Working with breaker panels
Configuring power connections
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
In the breaker panel you can add breakers with an exact definition of position and capacity available. This enables you to map out and track power connections within the PDU and to reduce stranded capacity. When correctly configured, the breaker panel provides an easy overview of available circuits, breakers, and phases. This overview can be printed and displayed inside the physical panel.
Working with breaker panels includes the following procedures:
When everything is set up, you can conduct impact analysis on connected breakers. See Simulating impact
Configuring breakers
Standard models of breakers are available in the Genome Library with detailed information about space and phase requirements. Add standard breakers from the Genome Library to your local genomes. Right-click the breaker in genomes to view and configure properties.
Modular breaker
Breaker Rating: The amount of power the breaker module is rated to
Module size: The number of positions the breaker module occupies in the panel
Power phases: The amount of phases connected to the breaker
Single: a single phase module has three single phase breakers and can be connected to three individual power consumers
Phase to phase (L1-L2, L2-L3, L3-L1): a phase to phase module has a two phase breaker and can have one power consumer (phase to phase modules are typically used in North America)
Three phase (L1-L2-L3): a three phase module can have one power consumer
Modular breaker
102237379_400x541_360037995754.png
Generic breaker
Breaker Rating: The amount of power the breaker is rated to
Pole count: The amount of phases connected to the breaker
Breaker size: The number of positions the breaker occupies on the rail
Generic breaker
102237508_400x544_360037995754.png
Configuring PDUs
You can configure power properties for the PDU in your local genomes or directly in the room layout.
Right-click the PDU and select Properties > Power to edit voltage outputs and voltage inputs. Note that the parameter for the output is phase to phase voltage. If you have an input breaker in front of the PDU, you can specify the value here. If you specify the input breaker, remember to also specify voltage input.
Configuration of a PDU in theroom layoutwill define properties for that individual PDU. Adjustments made in room layout will not affect the PDU in genomes.
In genomes the configurations will apply to the PDU model in general. Adjustments can be made individually to a PDU in room layout, but only within the margins of the configurations you made in genomes. Adjustments made in genomes will not affect the PDUs already placed in the room layout.
PDU power properties
102237516_400x541_360037995754.png
You can also add breaker panels to the PDU in genomes. The panels will be part of the configuration of the PDU. In genomes, right-click the PDU and select Properties > Power > Breaker Panel. You can add and delete panels and in a generic panel, you can edit the circuit numbers to match your setup. You cannot connect breakers from this view. To connect breakers, drag the PDU to the room layout, right-click PDU and select Properties > Power > Breaker Panel > select panel name. More on connecting breakers here.
Add breaker panel in genomes
102237510_400x542_360037995754.png
Configuring breaker panels
Custom breaker panel layouts can be specified individually within the PDU. The process will vary from generic to modular breaker panels.
Modular breaker panel
123 Steps to...
Configuring a modular breaker panel
Add a modular panel in the room layout. Right-click a PDU and select Properties>Power>Breaker Panel>Add panel.
Modular panels require minimum configuration. In the Breaker panel configuration dialog box, define Panel name, Panel size and Type - in this case Modular
If you have an input breaker on the panel, select Panel breaker and add the value.
Breaker panel configuration (modular)
102237514_400x796_360037995754.png
Generic Breaker Panel
If you have upgraded from a previous version of IT Advisor, you will have placeholder panels and need to reorganize, see here. If you are setting up a generic panel, see below.
123 Steps to...
Configuring a generic breaker panel
Add a generic panel in the room layout. Right-click a PDU and select Properties > power > add panel.
Name the panel, set size and choose type.
If you have an input breaker on the panel, select Panel breaker and add the value.
In Layout in the Breaker panel configuration dialog box, you have different options:
Start value: If you have more than one breaker panel in a PDU, it can be useful to give them different start values. For example one panel has circuit numbers 1-24 and the next panel starts at circuit number 25 that would be the start value for that panel.
Phase grouping: If you have one circuit number covering three phases, choose phase grouping.
Distribute poles on two rails: Choose how to organize your breakers on the rails:
odd/even - odd numbers in the left rail and even numbers on the right
sequential - sequential numbering beginning in the left rail ending in the right rail
Breaker panel configuration (generic)
102237520_400x814_360037995754.png
Custom Breaker Panels
You can block out positions and edit circuit numbers to create a custom breaker panel.
123 Steps to...
Creating a custom breaker panel
In Genomes, right-click a PDU and select Properties > Power > Breaker Panel
Double-click the circuit number of generic panels to change it
If you delete a circuit number, that position will be blocked out
Creating a custom panel
102240506_400x802_360037995754.png
Connecting Breakers
Before connecting breakers to the breaker panel, you need to add breaker modules or breakers to your local genomes from the Genome Library.
123 Steps to...
Connect breakers
Right-click a PDU and select Properties > Power > Breaker Panel to open the Properties dialog box
Choose the desired panel by clicking the panel name
The Selected panel details are now visible
Click a cell in the Breaker column and choose a beaker module or breaker in the drop-down menu
Choose a Power Consumer to each breaker to map out breaker connections
Note: Breaker modules or breakers that take up multiple positions will automatically block the cell below it.
Tip
You can take a picture of your breaker panel in your data center to help your memory when you map your connections.
Breaker panel
102237416_400x813_360037995754.png
A picture from your data center can help map connections
102240453_400x412_360037995754.jpg
Printing Breaker Panel Schedules
Manage occupied and free breaker positions on each breaker panel for an easy overview of available breakers, circuit numbers and available phases that can be printed out to display inside the physical breaker panel.
To print breaker panel schedules, right-click the PDU and select Reports >Panel Schedule >print.
For the Co-lo version, the tenant name will be added to the printed breaker panel schedule.