Good day
please help
I have two types of systems in place, which have different channel and CT requirement to be configured.
The following is setup thus far:
Setup requirements needed:
The meters monitoring between the two meters have different strips and CT’s counts per strip.
I have noted that the manual suggests that Modbus register 6 must be changed to 2 which is =sequential 2.
As we are using Bacnet as our communications, how do we access these parameters to enable different configurations?
Can you assist?
Link copied. Please paste this link to share this article on your social media post.
Hello @Gladwin ,
The meters can support communicating with multiple protocols. The BCPM unfortunatlly cannot be configured via the BACnet protocol. You will need to use a modbus client such as tester.exe (https://www.se.com/ca/en/faqs/FA180037/) to configure your device.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @Gladwin ,
The meters can support communicating with multiple protocols. The BCPM unfortunatlly cannot be configured via the BACnet protocol. You will need to use a modbus client such as tester.exe (https://www.se.com/ca/en/faqs/FA180037/) to configure your device.
Regards,
Charles