Hyper V 2012 running in Cluster UPS Shutdown

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Hyper V 2012 running in Cluster UPS Shutdown
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:01 AM . Last Modified: ‎2024-03-12 04:49 AM

0 Likes
5
1414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:01 AM . Last Modified: ‎2024-03-12 04:49 AM

Hyper V 2012 running in Cluster UPS Shutdown

Hi

Need some assistance or just some examples of what has been done.

We are running Hyper V in a HA cluster, and I need to configure the UPS software for shutdown of the Guest and the host systems in a given time frame.

I have seen some guys, just use PCNS to power down the Host and then the VMs will power them self down if setup correctly, what I am not to sure is in HA will the VM not try and migrate when the host go down, and then mid migration the second host also shut down so then there is a issue.

All I can think is run the PCNS on each server and let them shutdown after X min, and then the Host after X=X min.

Please share what have been done and what can be done

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:01 AM . Last Modified: ‎2024-03-12 04:49 AM

0 Likes
0
1413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:01 AM . Last Modified: ‎2024-03-12 04:49 AM

Hi Jano,

It is expected to be released mid December. But I don't have the official release date as of yet.

Regards,

B

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:01 AM . Last Modified: ‎2024-03-12 04:49 AM

0 Likes
0
1413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:01 AM . Last Modified: ‎2024-03-12 04:49 AM

Hi,

WE do not support Hyper-V in a cluster configuration at this time. WE will be supporting that configuration when we release PowerChute Network Shutdown version 3.1. We hope to release version 3.1 to the public in November.

In the mean time people that are running PowerChute on Hyper-V are installing the software on each host and the host/s are responsible for powering down the VMs. We have knowledge base document FA159689 that discusses the shut down of the VMs.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:01 AM . Last Modified: ‎2024-03-12 04:49 AM

0 Likes
0
1413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:01 AM . Last Modified: ‎2024-03-12 04:49 AM

would be able to share how the Cluster supporting Power chute would be different?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:01 AM . Last Modified: ‎2024-03-12 04:49 AM

0 Likes
0
1413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:01 AM . Last Modified: ‎2024-03-12 04:49 AM

Powershell scripts will be used to perform live migration of VMs and graceful VM shutdown. You will be able to enable VM migration and VM shutdown/startup options using the PowerChute Setup wizard or on the shutdown settingspage. Migration will only be supported for VMs running on Hyper-V hosts that are part of the same failover cluster and the VMs must have high availability configured.

If you enable virtual machine migration, you will use the duration field in PowerChute to set the time allowed for the VMs to migrate to another healthy host in the cluster. VMs will not be migrated to hosts that are powered off, in a disconnected state, in maintenance mode or affected by a UPS critical event. By default, PowerChute will migrate VMs to any available host in the same cluster. Once the delay set in the duration field PowerChute will command the host/s to power down.


Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:01 AM . Last Modified: ‎2024-03-12 04:49 AM

0 Likes
0
1413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:01 AM . Last Modified: ‎2024-03-12 04:49 AM

Hi,

Any news about PCNS 3.1 release time?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:01 AM . Last Modified: ‎2024-03-12 04:49 AM

0 Likes
0
1414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:01 AM . Last Modified: ‎2024-03-12 04:49 AM

Hi Jano,

It is expected to be released mid December. But I don't have the official release date as of yet.

Regards,

B

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of