The Power Dependency table shows details about power equipment in your data center infrastructure. You can right-click an item (row) to identify it in the layout or navigation, or to open its Properties.
Power equipment items and where they fit in the power path (indention and expandable arrows).
Location
Location of the power equipment items in the modeled data center infrastructure.
Phase
Phase to which the selected equipment is connected.
Outlet
Outlet to which the selected equipment is connected, shown only if rack PDU has power outlets definition.
Breaker module number
Breaker module number (can also be found in Properties > Power > Breaker Panel).
UPS used capacity
Power used by equipment connected to this UPS for power.
UPS reserved capacity
Power reserved by equipment connected to this UPS for power.
Distribution reserved capacity of UPS size
Relevant for distribution units, such as PDUs, RDPs, and Power Panels. UPS power reserved by this distribution unit (in %).
Distribution reserved UPS capacity
Relevant for distribution units, such as PDUs, RDPs, and Power Panels. UPS power reserved by this distribution unit.
Distribution estimated load
Relevant for distribution units, such as PDUs, RDPs, and Power Panels. Estimated load of equipment connected to this distribution unit for power. In redundancy configurations, this value will include potential failover load.
Distribution unreserved capacity
Relevant for distribution units, such as PDUs, RDPs, and Power Panels. Remaining power available on this distribution unit (total power available minus the load of connected equipment).
Rack remaining power
Relevant if you group racks with similar power requirements (capacity groups). Remaining power available in each rack connected to this distribution unit for power.
Rack maximum capacity
Relevant if you group racks with similar power requirements (capacity groups). The maximum load you can add to each rack connected to this distribution unit for power.