Problems installing Continuum

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Problems installing Continuum
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Chris_Asbury
    Chris_Asbury
  • sesa139513
    sesa139513
  • Dave_Shore
    Dave_Shore
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
7570 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Problems installing Continuum

Picard Product_Support
‎2018-09-07 08:32 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-07 11:26 PM

Issue

  • Problems installing Continuum
  • Continuum will not install correctly
  • SQL Express will not install correctly

Product Line

Andover Continuum

Environment

Continuum

Cause

Cyberstation fails to install or run correctly

Resolution

Continuum Cyberstation can normally be installed very quickly (usually less than half an hour) on a normal windows installation that fits within the Software and Firmware compatibility matrix for older versions of I/NET, Vista, Andover Continuum, Sa..., this would include SQL for a stand alone (Single User) installation.
The Continuum Cyberstation uses many Windows components and services, and runs many executable files and batch files within its normal operation.
We do not have a published list of services that Continuum requires to run since requirements vary depending on the site configuration. We obviously use Active Directory and .NET, RPC, MSMQ, SMNP, and all DCE services.

SQL Server Management Studio Express is a free down from Microsoft and is an excellent tool for checking the SQL install
Up to v1.94sp1 SQL2005 https://docs.microsoft.com/en-us/sql/ssms/download-sql-server-management-studio-ssms?view=sql-server...
v2.0 and beyond SQL2012 https://www.microsoft.com/en-us/download/details.aspx?id=35579

There are a few items that can interfere with the smooth installation or running of a Continuum Cyberstation

  1. Ensure the workstation PC is within the Software and Firmware compatibility matrix for older versions of I/NET, Vista, Andover Continuum, Sa... for the version being installed, especially Windows service packs and .NET framework versions.
  2. Ensure the minimum requirement for the workstation PC, is observed, as stated in the Cyberstation installation guide. Ensure the recommended requirement is observed, if the Cyberstation will be used for video or other more intense operations. 
  3. Local administrator accounts are required for some version of installation with passwords set. See How to create a local administrator log on in Windows.
  4. Automatic updates. See the individual installation guides, however, it is normally wise or even mandatory (depending on Continuum version) to leave them off, as updates include service packs and .NET framework updates that would take the installation off the Compatibility Matrix and could compromise the installation. There have also been other updates that have caused issues. See 5 below.
  5. MSXML6 Update
    • SQL Express install fails on MSXML 6
  6. Firewall & Anti virus issues. These should be disabled during installation.
    • Issues with starting Continuum after new installation (Anti-Virus and Firewalls)
    • Error when starting Continuum 1.9: Cannot find acc video recording service
    • Access denied errors when installing Continuum or Webclient
    • Crash of ACCDataServices on start up or running Continuum
    • Another example of antivirus interfering with Continuum install is getting Microsoft Visual V++ error when opening a pin point graphic, when the install is completed with AV "webRoot" enabled. 
  7. SQL2005 Express (1.82SA onwards) When creating the sa password ensure the password is tested in notepad before typing in Database Initialisation, as if the keyboard is not set up correctly, you may be using an illegal character (eg " rather than @, in this case you will need to uninstall SQL, before re-installing via Database Initialisation)
  8. Custom Windows Images - Some Windows Images installed on new PCs include modifications that interfere with the Cyberstation installation, always use a clean MS Windows if possible, as this avoid such issues.
    • HP Protect Tools - MFC error on Continuum startup or Continuum won't start on HP PC
  9. IT tampered Windows & domains. It is important to install Continuum with local Administrator rights as item 3, above, beware of PCs locked down by IT departments, the installation can be slow and difficult
  10. Error 1001, windows event log full.
    • Error 1001 when installing Cyberstation or Webclient
  11. Problems with MSMQ (MicroSoft Message Queue) can cause install problems
    • MSMQ errors and Continuum fails to start
    • MSMQ error starting Continuum. "There appears to be a problem with the configuration of this system....
    • MSMQ error message: "Appears to be a problem with configuration of system please check to make sure ...
  12. Trying to install CyberStation 1.9x.  It completes but then pops up 6 errors saying "Access denied"
    • "Access Denied" messages during a CyberStation 1.9x installation
  13. Microsoft Update issues see Windows updates and Continuum
  14. Continuum Version 1.93 Fails to install. IssueReceive AccDataservice errors on startup.
    Continuum Version 1.93 Fails to install
  15. For Windows 7 installs see Disabling administrator rights messages in Windows 7 OS and above (Also known as UAC / User Account ...
  16. If you see a Continuum install Error -  "Error, unable to open documentation list \misc\doclist.txt" then you are running the incorrect "setup.exe", you should install using the one in the Cyberstation root directory, not the one in the Continuum sub-directory.
  17. It has be found that Microsoft "Strong" passwords are required not only for the SQL sa password but also for Andover97 password, see Password requirements for Andover97 SQL Login for details
  18. For a v1.82 Stand Alone and beyond, if the install admin user has no password, it has been seen that the tasks (CS_Minute, CS_Distn and CS_hrly) are not always created, see Getting AccDataServices error with AlmUtil.dll error when closing Continuum
  19. If a Continuum re-install, on a LAN CyberStation is required (were some part or program has broken) then uninstall Continuum, then re-install. A workstation initialization may be required. Deleting the Continuum directory and clearing out Continuum from the registry may also be required (check for any local held graphics, .mnu files, etc. before deleting the Continuum directory)
  20. Seeing "Can not change directory to Continuum" see Cannot change directory to Continuum error during installation of Cyberstation
  21. Re-Installing Continuum is sometimes required, for example, an automatic update to the Antivirus software has been seen to stop listviews from working. The only way around this was to uninstall Continuum then re-install it. There are different levels to uninstalling possible, 1.Simple uninstall. 2. Uninstalled followed by removing the Continuum Directory and other .ini files. 3. Uninstalled followed by removing the Continuum Directory and other .ini files, followed by cleaning of the registry. 
  22. In a few more recent cases where Controllers will not come online (after testing for other errors) or where persistent MSMQ errors cannot be resolved, a complete re-install of the OS may be required to ensure a "clean" Windows OS is available.
  23. Uninstalling some Continuum required programs can cause issues, especially SQL. see Problem uninstalling software. The following method has been seen to work: Stop service, uninstall, delete folders, run CCleaner (or Revo) and clean registry, reboot, run CCleaner (or Revo) and clean registry, reboot, re-install SQL
  24. Shared Memory errors seen with 32b systems and v2.0SP1, see "Shared Memory" error on startup of Continuum
Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 4850
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore