Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
Options
  • Mark all as New
  • Mark all as Read
  • Float this item to the top
  • Subscribe
  • Bookmark
  • Invite a Friend
  • Threaded format
  • Linear Format
  • Sort by Topic Start Date
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Labels
Top Labels
  • Alphabetical
  • Smart-UPS & Symmetra LX | RM 4,611
  • UPS Management Devices & PowerChute Software 2,913
  • Racks, Rack Accessories, & Cooling 955
  • Data Center & Facility 3 Phase UPS 605
  • General Questions & Suggestions 240
  • Getting Started 166
  • Datacenter UPS 131
  • Server Room & Data Center Design Best Practices 106
  • Smart-UPS & Symmetra LX-RM 97
  • Other Environmental Monitoring Products & Questions 48
  • Business Power UPS 36
  • Datacenter Racks & Cooling 28
  • Rack Accessories & Cooling 16
  • Business Power Software & NMC 15
  • Home & Office - UPS & Software 15
  • Datacenter Accessories 15
  • Datacenter Netbotz & Monitoring 9
  • Network Management Card 6
  • Data Center Expert 6
  • Racks 6
  • power monitoring expert 5
  • IT Expert 5
  • Data Center Operation 4
  • Back-UPS & Surge Protectors 3
  • DCIM Support 2
  • apc 2
  • firmware 2
  • UPS 2
  • Home & Office - Accessories 2
  • Product Feedback 2
  • UPS Network Management Card 2
  • SMARTCONNECT 2
  • NetBotz 2
  • EcoStruxure IT Design CFD 1
  • Smart-750 1
  • Smart Design & Engineering 1
  • srt5000 1
  • detected 1
  • AP9210 1
  • Legacy Gateways & Energy Servers 1
  • symmetra 1
  • AP9619 1
  • 240v 1
  • spit phase 1
  • Certicate 1
  • AP7750A 1
  • Datacenter Forum 1
  • managedservices 1
  • dedicatedserver 1
  • managedserver 1
  • Electrical Calculation Tools 1
  • Tips and ideas 1
  • Building Operations 1
  • DDF 1
  • IT Advisor 1
  • Battery life 1
  • Safety 1
  • ssl 1
  • SERVER 1
  • Previous
  • 1 of 6
  • Next
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All
Related Products
Thumbnail of EcoStruxure™ IT SmartConnect
Schneider Electric
EcoStruxure™ IT SmartConnect
32
Thumbnail of Smart-UPS
Schneider Electric
Smart-UPS
29
Thumbnail of Uninterruptible Power Supply (UPS)
Schneider Electric
Uninterruptible Power Supply (UPS)
25
Load more

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

APC UPS Data Center & Enterprise Solutions Forum

Start a Topic
  • All
  • Solved
  • Unsolved
  • Unanswered
Solved
BillP
Administrator BillP Administrator

Inverter fault in SURT8000XLI - please for assistance

Dear fellows,we are operating 36 SURT8000xli in 36 different locations. During the warranty we have exchanged 16 of them with inverter fault. Could you please advise what is the problem?The UPSs feed n...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
1509 0 3
Latest Reply: BillP

Solved
Anonymous user
Anonymous user

I have a feeling that my SUA1000uxi's charger is not working or is fai...

My APC SmartUps 1000 contains (2) 12v batteries. The voltage across the pair of batteries when charging is 24V while plugged into the socket. Does this mean the charger is not working properly in the U...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
806 0 1
Latest Reply: BillP

Solved
legacy777_apc
Crewman legacy777_apc

Problems with SU1400NET changing to AC Power

Hi,I have an APC SU1400NET that I've had probably since about 2007. It's worked without any issues over the years. About a month or so ago I got a notification from it that the battery needed to be r...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
1874 0 8
Latest Reply: BillP

Solved
Anonymous user
Anonymous user

PowerView RM / AP9215RM / Symmetra RM Display Constant Reset

Hello all,I have a Symmetra RM that's been running fine with out any issue for quite some time.All of a sudden the AP9215RM display seems to have decided to emit a semi-long BEEP all the lights come on...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
2525 0 3
Latest Reply: Anonymous user

Solved
Anonymous user
Anonymous user

SMC1500I not registering load?

Hi there,I've just received a new unit under an RMA (thanks APC!) but I noticed something odd. I'm running a Synology DS212+ as a small SMB server hooked up behind it. I've also attached my workstation...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
715 0 1
Latest Reply: BillP

Solved
BillP
Administrator BillP Administrator

Hyper V 2012 running in Cluster UPS Shutdown

HiNeed some assistance or just some examples of what has been done.We are running Hyper V in a HA cluster, and I need to configure the UPS software for shutdown of the Guest and the host systems in a g...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
1813 0 5
Latest Reply: BillP

Solved
Anonymous user
Anonymous user

Strange temperature readings from SmartUPS 1400xl

I'm getting what I would consider to be odd temperature readings from one of a pair of 1400xl units powering a couple of servers.Basic setup:2 SmartUPS 1400XL each with 2 external battery packs (SU24R2...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
1924 0 5
Latest Reply: BillP

Solved
Anonymous user
Anonymous user

Using an AP9631 with a new SMT1500RM2U

I have used my AP9631 Network Management card with environmental probe for several years now. The UPS that it was installed on, was a SmartUPS 750, which has failed and has been replaced. The new UPS i...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
3156 0 7
Latest Reply: Anonymous user

Solved
Anonymous user
Anonymous user

Four Post Rack Mount Question

Hello,I am wondering if someone can confirm whether the SU032A mouting kit can be successfully used to mount an SMT2200R2X180 in a four post rack such as the Dell PowerEdge 4220 Rack.Thank You
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
569 0 1
Latest Reply: BillP

Solved
Anonymous user
Anonymous user

UPS Battery Resistance

Dear All,Our company sold a mount of UPS SUA1500I to our customer about 1.5 year ago.Last week, they checked the resistance of those UPS and they saw the resistance is bigger more than 30% from the sta...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
3638 0 10
Latest Reply: Anonymous user

Solved
toups_apc
Crewman toups_apc

SURTD5000 no leds, won't start, batteries good

I have a SURTD5000 that was acquired used. Recently, I shut it down and disconnected it for two months. I hooked it back up and now it won't start. The two battery packs each read 102 Volts (for a t...
APC UPS, Critical Power, Cooling and Racks icon_circle APC UPS Data Center & Enterprise Solutions Forum
1653 0 5
Latest Reply: toups_apc

  • « Previous
    • 1
    • …
    • 649
    • 650
    • 651
    • …
    • 1078
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore