UPS SURTD5000XLI . 9RoQBFnZQYcuMGFoXVe9SQ%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpeg it working fine~ 2 year until today ...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
8518 0 3
Latest Reply: BillP

Solved
Anonymous user
Anonymous user

How to get LOADPCT on SMT 1500 ID17 UPS Firmware 7.1

How can I get LOADPCT out of this UPS? Do I need to add a network card? I dont think I can update the firmware any further. APC : 001,027,0656DATE : 2019-02-24 15:44:43 -0500 HOSTNAME : debia...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
1204 0 2
Latest Reply: BillP

Solved
Anonymous user
Anonymous user

SmartUPS X 1500 not recognizing that a battery is connected. Battery s...

My UPS is not recognizing that a battery is connected. I tested the batteries individually and all four tested between 12.95v-13.30v. When I power on the UPS while connected to utility power, the UPS i...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
1888 0 2
Latest Reply: BillP

Solved
BillP
Administrator BillP Administrator

SRT 8KVA battery says error 0040

Can anyone state what does this code mean? Also is there is a document available that states what all the fault codes mean?
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
2308 0 2
Latest Reply: BillP

Solved
Anonymous user
Anonymous user

APC Smart-UPS 3000VA Self Test Drained Battery By 100% But Passed

Have any of you encountered the situation that when you run a self test it completely drains the batteries from 100% to 0? It happened almost instantly but it stated that it passed the test. Any inform...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
3639 0 8
Latest Reply: Anonymous user

Solved
GiovanniSilvestri_apc
GiovanniSilvestri_apc

APC Smart-UPS RT 2000 internal fault

I have a APC Smart-UPS RT 2000 and the fault red led "X" is blinking together with two LEDs of the batteries. Starting from the bottom are the second and third, as shown in the picture. All 3 leds flas...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
4834 0 3
Latest Reply: BillP

Solved
Anonymous user
Anonymous user

Vmin significant drop, Bypass not in range; high voltage

HI I have Smart-UPS SRT 5000 and it reported Bypass not in range; In the data log i can see that Vmin significantly dropped at 02/02/2019 18:57:44. What could cause Vmin to drop like this ?Could this b...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
1888 0 4
Latest Reply: Anonymous user

Solved
Anonymous user
Anonymous user

SMT1500 firmware update

Hey guys, Just double checking I'm not being a muppet, and if I am, how to alieviate that! I've just got a second hand SMT1500 UPS, and I'm looking to upgrade to the latest firmware (especially if I ...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
7818 0 4
Latest Reply: Anonymous user

Solved
Anonymous user
Anonymous user

APC 1500 UPS: The output power is turned off.

Hi, APC team On our ups see all the time of the error and they are not included below log and status UPS 02/02/2018 22:50:33 Device UPS: The output power is turned off. 02/02/2018 22:50:33 Device...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
8320 0 4
Latest Reply: BillP

Solved
Anonymous user
Anonymous user

Smart-UPS SRT10000 : An internal UPS communication fault exists

Hi! We bought Smart-UPS SRT 10000 a couple of years ago, but installed it a week ago. It worked ok until we connected a external battery pack. There was an error on the lcd-display "Battery Sys Error 0...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
4290 0 4
Latest Reply: Anonymous user

  • « Previous
    • 1
    • …
    • 847
    • 848
    • 849
    • …
    • 1078
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore