Configure Gateway backup
Configuration
Detailed instructions for how to configure the EcoStruxure IT Gateway
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Gateway is automatically backed up on a weekly schedule. By default, three backup files are retained. The oldest backup file is deleted when another is created. See Backup schedule
Gateway backup configuration and one time backup is performed via the command line. Local or remote terminal access is required to create and maintain Gateway backups.
Backup files are stored to the local file system. Backup files can be stored on a remote system of your choice, independent of the Gateway application, through the OS as a one time or recurring task.
IMPORTANT: You can restore a backup from the same version of Gateway only.
Create a onetime backup
Note: This example is on a Windows based system. The Linux commands are identical; the install directory is slightly different. Sudo can be used to run with administrator level privileges.
Open a command prompt as administrator on the computer where the Gateway is installed.
Navigate to the bin subdirectory in Gateway install directory on the files system, for example, C:\Program Files\EcoStruxure IT Gateway\<version number>\bin.
Type the command ./backup
If prompted, enter a password used to encrypt and decrypt the configuration data. Be sure to save this password for later to use during restoration. After confirming the password, the backup archive will be created. When not prompted, the gateway administrator password will be used.
Upon creation, output is displayed with the Gateway backup id, name, date, and other version information.
GW18_backup_1_360007070377.png
Backup files are stored locally on the Gateway server file system, under the backups subdirectory in the Gateway install directory, for example, C:\Program Files\EcoStruxure IT Gateway\backups. From here, the file can be copied or configured for export to a remote file share through the operating system.
GW18_backup_2_360007070377.png
Backup config options
The instructions above use the default Gateway backup settings. Some aspects of the backup are configurable by adding the config parameter to the backup command.
View the backup configuration
./backup config
View the backup configuration settings.
GW18_backup_3_360007070377.png
Configure the backup password
You will be prompted for a new password to use for encrypting backups.
./backup config --archive-password
GW18_backup_4_360007070377.png
Configure the backup destination
Set the directory used to store backup file contents.
./backup config --destination <file path>
GW18_backup_5_360007070377.png
Configure the maximum number of backups to keep
Set the maximum number of backup entries to store before rotating older entries.
./backup config --rotation <maximum number of backups to store>
GW18_backup_6_360007070377.png
Backup schedule
Set the schedule of backups. The default settings are to backup on Sunday at midnight each week.
--repeat accepts one of the following values: monthly, weekly, daily, or hourly.
--on accepts one of the following values when repeat is weekly: monday, tuesday, wednesday, thursday, friday, saturday, or sunday. When repeat is monthly it accepts the day of the month instead (see examples below).
--at accepts time in twelve or twenty four hour format with hours separated by a colon. Valid examples: 8:00am, 14:00, 2:00pm, or 03:00pm.