Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Metering

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Metering
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Blondie
Blondie
Cadet

Posted: ‎2025-02-07 02:45 AM

0 Likes
5
351
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-07 02:45 AM

Metering

Hello

I am looking for advice on the metering system RA we have on site and the reason why we are out by 6/7%. of total PM8000 vs ION 7650

We have a ION 7650 on our MV main income and 13 transformers with PM 8000 on the LV side.

Over 24hr ION 7650 = 42153kWh & the total 13 PM 8000 = 39461kWh = 2692kWh Difference. 

I know we will have small loses in the transformers and maybe the system but I don't think it would be this  much.

Each transformer has its own PF and this is good and well maintained, to be honest most of them would not be called in. I am told that all the meters were all set up correctly at the time on installation 8/9 years ago.

The few questions I have is, Do The PM8000 record the PF load in total energy used/ is this down to loses in the whole system/ is it down to metering issues.

Any Help would be much  appreciated.

Thanks 

 

 

 

 

Labels
  • Labels:
  • PM8000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2025-03-31 05:24 PM

0 Likes
0
97
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-03-31 05:24 PM

Hello Blondie,

 

Given we have not heard back from you in a long time we will mark this post as solved, if you have questions or follow up please feel free to respond.

 

Regards,

Charles 

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 5
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
Captain

Posted: ‎2025-02-07 09:55 AM

0 Likes
0
321
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-07 09:55 AM

Hi @Blondie 

 

Yes, by default, PF is recorded every 15 minutes under 'Historic Average' Data Recorder.

Mehran_Mehrnia_0-1738950880325.png

 

Regarding 6.7% Energy reading difference between main income and 13 transformers outgoing feeders, if all parameters such as CT/PT ratio, etc, in all meters have been set accordingly, I am wondering if 13 times of phase shift caused by transformers(on average 0.5% per each transformer) could cause such difference that can be checked by PF measured by ION7650 and PM8000 meters.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2025-02-07 09:59 AM . Last Modified: ‎2025-02-07 10:00 AM

0 Likes
0
320
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-07 09:59 AM

Hello @Blondie ,

 

There are many elements to include in a topic like this. First that comes to mind is tolerances of elements used. There is not just the PTs and CT, there is also the meter as well. CTs are typically the single largest tolerance however the construction of the CT can make a difference, as can the placement of the conductor though the CT. Is conductor centered in the CT, is the CTs spaced far enough apart to not provide interference etc.?

Another factor to consider is are all meters synced to the same time source. If one meter is way ahead of other meters in time the logging intervals will not be the same.

Another element that could come into play is settings on the meters. Could one or more meters have incorrect settings that can account for the differences. One item you could investigate, assuming meters are all time synced, is calculating the energy per interval for the main meter and all sub meters. If you plot the difference between total and summation of sub meters, then plot the interval of each sub meter to this difference oy might see trends where if one meter goes up, the difference also goes up, or if a meter goes down the difference goes down. If one or 2 meters have a strong correlation to the difference those would be meters I would want to check first.

 

Do you have 15 minute Energy from the main meter and the sub meters?

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2025-02-25 09:26 AM

0 Likes
0
226
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-25 09:26 AM

Hello @Blondie ,

How has the investigation be going? Do you still need assistance?

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2025-03-16 03:15 PM

0 Likes
0
164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-03-16 03:15 PM

Hello @Blondie ,

 

Any news on the investigation?

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2025-03-31 05:24 PM

0 Likes
0
98
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-03-31 05:24 PM

Hello Blondie,

 

Given we have not heard back from you in a long time we will mark this post as solved, if you have questions or follow up please feel free to respond.

 

Regards,

Charles 

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of