Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Testing of circuit breakers

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Testing of circuit breakers
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
80
J_Travostino
Sisko J_Travostino Sisko
70
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Expert on Demand for Standards & Regulations

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Start a Topic
Solved
jparasu
jparasu
Cadet

Posted: ‎2024-12-17 11:14 AM

0 Likes
2
1676
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-17 11:14 AM

Testing of circuit breakers

Hello everyone,

 

We have following circuit breakers in our electrical distribution, a vendor has recommended that we are required to perform breaker testing (Primary injection and secondary injection) as per NFPA 70E, which requires the facility to be shutdown for 1 day. Would like get the input of the experts here, is it really mandatory to perform these tests, we currently do Infrared test once an year. Would like to confirm if there any safety mandate which warrants us to do this detailed testing. 

 

Breakers used

PJ1000A 6.0A

PG400

RG1600 6.0A

LJ400

RG200 6.0A

PG600

Labels
  • Labels:
  • India Power Distribution & Digital
  • Safety - Electrical Fire Prevention
  • Safety - People Safety
  • Tags:
  • LV breaker testing
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Gregoire_Brun
Commander Gregoire_Brun Commander
Commander

Posted: ‎2024-12-19 01:57 AM

2 Likes
0
1633
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-19 01:57 AM

hello @jparasu 

after some discution with some other experts.

 

The only MCCB testing requirements for NFPA 70E are in Article 225 and only requires tests after a fault based on manufacturer’s instructions .  There are electrical testing requirement in NFPA 70B Section 15.3.5, but does not tell the user what method of testing to use. 

The NEC also has performance testing for any 1200A and above breaker where section 240.87 is required to verify arc energy reduction requirements are met.  SE’s position on testing  is secondary current injection testing, Commissioning Software testing, and primary current injection, in that order.

 

Manufacturer’s recommendations from document 0613IB1202 (recomendations are same on compact NSx MCCB IEC). 

Secondary injections every 2 years. (secondary injection to test the tripping, and low current level primary just to check that display meters current which verifies chain from CTs to trip unit connections).

 

Some kind of primary injection testing every 5 years to check the tripping chain. 

 

 

Gregoire_Brun_0-1734601804137.png

Gregoire_Brun_1-1734601852631.png

Gregoire_Brun_2-1734601868155.png

Best regards

 

 

 

 

Gregoire Brun
Breaker Product Expert

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Manon_Chaboud
Commander Manon_Chaboud Commander
Commander

Posted: ‎2024-12-17 11:26 PM

0 Likes
0
1667
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-17 11:26 PM

Hello @jparasu, thank you for your post!

@Gregoire_Brun can you please advise @jparasu?

Thank you in advance!

Reply

Link copied. Please paste this link to share this article on your social media post.

Gregoire_Brun
Commander Gregoire_Brun Commander
Commander

Posted: ‎2024-12-19 01:57 AM

2 Likes
0
1634
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-19 01:57 AM

hello @jparasu 

after some discution with some other experts.

 

The only MCCB testing requirements for NFPA 70E are in Article 225 and only requires tests after a fault based on manufacturer’s instructions .  There are electrical testing requirement in NFPA 70B Section 15.3.5, but does not tell the user what method of testing to use. 

The NEC also has performance testing for any 1200A and above breaker where section 240.87 is required to verify arc energy reduction requirements are met.  SE’s position on testing  is secondary current injection testing, Commissioning Software testing, and primary current injection, in that order.

 

Manufacturer’s recommendations from document 0613IB1202 (recomendations are same on compact NSx MCCB IEC). 

Secondary injections every 2 years. (secondary injection to test the tripping, and low current level primary just to check that display meters current which verifies chain from CTs to trip unit connections).

 

Some kind of primary injection testing every 5 years to check the tripping chain. 

 

 

Gregoire_Brun_0-1734601804137.png

Gregoire_Brun_1-1734601852631.png

Gregoire_Brun_2-1734601868155.png

Best regards

 

 

 

 

Gregoire Brun
Breaker Product Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore