Operating Mode


Last Updated:
LFleming
2024-11-04
03:54 AM
- Red indicates a Critical state.
- Yellow indicates a Warning state.
- Blue indicates an Informational state.
- Green indicates a normal UPS state.
Status | Description | Severity |
On Line |
Estimated Runtime
Device Health Critical |
Not Applicable |
On Battery |
Estimated Runtime
Input utility power is interrupted, and the UPS is supporting its load on battery. The estimated runtime is the number of minutes the load can be supported by the UPS on battery. Runtime Calibration Initiated
The UPS is performing a battery calibration to determine an accurate reading of battery runtime available. The calibration is initiated from PowerChute Serial Shutdown, or via the UPS LCD. See Knowledge Base article FA284198 for more information on runtime calibration. |
Warning
Informational |
Low Battery | Estimated Runtime The UPS operating on battery has reached the Low Battery Threshold, which is configured via the UPS LCD or via PowerChute Serial Shutdown or Network Shutdown. If the UPS runtime remaining falls below the Low Battery threshold, and if input power is not restored to the UPS, it will shut down when the battery has exhausted. |
Critical |
Bypass |
UPS Initiated Bypass
User Initiated Bypass
A user has placed the UPS into bypass mode, which allows maintenance to be performed without turning off utility power to the UPS. NOTE: This option is not available for all UPS models
|
Critical
Warning |
UPS Off |
Output Power Turned Off
The UPS output is turned off, and is no longer supporting any connected devices. |
Informational |