Vmin significant drop, Bypass not in range; high voltage

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Vmin significant drop, Bypass not in range; high voltage
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:47 AM . Last Modified: ‎2024-03-15 06:12 AM

0 Likes
4
1354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:47 AM . Last Modified: ‎2024-03-15 06:12 AM

Vmin significant drop, Bypass not in range; high voltage

HI 

I have Smart-UPS SRT 5000 and it reported Bypass not in range; 


In the data log i can see that Vmin significantly dropped at 02/02/2019 18:57:44. What could cause Vmin to drop like this ?Could this be a reason for bypass?  It is still ongoing issue, last time occurred on 02/14

Thank you

1 Critical Alarm Present
 - Bypass not in range ; either frequency or voltage.
UPS Input
Input Voltage: 247.2  VAC @  60.0  Hz
UPS Output
Output Voltage: 207.8  VAC @  59.9  Hz
Output VA: 9.7 %
Output Efficiency: load too low
Load Current: 2.5  Amps
Output Watts: 9.7 %
Output Energy Usage: 1170.67 kWh
Data Log 
  Smart-UPS SRT 5000
Date Time                    Vmin    Vmax    Vout   Iout %Wout %out FrqOut %Cap Vbat Tups 
 02/02/2019 20:37:59 243.13 247.16 207.81 2.44 9.44 9.51 60.00 100.00 217.03 +21.00 
 02/02/2019 20:27:59 246.20 247.22 207.81 2.44 9.67 9.61 59.95 100.00 217.22 +21.00 
 02/02/2019 20:17:59 246.27 247.06 207.80 2.50 9.61 9.66 59.95 100.00 217.13 +21.00 
 02/02/2019 20:07:59 246.28 247.05 207.83 2.41 9.42 9.31 59.94 100.00 217.22 +21.00 
 02/02/2019 19:57:59 246.23 247.06 207.84 2.47 9.46 9.28 60.00 100.00 217.25 +21.00 
 02/02/2019 19:47:59 241.55 247.02 207.81 2.50 9.66 9.64 60.00 100.00 217.25 +21.00 
 02/02/2019 19:37:59 246.00 246.72 207.80 2.53 9.55 9.64 60.00 100.00 217.38 +21.00 
 02/02/2019 19:27:44 246.05 246.72 207.80 2.44 9.38 9.37 60.00 100.00 217.72 +21.00 
 02/02/2019 19:17:44 245.73 246.77 207.81 2.50 9.44 9.70 60.00 100.00 217.75 +21.00 
 02/02/2019 19:07:44 222.42 246.91 207.78 2.50 9.56 9.65 60.00 100.00 217.69 +21.00 
 02/02/2019 18:57:44 166.64 246.91 207.80 2.44 9.64 9.54 60.00 100.00 217.72 +21.00 
 02/02/2019 18:47:44 244.59 245.41 207.78 2.50 9.52 9.51 59.94 100.00 217.72 +21.00 
02/02/2019 10:37:41 245.63 246.55 207.80 2.50 9.44 9.65 60.00 100.00 217.81 +21.00 
 02/02/2019 10:27:41 245.56 246.55 207.83 2.50 9.61 9.58 59.95 100.00 217.09 +21.00 
 02/02/2019 10:17:41 245.17 246.36 207.83 2.47 9.43 9.56 60.00 100.00 216.47 +21.00 
Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:48 AM . Last Modified: ‎2024-03-15 06:11 AM

0 Likes
0
1354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:48 AM . Last Modified: ‎2024-03-15 06:11 AM

Thank you Liam. 

I think at this point my problem has been solved. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:47 AM . Last Modified: ‎2024-03-15 06:12 AM

0 Likes
0
1354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:47 AM . Last Modified: ‎2024-03-15 06:12 AM

Hi Eduard - 

Yes, these voltage drops would be the cause of your "Bypass not in range" alerts. This is in reference to the input power to the UPS, so you might have to speak to an electrician or your Utility company to know the exact cause of the sags. You can adjust the acceptable bypass range via the network management card. Go to the Configuration menu and then select "Power Options". 

Yk5swsbbUBiiLEUa0VGYFw%3D%3D.pngYk5swsbbUBiiLEUa0VGYFw%3D%3D.png

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:47 AM . Last Modified: ‎2024-03-15 06:12 AM

0 Likes
0
1354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:47 AM . Last Modified: ‎2024-03-15 06:12 AM

HI Liam

Thank you for a quick reply. I appreciate your time.

I will go ahead and change lower bypass voltage and talk to an electrician.

Do you think input voltage and output voltage settings are not a problem in this case? I wanted to change rated output, but only value there  is 208/240 and Output upper limit is only 235, not sure if this might cause any problems.

UPS Input
Input Voltage: 247.2  VAC @  60.0  Hz
UPS Output
Output Voltage: 207.8  VAC @  59.9  Hz
Output VA: 9.7 %
Output Efficiency: load too low

Again thank you for your help.
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:47 AM . Last Modified: ‎2024-03-15 06:12 AM

0 Likes
0
1354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:47 AM . Last Modified: ‎2024-03-15 06:12 AM

Yes, you will definitely get improved performance by setting the output to match the nominal input. In this case that would be 240v. You have to turn off the UPS output in order to make this change.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:48 AM . Last Modified: ‎2024-03-15 06:11 AM

0 Likes
0
1355
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:48 AM . Last Modified: ‎2024-03-15 06:11 AM

Thank you Liam. 

I think at this point my problem has been solved. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of