Working with rack ATS

Configuring power connections

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • IT Advisor
  • ITA desktop client
  • Configuring the ITA desktop client
  • Configuring power connections
  • Working with rack ATS
Options
  • Subscribe to RSS Feed
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • EcoStruxure IT forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

EcoStruxure IT Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to Configuring power connections
Options
  • Subscribe to RSS Feed
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
900 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Working with rack ATS

Picard EcoStruxureIT
‎2022-03-22 11:09 PM

There are two types of genomes:

  • Simple rack ATS: Does not have extended information (banks, type of outlets)
  • Extended rack ATS: Includes extra information (banks, breakers, inlets, outlets)

Before using a rack ATS, you must add one from the local Genome library to the rack:

To add power suppliers to the rack:

  1. In the Floor Layout, right click the rack and select Properties > Power.
  2. In the Properties dialog, choose one of the following:
    1. Select a rack PDU and click Edit to enter the connection details.
    2. Select a floor standing PDU and add a new power receptacle.
    3. Select a rack mount PDU (if it is already added to the rack).
  3. Right-click the ATS in a rack and go to Properties > Power Dependency.

Working with simple rack ATSs

Defining the upstream connection

The upstream connection is a connection from the power supplier to the rack ATS. You must define power suppliers in the rack to establish a connection.

Connecting a simple rack ATS to a simple rPDU (3-phase breaker)

Because both the ATS inlet type and rPDU outlet types are unknown, the connection may be defined by choosing a phase that is available on the rPDU’s breaker. Be sure to choose the correct phase that matches the ATS inlet type.

 

mceclip0_4642636951197.pngmceclip0_4642636951197.png

 

Connecting a simple rack ATS to an extended RPDU (3-phase breaker)

Define the rPDU outlet to use for the connection. The power outlet list contains all PDU outlets that are not occupied by other connections. You must be aware to select the correct outlet and phase.

mceclip1_4642636951197.pngmceclip1_4642636951197.png

 

Connecting a simple rack ATS via power receptacle

You must choose the power receptacle available in the list. There is no validation between the phase on the receptacle’s breaker and the ATS inlet type. The phase is taken from the breaker.

 

mceclip2_4642636951197.pngmceclip2_4642636951197.png

 

Defining the downstream connection

To connect a server to a simple ATS:

  1. Right click the server you want to connect and select Properties > Power.

In the Power Cable Connection section, choose a device and phase that is available on the primary connection of the ATS.

mceclip3_4642636951197.pngmceclip3_4642636951197.png

 

Working with extended rack ATSs

Defining the upstream connection

Connecting extended  rack ATS via simple rPDU (3-phase breaker)

Choose the power phase for primary and secondary connections.

In this case, the ATS inlet type is known, and the list of of available phases filters out non-matching phases.

mceclip4_4642636951197.pngmceclip4_4642636951197.png

Connecting extended rack ATS via extended rPDU

In this case you must define which outlet of the rPDU is used for the connection. The power outlet list contains all PDU outlets that are not occupied by other connections. The list does not contain outlets where the pin configuration does not match the server’s inlet.

mceclip5_4642636951197.pngmceclip5_4642636951197.png

 

Connecting extended rack ATS via power receptacle

You must choose the power receptacle available in the list. The list is restricted to the receptacles (phase) matching the ATS inlet type.

Defining downstream connection

Connecting the server to a simple ATS:

  1. Right click a server you want to connect and choose: Properties > Power

In Power Cable Connection sections, choose a device and outlet that are available on the primary connection of extended ATS:

Power outlet list contains only outlet types that match the server inlet type.

 

mceclip6_4642636951197.pngmceclip6_4642636951197.png

Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

Didn't find what you are looking for? Ask our Experts
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of