Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PM8000

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM8000
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Andy_Hubert
Andy_Hubert Contributor
Contributor

Posted: ‎2016-11-15 11:45 PM

0 Likes
8
4474
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-11-15 11:45 PM

PM8000

Hi,

I was on a site yesterday where we have recently installed a number of PM8000 meters, and I discovered something that I didn't know about

There are a couple of modules that will give you a Sag and Swell alarm on Current, based on a nominal value within the framework of the meters

This nominal value is set to 10Amps, and in my case I got several thousand alarms from the 5 meters in a week!

This obviously fills the database very quickly, mine was growing at a stupid rate, as the meters were reporting this alarm several times a second!!

To get around this search for the sag/swell module, and on the same page there are two new modules called current sag and current swell.

These can either be set up to suit, or in my case disabled due to the nature of the load.

I wonder if these could be set to disabled out of the factory, rather than enabled.

Thanks

Andy

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Daniel_Brandao
Daniel_Brandao Mentor
Mentor

Posted: ‎2017-06-29 10:55 PM

1 Like
1
4346
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-06-29 10:55 PM

This will be addressed in the next firmware release and the sag / well for current won't be enabled by default anymore.

See Answer In Context

Reply
Replies 8
sesa64419
sesa64419 Leader
Leader

Posted: ‎2016-11-16 07:17 AM

0 Likes
2
4346
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-11-16 07:17 AM

Hi Andy

There is a another way to deal with unwanted alarms.

Go to your meter's Display, access the Setup menu and select Alarm.

Scroll down to the current sag/swell alarms, select the first one and click the gear icon. Press the two center buttons to disable.

**This disables the module and its functions. If you want to still have the module operate, but without making an alarm, go to ION Setup and select Alarming.

Set the priority to None, that means the alarm will not be displayed nor will it show up in the event log.

Disabling alarms through the display is described on page  124 of the PM8000 user manual (7EN02-0336-01)

Configuring your alarms using ION Setup is described on pages 126 through 129, including modifying nominal values and configuring setpoint and sag/swell learning.

To get the latest PM8000 user manual, go to www.schneider-electric.com and search "pm8000 user manual" or "7EN02-0336"

Cheers,

Alana

Reply
ShaunTaylor
ShaunTaylor Contributor
Contributor

Posted: ‎2017-01-12 02:57 AM

1 Like
1
4346
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-01-12 02:57 AM

Hi Alana,

Thanks for the above, however I'm also on a site with around 100 of these meters and when you walk to a switchroom, all are flashing in alarm state which you can imagine customers are not happy about. It's not practical to have to change each individual alarm on the meter display or ION setup due to the time that would take.

Could a firmware update be released to resolve this unwanted feature? The user can always configure the alarms they actually want at a later date.

Regards

Shaun

Reply
sesa64419
sesa64419 Leader
Leader

Posted: ‎2017-01-12 09:28 AM

2 Likes
0
4346
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-01-12 09:28 AM

Hi Shaun

Yes, I can guess that is not a desirable instance. And although certainly you could fix the framework on one device and then paste it to the other meters, that isn't an ideal large-scale solution either. For firmware requests, I recommend contacting Daniel Brandao as the offer manager for the PM8000, and I have sent him the link to this conversation thread.

cheers,

Alana

Reply
Arneil_Dalope
Arneil_Dalope
Mentor

Posted: ‎2017-01-12 08:25 PM

3 Likes
0
4346
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-01-12 08:25 PM

We have the same issue that is why we raised this topic\\What is Current Sag/Swell and its application? . What we have done is to disable this feature on the meters  individually so it will not flood the database with undesired records. We would certainly suggest that this feature be disabled by default. 

Regards,
Arneil

Reply
Andy_Hubert
Andy_Hubert Contributor
Contributor

Posted: ‎2017-06-16 01:32 AM

1 Like
0
4346
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-06-16 01:32 AM

I had another occurence of this yesterday, my waveformlog2 table in the database was 45,414,104 rows!

Most customers are going to install these meters without looking at the alarm setup, so having this alarm enabled by default is in my opinion the wrong way to do it.

This caused the customer database to fill the disk it was on, and because the server was only sized for 14 devices, I have nowhere to put a log file that will grow to the same size as the database when I try to trim or archive these records.

The biggest drive is 199GB the databse, due to the alarms is 180GB, and the next biggest drive is only 19.99GB.

All of this has been caused by only 4 PM8000 meters, I would not like to think what this would do to a system with 200!

Regards

Andy

Reply
Tom_Stevenson
Tom_Stevenson Champion
Champion

Posted: ‎2017-06-16 08:09 AM

0 Likes
0
4346
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-06-16 08:09 AM

Daniel Brandao Neto Cliff Schubert 

Reply
Daniel_Brandao
Daniel_Brandao Mentor
Mentor

Posted: ‎2017-06-29 10:55 PM

1 Like
1
4346
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-06-29 10:55 PM

This will be addressed in the next firmware release and the sag / well for current won't be enabled by default anymore.

Reply
Andy_Hubert
Andy_Hubert Contributor
Contributor

Posted: ‎2017-07-27 02:23 AM

0 Likes
0
4346
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-07-27 02:23 AM

Hi Daniel,

I have another one for you, the same site again, this time the nominal voltage out of the box is set to 120, the meter is on a system that is 11,000V, I get hundreds, if not thousands of waveforms caused by the voltage swell alarm.

Can this also be disabled by default??

Thanks

Andy

Reply

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore