"Lost communication with UPS" every few days

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • "Lost communication with UPS" every few days
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:56 AM . Last Modified: ‎2024-03-15 06:10 AM

0 Likes
7
778
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:56 AM . Last Modified: ‎2024-03-15 06:10 AM

"Lost communication with UPS" every few days

Hello. We have a number of SMT1500IC UPSes, connected via USB cables to HP PCs running PowerChute Business Edition 9.2.5 that came with them. USB cables are all OK and nobody touches them. We turn the PCs off after work, but not the UPSes. APC services on the PCs work fine. But after every few days of normal operation, UPSes loose communication with PCBE.

Refresh in PCBE console doesn't help. Restart of APC services doesn't help. Changing USB cable and/or port doesn't help. Sometimes (rarely) they do re-establish communication all by themselves (without any action from our side) after quite some time, but that seems to be out of our control.

In most cases, it helps when we turn the affected UPS off and back on. But sometimes we must perform the "brain dead" reset. We have the same issue on all UPSes and it re-occurs quite often. I repeat, nobody disconnects and reconnects USB cables, nobody changes services, nobody touches anything.

Is that a known issue? Would a change of UPS firmware help? Would a change of PCBE version help?

Thanks and best regards.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:56 AM . Last Modified: ‎2024-03-15 06:09 AM

0 Likes
0
778
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:56 AM . Last Modified: ‎2024-03-15 06:09 AM

Hi Bill,

Unfortunately the problem is not solved - it just took them longer to fail... When I checked again after a few more days, 6 of the 7 were in lost state. Just one of 10 is still OK all the time from the USB power options change.

OS is Windows 10 Pro, 64-bit, version 10.0.17134.137, on all computers.

All computers are HP EliteDesk 800 G4 TWR. Some of them have i5 CPU and use built-in graphic adapter, and some i7 CPU and a stronger graphic card. No relation between CPU, graphic and UPS behavior.

PCBE Agent file version is 9.2.0.4 on all computers.

USBDeview sees the UPS even when PCBE Agent doesn't. I'm attaching full report of USBDeview on a PC whose agent doesn't see the UPS and on a PC whose agent does.

UPS firmware is 03.5, ID:1015. I couldn't find any info and/or update of SMT1500IC firmware online. The system is not and will not be connected to the Internet.

Thanks for your help and best regards.

See Answer In Context

Attachments
usbdeview-reports.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:56 AM . Last Modified: ‎2024-03-15 06:10 AM

0 Likes
0
778
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:56 AM . Last Modified: ‎2024-03-15 06:10 AM

Hi,

When PowerChute is communicating with the UPS properly open the control panel and go to power option. Click on change plan settings for the plan in use. Then click on change advanced power settings, USB settings, selective suspend settings and disable the setting/s. Click save changes to change the settings. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:56 AM . Last Modified: ‎2024-03-15 06:09 AM

0 Likes
0
778
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:56 AM . Last Modified: ‎2024-03-15 06:09 AM

Hi Bill, thanks for the idea! Just changed the setting on all PCs, I'll let you know after a few days if that helped. Best regards.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:56 AM . Last Modified: ‎2024-03-15 06:09 AM

0 Likes
0
778
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:56 AM . Last Modified: ‎2024-03-15 06:09 AM

Hi Bill, here's the situation 5 days after changing the setting. Out of 10 UPS units, 7 were OK. On the remaining 3, I had to perform brain dead reset again; on one of them, I even had to wait a number of minutes after the reset for UPS status to become Online.

Any other ideas? Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:56 AM . Last Modified: ‎2024-03-15 06:09 AM

0 Likes
0
778
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:56 AM . Last Modified: ‎2024-03-15 06:09 AM

The SMT UPS line has user upgradeable firmware. You might want to check and see if all of them are running the most recent release.

https://www.apc.com/us/en/faqs/FA164737/

The update will require turning the UPS off.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:56 AM . Last Modified: ‎2024-03-15 06:09 AM

0 Likes
0
778
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:56 AM . Last Modified: ‎2024-03-15 06:09 AM

Hi,

I am glad the issue is resolved with some of the unit. when this happens on the remaining 3 would you check the UPS status using USBDeview.exe? 

Np9nu%2FK4WgB%2FSUgErx3Xcw%3D%3D.pngNp9nu%2FK4WgB%2FSUgErx3Xcw%3D%3D.png

In the image you can see USBDeview.exe has discovered the UPS and is reporting the serial number. 

USBDeview.exe is a freeware that is available on line. I downloaded the app from nirsoft.net. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:56 AM . Last Modified: ‎2024-03-15 06:09 AM

0 Likes
0
778
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:56 AM . Last Modified: ‎2024-03-15 06:09 AM

Hi,

Would you please share what OS PCBE agent is running on and the model of the HP PCs. Also, are all of the systems HP?

Thanks,

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:56 AM . Last Modified: ‎2024-03-15 06:09 AM

0 Likes
0
779
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:56 AM . Last Modified: ‎2024-03-15 06:09 AM

Hi Bill,

Unfortunately the problem is not solved - it just took them longer to fail... When I checked again after a few more days, 6 of the 7 were in lost state. Just one of 10 is still OK all the time from the USB power options change.

OS is Windows 10 Pro, 64-bit, version 10.0.17134.137, on all computers.

All computers are HP EliteDesk 800 G4 TWR. Some of them have i5 CPU and use built-in graphic adapter, and some i7 CPU and a stronger graphic card. No relation between CPU, graphic and UPS behavior.

PCBE Agent file version is 9.2.0.4 on all computers.

USBDeview sees the UPS even when PCBE Agent doesn't. I'm attaching full report of USBDeview on a PC whose agent doesn't see the UPS and on a PC whose agent does.

UPS firmware is 03.5, ID:1015. I couldn't find any info and/or update of SMT1500IC firmware online. The system is not and will not be connected to the Internet.

Thanks for your help and best regards.

Attachments
usbdeview-reports.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of