Disabling administrator rights messages in Windows 7 OS and above

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Disabling administrator rights messages in Windows 7 OS and above
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3795 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Disabling administrator rights messages in Windows 7 OS and above

Picard Product_Support
‎2018-09-10 12:23 AM

Last Updated: Crewman ContentModerator ‎2025-09-01 03:38 AM

Issue

Software installation problems with Windows 7 OS and above

Configuration problems also known as UAC / User Account Control

These problems occur when you receive an error message stating that you do not have the correct administrative rights to continue.

Product Line

Andover Continuum, EcoStruxure Building Expert, EcoStruxure Building Operation, Satchwell MicroNet, Satchwell Sigma, TAC INET, TAC Vista

Environment

  • Windows 7
  • Windows 8 8.1
  • Windows 10
  • Server 2012

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance.

Cause

Windows 7 and above user administrator privilege settings (UAC)

Resolution

The solution to this issue is to turn off the user admin settings before the software is installed by following these instructions:

  1. Go to Start > Control Panel. Set the view to "small icons" to show all Control Panel icons
  2. Click on "User Accounts." Make sure that the account used for installing the software is a full admin user.
    On this page, click on "Change User Account Control settings", a slider bar that starts with "Never notify" up to "Always notify" by default will be set to "Notify me only when programs try to make changes to my computer"
  3. Set it to "Never notify." This will disable all the admin blocks that pop up in installing and configuring software
  4. Once set, restart the PC and then continue with your software installation and configuration
  5. Once all is installed and working, the feature may be turned back on if required.

Additional requirements for Windows server 2012 and Windows 10.

Please note: this process may open the "Windows 10 Firewall up"

For Windows Server 2012 and Windows 10, additional steps are required to disable User Account Control. Although the slider bar can be set to “Never Notify”, the User Account Control does not disable completely. The User Account Control can be disabled for any user by setting the system registry value “EnableLUA” to zero in the system registry under the registry key “HKEY_LOCAL_MACHINE\SOFTWARE\Microsoft\Windows\CurrentVersion\policies\system”.

A Windows registration file has been included in the Continuum 2.01 release in order to expedite these additional steps.

Or the attached file EnableLUA.zip can be used, unzip and execute. 

Supplement:

Using the right click "run as administrator" instead of this is not the same. The right click will only run that .exe as an administrator and not the whole install/configuration package, i.e. SQL2005 manager will fail to run if you do not do as instructed above. You will always get an error stating that you do not have permission to run this program.

 Alternate Windows 10 Admin. to User privilege for I/Net Seven:

  Go to this path: C:\Program Files (x86)\ Inet Seven

1) Rename and move to a new folder these files.

      A) INetIoSrv.exe.manifest

      B) INetW.exe.manifest

      C) If there is a file equalization client, then there is INetEqzMerge.exe.manifest to do this change on as well.

 2) Change the DbCreate by doing this:

      Another problem for non-admin users will be logging into and using DbCreate. A work-around for that would be to create a new login into the SQL database that could be shared among all DbCreate users and would provide the necessary rights.    

 

Alternate Windows 7 Admin to User privilege for I/Net Seven:

 See the attached Document and Manifest Files

 

Labels (7)
Labels:
  • Andover Continuum
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC INET
  • TAC Vista
Attachments
Manifest Win 7.7z
EnableLUA.zip
Tags (4)
  • Find more articles tagged with:
  • 5739
  • Andover97
  • DavidChild19
  • sql
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore