APC 1500 UPS: The output power is turned off.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC 1500 UPS: The output power is turned off.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:46 AM . Last Modified: ‎2024-03-15 06:12 AM

0 Likes
4
8271
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:46 AM . Last Modified: ‎2024-03-15 06:12 AM

APC 1500 UPS: The output power is turned off.

Hi, APC team

On our ups see all the time of the error and they are not included

below log and status UPS

02/02/2018 22:50:33 Device UPS: The output power is turned off.
 02/02/2018 22:50:33 Device UPS: The output power is now turned on.
 02/02/2018 22:50:33 Device UPS: The output power is turned off.
 02/02/2018 22:50:33 Device UPS: The output power is now turned on.
 02/02/2018 22:50:33 Device UPS: The output power is turned off.
 02/02/2018 22:50:33 Device UPS: The output power is now turned on.
 02/02/2018 22:50:33 Device UPS: The output power is turned off.

Model

Smart-UPS 2200
SKU
SMT2200RMI2U
Serial Number
AS1752161180
Firmware Revision
UPS 09.3 (ID18)
Manufacture Date
12/29/2017
Apparent Power Rating
2200  VA
Real Power Rating
1980  W
Battery SKU
RBC43
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:46 AM . Last Modified: ‎2024-03-15 06:12 AM

0 Likes
0
8266
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:46 AM . Last Modified: ‎2024-03-15 06:12 AM

Hi Ali,

Apologies for the late reply. The second series of entries also appears to be an event log transcript. What we would need to have a look at is the UPS logs that are available on the LCD display under Main Menu->Logs. The last 10 transfer events (displayed as Xfer event 1 to 10) and last 10 fault events are listed here and could be useful in finding out why the UPS is turning off the output.

Alternatively, if the UPS is not easily accessible to check the LCD display, I recommend downloading the complete log archive from the network management web interface (About>Support>Generate Logs>Download) and contacting your local APC tech support with the log file.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:46 AM . Last Modified: ‎2024-03-15 06:12 AM

0 Likes
0
8266
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:46 AM . Last Modified: ‎2024-03-15 06:12 AM

Hi Ali,

Could you go to the Main Menu > Log section of your UPS LCD display, and let me know the last 10 transfer event and last 10 fault event entries.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:46 AM . Last Modified: ‎2024-03-15 06:12 AM

0 Likes
0
8266
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:46 AM . Last Modified: ‎2024-03-15 06:12 AM

Hi Szabi,

02/05/2018 07:13:31 Device UPS: The output power is turned off.
 02/05/2018 07:13:31 Device UPS: The output power is now turned on.
 02/05/2018 07:13:31 Device UPS: The output power is turned off.
 02/05/2018 07:13:31 Device UPS: The output power is now turned on.
 02/05/2018 07:13:31 Device UPS: The output power is turned off.
 02/05/2018 07:13:31 Device UPS: The output power is now turned on
02/05/2018 07:13:31 Device UPS: The output power is turned off.
 02/05/2018 07:13:31 Device UPS: The output power is now turned on.
 02/05/2018 07:13:31 Device UPS: The output power is turned off.
 02/05/2018 07:13:31 Device UPS: The graceful shutdown period has ended.
 02/05/2018 07:13:31 Device UPS: The power for switched outlet group 1, Outlet Group 1, is off.
 02/05/2018 07:13:31 Device UPS: The power for the main outlet group, UPS Outlets, is off.
 02/05/2018 07:13:28 Device UPS: Restored the local network management interface-to-UPS communication.
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:46 AM . Last Modified: ‎2024-03-15 06:12 AM

0 Likes
0
8266
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:46 AM . Last Modified: ‎2024-03-15 06:12 AM

up

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:46 AM . Last Modified: ‎2024-03-15 06:12 AM

0 Likes
0
8267
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:46 AM . Last Modified: ‎2024-03-15 06:12 AM

Hi Ali,

Apologies for the late reply. The second series of entries also appears to be an event log transcript. What we would need to have a look at is the UPS logs that are available on the LCD display under Main Menu->Logs. The last 10 transfer events (displayed as Xfer event 1 to 10) and last 10 fault events are listed here and could be useful in finding out why the UPS is turning off the output.

Alternatively, if the UPS is not easily accessible to check the LCD display, I recommend downloading the complete log archive from the network management web interface (About>Support>Generate Logs>Download) and contacting your local APC tech support with the log file.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore