I have a APC Smart-UPS RT 2000 and the fault red led "X" is blinking together with two LEDs of the batteries.
Starting from the bottom are the second and third, as shown in the picture.
All 3 leds flash together and slowly.
What can it be ?
Thanks in advance. Giovanni
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:48 AM . Last Modified: 2024-03-15 06:11 AM
Thanks Giovanni. On that model this would indicate a "DC/DC Converter Fault".
You can try "brain deading" the unit by turning it off, disconnecting the battery, and unplugging it from the wall. If this does not clear the fault, or if the fault returns, I would recommend replacing the UPS. This unit is over 10 years old, which is a pretty typical life span.
Thanks
Liam
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:48 AM . Last Modified: 2024-03-15 06:11 AM
Hi Giovanni -
Can I get the exact model and serial number of your unit? It will be on a small white sticker under the front cover.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:48 AM . Last Modified: 2024-03-15 06:11 AM
Hi Liam,
The model number is: SURT2000XL I
The Serial Number is: JS0823011887
Regards
Giovanni
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:48 AM . Last Modified: 2024-03-15 06:11 AM
Thanks Giovanni. On that model this would indicate a "DC/DC Converter Fault".