Configuring distributed redundant UPS systems

Configuring power connections

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • IT Advisor
  • ITA desktop client
  • Configuring the ITA desktop client
  • Configuring power connections
  • Configuring distributed redundant UPS systems
Options
  • Subscribe to RSS Feed
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • EcoStruxure IT forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

EcoStruxure IT Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to Configuring power connections
Options
  • Subscribe to RSS Feed
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
2806 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Configuring distributed redundant UPS systems

Picard EcoStruxureIT
‎2019-11-06 07:12 AM

A distributed redundant UPS configuration can be used as an inexpensive way to obtain complete redundancy as it is less expensive than a 2N architecture. It is usually chosen for large multi-megawatt installations where concurrent maintenance is a requirement and space is limited. It involves 3 or more UPS modules with independent input and output feeders. The critical load is connected through multiple PDUs. In some cases, STS are also used.

For further information about UPS System Design Configurations, see White Paper 75.

IT Advisor allows you to model all distributed redundant UPS design configurations mentioned in the white paper.

Distributed redundant "catcher" UPS configuration

This configuration includes 3 UPS modules in a distributed redundant design that could also be referred to as a "catcher system". In this configuration, module 3 is connected to the secondary input on each STS, and would "catch" the load upon the failure of either primary UPS module. It is only supported to have one "catcher" UPS per "catcher system" and it must be unloaded. Otherwise, you should set up a distributed redundant UPS configuration as described below.

Configuration:

  1. Add UPS modules, PDUs, STS, and racks to the floor layout as illustrated.
    For the STS, add ATS from Genomes, right-click them and rename them STS.
  2. Add servers and rack PDUs to the racks.
  3. Configure the power paths.
    1. Right-click the UPS modules one by one and select Properties>Power to set up redundancy feeds.
      1. For UPS 1, select "With Catcher" (Distributed Redundant).
      2. For UPS 2, select "With Catcher" (Distributed Redundant).
      3. For UPS 3, select "Catcher" (Distributed Redundant).
    2. Connect all equipment to the power paths (see tip below).

In normal operation, UPS 1 and 2 carry the full load.
In case of a failure of either UPS 1 or 2, UPS 3 catches the load of the failing UPS.

102239844_360038495393.png102239844_360038495393.png

Distributed redundant UPS configuration (with STS)

This is a distributed redundant design with three STS and the load evenly distributed across the three modules in normal operation. The failure on any one module would force the STS to transfer the load to the UPS module feeding its alternate source.

Configuration:

  1. Add UPS modules, PDUs, STS, and racks to the floor layout as illustrated.
  2. Add servers and rack PDUs to the racks.
    1. Right-click the UPS modules one by one and select Properties>Power to set up redundancy feeds, all Distributed Redundant.
    2. Right-click the STS one by one and select Properties>Power Dependency to set up primary and secondary connections.
      1. Set the primary load so each UPS carries its own load.
      2. Set the secondary load so the UPS modules alternately catch the load for each other in case of a failover.
    3. Connect all equipment to the power paths (see tip below).

In normal operation, the load is evenly distributed across all 3 UPS modules.
In case of a failure of any of the UPS modules (but only one at a time), the load gets transferred (failover) to the other UPS modules.

102239837_360038495393.png102239837_360038495393.png

Distributed redundant UPS configuration (no STS)

As the quantity of single-corded loads in data centers today are becoming fewer and fewer, it is becoming more practical and less costly to apply multiple, small, point of use transfer switches close to the single-corded loads. In cases with 100% dual-corded loads, this configuration could be designed without STS units. This design is typically known as a tri-redundant and uses no static transfer switches.

Configuration:

  1. Add UPS modules, PDUs, and racks to the floor layout as illustrated.
  2. Add servers and rack PDUs to the racks.
  3. Right-click the UPS modules one by one and select Properties>Power to set up redundancy feeds, all Distributed Redundant.
  4. Connect all equipment to the power paths (see tip below).

In normal operation, the load is evenly distributed across all 3 UPS modules.
In case of a failure of any of the UPS modules (but only one at a time), the load gets transferred (failover) to the other UPS modules.

102239813_360038495393.png102239813_360038495393.png

Tip

Use different colors for the power paths to visually distinguish between them. (Right-click on the UPS, select Properties>Power>Power Path Color.)

The Power overlay tool tips displaying when you hover over equipment in racks provide a visual overview of the load distribution and redundancy settings.

Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

Didn't find what you are looking for? Ask our Experts
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of