Hi all,
We recently buy 3 x APC SMT750RM2UC, but one of them don't complete the battery charging process, just up to 98%. The other two units showed as fully charged in 6 hours more less. We tried replace the battery module with other one installed and charged by one of the other 2 units, but the same issue happened, the UPS show the battery as 98% charged (see attach) and this is an issue for us.
Thanks in advance for your assistance.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:57 AM . Last Modified: 2024-03-15 06:09 AM
If I am not mistaken, I believe the battery charge has to be at 100% to initiate a calibration cycle and, with his at 98%, it probably would not start the calibration.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:57 AM . Last Modified: 2024-03-15 06:09 AM
hi Carols,
If you have already cross tested the SMT750RM2UC with one of the batteries from the other systems and experienced the same behavior, it may be that the UPS run time requires calibration. I recommend performing the manual calibration instead of the one initiated form the UPS LCD display, please follow the second method described in this Kbase article.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:57 AM . Last Modified: 2024-03-15 06:09 AM
If I am not mistaken, I believe the battery charge has to be at 100% to initiate a calibration cycle and, with his at 98%, it probably would not start the calibration.