Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Industrial Automation Knowledge Base

Access vast amounts of technical know-how and pro tips from our community of Industrial Automation experts.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Industrial Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • EcoStruxure Process Expert 20
  • M580 20
  • EcoStruxure Automation Expert 16
  • EPE 16
  • Robotics 13
  • Communication 13
  • Citect SCADA 13
  • IEC 61499 13
  • Networking 13
  • Control Expert 12
  • EcoStruxure Machine SCADA Expert 11
  • Cybersecurity 11
  • EcoStruxure Control Expert 11
  • Automation Expert 11
  • HDCS 10
  • PES 10
  • PROCESS EXPERT 10
  • Connectivity 10
  • EcoStruxure Hybrid DCS 9
  • AVEVA System Platform 9
  • node-red 9
  • dPAC 8
  • EcoStruxure Machine Expert 8
  • Function Block Programming 8
  • Machine Control 8
  • Security 7
  • WWW 7
  • AVEVA 6
  • Architecture 6
  • Docker 6
  • IIoT 6
  • Cloud Connectivity 6
  • High Availability 5
  • firmware 5
  • Asset Link 5
  • Motion 5
  • HVAC 4
  • Cloud Services 4
  • RBAC 4
  • Dashboards 4
  • Maintenance 4
  • Safety 4
  • Augmented Reality 3
  • Machine Safety 3
  • Fieldbus 3
  • High Performance Machine Control 3
  • Redundancy 3
  • Process Safety 2
  • Reporting 2
  • drives 2
  • OPC UA 2
  • Transport 2
  • SCADA 2
  • AOA 2
  • SQL 2
  • General Purpose Library 2
  • ALTIVAR 2
  • MMM 2
  • Lexium 2
  • SE Template 1
  • Palletizing 1
  • PacDrive3 1
  • Hoisting 1
  • Event Logging 1
  • Runtime tags 1
  • CSharp 1
  • ModbusGateway 1
  • C Sharp 1
  • Modicon M262 1
  • Aquis 1
  • Recipe Management 1
  • Situational Awareness 1
  • Cloud 1
  • Service 1
  • timestamp 1
  • EcoStruxure Machine 1
  • Harmony 1
  • Feature 1
  • Cement 1
  • Packaging 1
  • Altistart 1
  • DCS 1
  • 4G 1
  • CPG 1
  • programming 1
  • Scripting 1
  • Cobot Expert 1
  • diagnostics 1
  • STB 1
  • Plant SCADA 1
  • Custom Widget 1
  • Google Maps 1
  • Tracking 1
  • Robot 1
  • Custom Gripper 1
  • Visual Studio 1
  • Lexium Cobot 1
  • Previous
  • 1 of 7
  • Next
Top Contributors
  • Michael_Chan
    Michael_Chan
  • RobertSanders
    RobertSanders
  • kingslim
    kingslim
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Automation Expert
Schneider Electric
EcoStruxure™ Automation Expert
71
Thumbnail of Modicon M580
Schneider Electric
Modicon M580
58
Thumbnail of EcoStruxure™ Control Expert
Schneider Electric
EcoStruxure™ Control Expert
53
Load more

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Industrial Automation Knowledge Base

Sort by:
Helpfulness
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 9
    • 10
    • 11
    • …
    • 19
  • Next »

How to use M580 OPC-UA Client Read-Write Function Blocks

Issue One of the biggest challenges in the industrial automation and control field is how to get machines to talk to each other. Exchanging data from machine to machine, or a machine to PC, machine integration between vendors of different types can be complex, laborious, and difficult, requiring expensive engineers and incurring significant expense. When you integrate systems of multiple vendors to provide total solutions to your customers, you want to use standardized, reliable, secure, scalable and platform independent technology. Resolution This is where we can leverage the OPC UA (Open Platform Communications Unified Architecture) to solve these strategic issues faced by most manufacturers. It is a standardized protocol that allows for seamless and secure communication between different systems and devices, regardless of the vendor or platform. The document here describes one of the methods of exchanging data between different machines. By implementing OPC UA client function blocks in a controller, the controller can directly access data from any other OPC UA servers. As an example, a demo architecture is shown: A virtual machine or PC is used here as the OPC-UA server and the Modicon M580 ePAC as the OPC UA client, should be on the same network and should have the correct network settings configured. The virtual machine's network adapter should be set to bridged mode, and the virtual machine PC's firewall settings should allow communication with the M580 CPU (Firmware ≥ 4.10). See attached document on how to implement the Modicon M580 OPC-UA Client Read/Write function blocks. Disclaimer The views and opinions expressed in this article are those of the author(s) and do not necessarily reflect the official policy or position of Schneider Electric.  
View full article
Commander Michael_Chan Commander
‎2023-04-30 09:09 PM

