Is the EM4300 wireless meter only valid with 3P4W circuits?
If not can someone direct me to a wiring diagram?
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Installation guide can be found here
User Guide can be found here.
This meter derives its control power from the L*N connection. So the EM4300 cannot support loads without a N.

Posted: 2016-07-15 05:05 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Clear on the control power requirement for a Neutral. What about single phase circuits 1P2W in circuits closer to final distribution?
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
It does support single phase , But It still has the have a N .

Posted: 2016-07-15 06:46 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Can you direct me to this in the documentation?
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
The documentation is in the first post, I linked the user guide and the installation guide.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
The OP mentioned single phase connection. We have an application for a 1PH3W, same as typical residential 220-240V systems. Can the EM4300 do this?