Problems with SU1400NET changing to AC Power

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Problems with SU1400NET changing to AC Power
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
legacy777_apc
Crewman legacy777_apc
Crewman

Posted: ‎2021-06-29 07:01 AM . Last Modified: ‎2024-03-12 04:48 AM

0 Likes
8
1124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:01 AM . Last Modified: ‎2024-03-12 04:48 AM

Problems with SU1400NET changing to AC Power

Hi,

I have an APC SU1400NET that I've had probably since about 2007.  It's worked without any issues over the years.  About a month or so ago I got a notification from it that the battery needed to be replaced (this battery was the second battery I had installed in it).  So I ordered a new battery and during the time the battery was being shipped, one day I noticed an odd smell and discovered that the UPS was very hot and the fan was running.  I shutdown the server, unplugged the UPS from AC power and disconnected the jumper in the back. I used an external fan to help cool everything.  The old battery was bulged, but had not leaked/ruptured.

Once I got the new battery I installed the battery to see if everything was working, the UPS came up and everything appeared ok.  However, I didn't reconnect the server at this time and the UPS sat for a 2-3 weeks.  Now when I try to start up the UPS, it appears to go through the self test process, but when it trys to switch to AC power, it doesn't switch and the AC power light just flashes.

I've taken two videos of the startup.  The first was earlier this week, and the second is after trying to brain dead the UPS.  The only difference, other than the case being off since the plastic clips broke that hold the circuit board in, is that it beeps once turned on.  I'm not sure if that's related to the battery juice draining.

1st Video - http://youtu.be/yYGRp5thwS4

2nd Vido - http://youtu.be/FP8Gra5h-As

I've tried the test mentioned in this link, http://forums.apc.com/message/30266#30266 and I can get it to power up on the battery.  However, when I plug it in to the outlet, it acts the same way as in the videos.

The last post in this thread, http://forums.apc.com/message/48533#48533 mentions that with the UPS plugged in, but no battery it should read 27-28 volts DC, and mine does not.

Any thoughts, comments, or suggestions are appreciated.

Thanks

Josh

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:02 AM . Last Modified: ‎2024-03-12 04:48 AM

0 Likes
0
1122
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:02 AM . Last Modified: ‎2024-03-12 04:48 AM

Yes, that can be true about lead acid batteries, typically though that type of thing happens to older batteries and after many deep discharges. Let me know if you have any other questions.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
legacy777_apc
Crewman legacy777_apc
Crewman

Posted: ‎2021-06-29 07:01 AM . Last Modified: ‎2024-03-12 04:48 AM

0 Likes
0
1122
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:01 AM . Last Modified: ‎2024-03-12 04:48 AM

Hi,

I have an APC SU1400NET that I've had probably since about 2007.  It's worked without any issues over the years.  About a month or so ago I got a notification from it that the battery needed to be replaced (this battery was the second battery I had installed in it).  So I ordered a new battery and during the time the battery was being shipped, one day I noticed an odd smell and discovered that the UPS was very hot and the fan was running.  I shutdown the server, unplugged the UPS from AC power and disconnected the jumper in the back. I used an external fan to help cool everything.  The old battery was bulged, but had not leaked/ruptured.

Once I got the new battery I installed the battery to see if everything was working, the UPS came up and everything appeared ok.  However, I didn't reconnect the server at this time and the UPS sat for a 2-3 weeks.  Now when I try to start up the UPS, it appears to go through the self test process, but when it trys to switch to AC power, it doesn't switch and the AC power light just flashes.

I've taken two videos of the startup.  The first was earlier this week, and the second is after trying to brain dead the UPS.  The only difference, other than the case being off since the plastic clips broke that hold the circuit board in, is that it beeps once turned on.  I'm not sure if that's related to the battery juice draining.

1st Video - http://youtu.be/yYGRp5thwS4

2nd Vido - http://youtu.be/FP8Gra5h-As

I've tried the test mentioned in this link, http://forums.apc.com/message/30266#30266 and I can get it to power up on the battery.  However, when I plug it in to the outlet, it acts the same way as in the videos.

The last post in this thread, http://forums.apc.com/message/48533#48533 mentions that with the UPS plugged in, but no battery it should read 27-28 volts DC, and mine does not.

Any thoughts, comments, or suggestions are appreciated.

Thanks

Josh

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:01 AM . Last Modified: ‎2024-03-12 04:48 AM

0 Likes
0
1122
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:01 AM . Last Modified: ‎2024-03-12 04:48 AM

I don't suppose you have PowerChute Business Edition configured or a Network Management Card installed to see if it reports anything i.e. output relay failure or similar?

Oh and thank you for the videos smile

Reply

Link copied. Please paste this link to share this article on your social media post.

legacy777_apc
Crewman legacy777_apc
Crewman

Posted: ‎2021-06-29 07:01 AM . Last Modified: ‎2024-03-12 04:48 AM

0 Likes
0
1122
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:01 AM . Last Modified: ‎2024-03-12 04:48 AM

I do have PowerChute Business edition setup and my memory is failing me on exactly what it said.  I'll try and take some screen captures this evening of the software and what it's saying.

Thanks

Josh

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:01 AM . Last Modified: ‎2024-03-12 04:48 AM

0 Likes
0
1121
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:01 AM . Last Modified: ‎2024-03-12 04:48 AM

Alrighty. Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:02 AM . Last Modified: ‎2024-03-12 04:48 AM

0 Likes
0
1121
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:02 AM . Last Modified: ‎2024-03-12 04:48 AM

I had someone else check the video and they said it appears to be an incomplete self test due to internal failure and it is hard to say what the fault could be for sure because these older models don't have much in the way of error reporting.

My first thought is if you're interested in getting it repaired, CoastTec is our authorized service provider.

Reply

Link copied. Please paste this link to share this article on your social media post.

legacy777_apc
Crewman legacy777_apc
Crewman

Posted: ‎2021-06-29 07:02 AM . Last Modified: ‎2024-03-12 04:48 AM

0 Likes
0
1122
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:02 AM . Last Modified: ‎2024-03-12 04:48 AM

Angela,

I hooked up the Powerchute communications cable and when I turned the UPS on this time I got a different response, it made a buzzing sound and then all the lights came on.  However, it did leave an error code in the Powerchute software indicating a main relay fault.

Here is the video from this evening:

http://youtu.be/Y2K_l8uB0xE

Attached is the screen capture from the Powerchute software

Does this sound like the main relay is the culprit, and is it something I can replace myself if I order the parts?  I am comfortable taking apart the UPS and working on it.

Thanks

Josh

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

legacy777_apc
Crewman legacy777_apc
Crewman

Posted: ‎2021-06-29 07:02 AM . Last Modified: ‎2024-03-12 04:48 AM

0 Likes
0
1122
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:02 AM . Last Modified: ‎2024-03-12 04:48 AM

Angela,


Thanks for the iniput, I really appreciate it!  When I get some time I may try and look at it a little closer to see what I can see.

My concern now is that the new battery I bought has been drained and I've heard/been told that if lead-acid batteries are drained too far for too long, they never come back to an original charge.  My only thoughts are to separate the batteries and put them on a standard 12v battery trickle charger.

Josh

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:02 AM . Last Modified: ‎2024-03-12 04:48 AM

0 Likes
0
1123
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:02 AM . Last Modified: ‎2024-03-12 04:48 AM

Yes, that can be true about lead acid batteries, typically though that type of thing happens to older batteries and after many deep discharges. Let me know if you have any other questions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of