Last Updated: Lieutenant Vartika ‎2023-11-23 12:38 AM

Labels:
  • EcoStruxure Control Expert
6605 Views

EcoStruxure Control Expert - How to migrate the Security Editor Database ?

Issue A security database was created with the Security Editor tool on a PC where an old version of EcoStruxure Control Expert is installed (i.e. version 15.0). Then, a newer version of EcoStruxure Control Expert is installed (i. e. version 16.0) on the same PC. How to avoid creating the entire security database from scratch after installing a newer version of EcoStruxure Control Expert. Resolution Use the Security Database Migration Tool to migrate the previous security database to the one that is automatically created as part of the installation process of EcoStruxure Control Expert V16.0.
View full article
Lieutenant Mumuny_Gbadamosi Lieutenant
‎2023-12-05 08:52 AM

on ‎2023-12-05 08:52 AM

Labels:
  • Security
4317 Views

EcoStruxure Process Expert - Simulator Tips and Tricks

Issue With the EcoStruxure Process Expert, a Control Simulator can be used for testing the logic. This is usually done on the development workstation and there is often a requirement to run more than one simulator to test connections between controllers and/or the SCADA system. Resolution This document contains trick and tips for using the simulator with EcoStruxure Process Expert. Disclaimer The views and opinions expressed in this article are those of the author(s) and do not necessarily reflect the official policy or position of Schneider Electric.
View full article
Lt. Commander Richard Lt. Commander
‎2025-12-11 09:59 AM

Last Updated: Commander TristanPowell Commander ‎2025-12-12 12:12 AM

48 Views

EcoStruxure Control Expert and Syslog in Ubuntu

Issue Cyber security defence is increasingly difficult in any Ethernet network-based architecture. Putting more layers of protection is a good strategy but knowing what has happened to a system is essential to any investigation of an incident. Analysing system logs is often the key to discovering what has happened during a forensic  examination. EcoStruxure Control Expert, M580 and other communication modules support posting logs to a centralized system known as a Syslog Server. Resolution Using the Syslog servers in Ubuntu for event logging on M580 is detailed in the attached article. Disclaimer The views and opinions expressed in this article are those of the author(s) and do not necessarily reflect the official policy or position of Schneider Electric.  
View full article
Ensign DavidBillingham Ensign
‎2025-12-11 06:23 AM

on ‎2025-12-11 06:23 AM

Labels:
  • Communication
  • Cybersecurity
  • Networking
38 Views

EcoStruxure Operator Terminal Expert – Using FTP to store a project file

How can I upload my project from my HMI? Well you cant, but this article discuss a work around using FTP.
View full article
Lt. Commander TomDroll Lt. Commander
‎2025-10-06 01:21 PM

on ‎2025-10-06 01:21 PM

416 Views

EcoStruxure Operator Terminal Expert - Configuring FTPS Client using a certificate

The document provides a detailed guide on configuring the FTPS client in EcoStruxure Operator Terminal Expert (EOTE) using certificate-based validation to enhance secure file transfers between HMI systems and FTPS servers
View full article
Lt. Commander TomDroll Lt. Commander
‎2025-10-06 08:31 AM

on ‎2025-10-06 08:31 AM

511 Views

EcoStruxure Automation Expert - How to communicate with TM3 Bus Couple via Ethernet IP

Objective The purpose of this article is to demonstrate the steps to setting the communication between EcoStruxure Automation Expert and TM3 Bus Coupler via EthernetIP protocol. Resolution The attached document provides a step-by-step guide to setting the communication between EcoStruxure Automation Expert and TM3 Bus Coupler via EthernetIP protocol.  
View full article
Ensign Sweetly Ensign
‎2025-09-05 05:08 AM

1464 Views

How to Attach and Detach a Tool in EcoStruxure Machine Expert Twin

Objective The purpose of this article is to introduce the necessary steps to Attach and Detach a Standard Tool and a Custom Tool at a robot in EcoStruxure Machine Expert Twin. Resolution This article has highlighted how to Attach and Detach a Robot Standard and Custom Tool in EcoStruxure Machine Expert Twin from version 2.2. It shows which steps must be completed and guides the reader through the instructions.  
View full article
Lieutenant SvenBrand Lieutenant
‎2025-09-03 12:00 AM

on ‎2025-09-03 12:00 AM

Labels:
  • Motion
  • Robotics
1207 Views

EcoStruxure Operator Terminal Expert - Configuring FTPS Client

This article describes the configuration of the newly added (v4.0) FTP client functionality.  It also includes a simple project file for demonstration purposes.
View full article
Lt. Commander TomDroll Lt. Commander
‎2025-08-11 08:36 AM

on ‎2025-08-11 08:36 AM

Labels:
  • IIoT
1346 Views

EcoStruxure Control Expert and Modicon Edge I/O NTS using Explicit Communications

Issue There are many ways of natively communicating between an EcoStruxure Control Expert based control system and a Modicon Edge I/O NTS Island, most involve stopping the CPU to download a new configuration. Resolution This document presents another method, explicit communications using the DATA_EXCHANGE function block. This function block can be used to code Modbus requests other than those provided in the READ_VAR and WRITE_VAR functions. Specifically, the simultaneous read/write Modbus function. Disclaimer The views and opinions expressed in this article are those of the author(s) and do not necessarily reflect the official policy or position of Schneider Electric.  
View full article
Ensign DavidBillingham Ensign
‎2025-08-11 08:41 AM

on ‎2025-08-11 08:41 AM

1592 Views

Transitioning from BME NOC 0301/0311 to BME NOC 0302 Ethernet Modules

Issue Why Transition from BME NOC 0301/0311 to BME NOC 0302? The BME NOC 0302 Ethernet module offers key advantages over BME NOC 0301/0311: Better Reliability: Lower latency and improved traffic handling Enhanced Security: Compliant with current cybersecurity standards Future-Ready: Compatible with upcoming system upgrades Lower Maintenance Risk: Avoids issues from outdated hardware and firmware Resolution Transitioning to the BME NOC 0302 module is a strategic upgrade that delivers improved performance, enhanced cybersecurity, and long-term system compatibility. It ensures your network infrastructure remains robust, scalable, and aligned with evolving industrial standards. Disclaimer The views and opinions expressed in this article are those of the author(s) and do not necessarily reflect the official policy or position of Schneider Electric.  
View full article
Commander Michael_Chan Commander
‎2025-08-03 09:55 PM

Labels:
  • Architecture
  • Communication
  • Connectivity
1433 Views

EcoStruxure Automation Expert: Display CAT Instance Name in the Faceplate Title.

Issue In EcoStruxure Automation Expert HMI, It is possible to create a faceplate with a fixed title. However, by default, it is not possible to display the name of the CAT instance. The issue occurs when multiple faceplates are open simultaneously, making it challenging to identify which asset each one is associated with. Resolution The purpose of this document is to explain how to add the CAT instance name to the faceplate title. More generally, the document explains how to access the faceplate title from C# code. Disclaimer The views and opinions expressed in this article are those of the author(s) and do not necessarily reflect the official policy or position of Schneider Electric.  
View full article
Lt. Commander Eric_Coudurier Lt. Commander
‎2025-07-28 07:02 AM

Labels:
  • IEC 61499
1427 Views

PacDrive 3 / EcoStruxure Machine Expert - Create a Cam Profile from Trace

Implemented feature in EcoStruxure Machine Expert to import trace as profile.
View full article
Lieutenant JG Wolfram64 Lieutenant JG
‎2025-07-25 01:55 AM

Last Updated: Commander TristanPowell Commander ‎2025-08-11 08:40 AM

Labels:
  • Motion
733 Views

How to create a Custom Node for EcoStruxure Machine Expert Twin Logic Configurator

Issue Within EcoStruxure Machine Expert Twin you require custom logic for your model combined with other logic blocks in Logic Configurator. Resolution Based on the Plugin template it is possible to develop a custom node to be used in Logic Configurator. Disclaimer The views and opinions expressed in this article are those of the author(s) and do not necessarily reflect the official policy or position of Schneider Electric.
View full article
Lieutenant JG Stefan_Winkler Lieutenant JG
‎2025-07-08 09:27 PM

Last Updated: Commander TristanPowell Commander ‎2025-07-10 07:46 AM

Labels:
  • Machine Control
1382 Views

EcoStruxure Automation Expert - How to install EAE Archive & pgAdmin4 on Linux OS

Objective The purpose of this article is to demonstrate the steps for install EcoStruxure Automation Expert (EAE) Archive and pgAdmin4 software to Linux OS (Ubuntu) Resolution The attached document provides a step-by-step guide to install EcoStruxure Automation Expert (EAE) Archive and pgAdmin4 software to Linux OS (Ubuntu)  
View full article
Ensign Sweetly Ensign
‎2025-07-10 09:12 PM

on ‎2025-07-10 09:12 PM

1604 Views

EcoStruxure Automation Expert - How to install EAE HMI on Linux OS

Objective The purpose of this article is to demonstrate the steps for install and configure the EcoStruxure Automation Expert (EAE) HMI to the Linux OS (Ubuntu). Resolution The attached document provides a step-by-step guide to install and configure EcoStruxure Automation Expert (EAE) HMI to the Linux OS (Ubuntu)
View full article
Ensign Sweetly Ensign
‎2025-07-10 09:10 PM

on ‎2025-07-10 09:10 PM

1724 Views

How to Set Up a UserException in Motion Applications

Objective The purpose of this article is to introduce the necessary steps to explain the basics of UserWarning and UserException based on the Lexium Multicarrier example project embedded in EcoStruxure Machine Expert. Resolution This article outlines how to implement a UserWarning and a UserException within a template project. It explains the necessary steps and guides the reader through the basic concepts and the provided project structure.  
View full article
Lieutenant SvenBrand Lieutenant
‎2025-06-27 02:14 AM

Labels:
  • Motion
927 Views

OPCUA Server-Client connection in EcoStruxure Automation Expert Motion

Objective The purpose of this article is to highlight an OPCUA connection example between EcoStruxure Automation Expert Motion and EcoStruxure Machine Expert Twin. Resolution This article highlighted how to set up an OPCUA Server Client connection in EcoStruxure Automation Expert Motion. It explained the required steps and guides the reader through the necessary setup in the related software.  
View full article
Lieutenant SvenBrand Lieutenant
‎2025-06-22 10:36 PM

on ‎2025-06-22 10:36 PM

1829 Views

Modicon Redundant Switch - Factory Reset Using Command Line

Issue Resetting a Modicon Redundant Switch may leave the web browser inaccessible, so it is not possible to configure the switch. Resolution This article describes how to do a full factory reset using the command line of the switch. It follows on from the knowledgebase article Modicon Redundant Switch - Factory Reset Without Password which is included here for convenience. Disclaimer The views and opinions expressed in this article are those of the author(s) and do not necessarily reflect the official policy or position of Schneider Electric.  
View full article
Lt. Commander Richard Lt. Commander
‎2025-06-17 02:14 AM

Last Updated: Commander TristanPowell Commander ‎2025-06-17 11:04 PM

Labels:
  • Architecture
  • Networking
  • Redundancy
2478 Views

EcoStruxure Automation Expert Motion - How to Create a Task Group and Assign a Task to a Core

Issue In a multi-core system such as Modicon M660, performance issues such as uneven CPU load distribution, jitter in cyclic tasks or unexpected task interference may occur when all tasks are executed on the same CPU core by default. Resolution To improve task scheduling, optimize performance and reduce interference, EcoStruxure Automation Expert Motion allows assigning task group to specific CPU core. Disclaimer The views and opinions expressed in this article are those of the author(s) and do not necessarily reflect the official policy or position of Schneider Electric.  
View full article
Lieutenant JG Lrhaouch Lieutenant JG
‎2025-06-09 07:02 AM

837 Views
  • « Previous
    • 1
    • …
    • 9
    • 10
    • 11
    • …
    • 19
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore