Configure Gateway restore on Gateway 1.7.0

Configuration

Detailed instructions for how to configure the EcoStruxure IT Gateway

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • Gateway
  • Configuration
  • Configure Gateway restore on Gateway 1.7.0
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • File transfer status sensor on EcoStruxure IT Gate...
  • Video: Configure Gateway device file transfer sett...
  • Video: Configure device credentials in the Gateway
  • Configure Gateway device polling
  • Configure 1 minute polling in EcoStruxure IT Gatew...
  • Configure Gateway backup
  • Configure Gateway restore on Gateway 1.8+
  • Configuring Gateway backup in Gateway 1.7.0
  • Configure Gateway restore on Gateway 1.7.0
  • Configure SNMP trap ports
  • Trap receiver registration for third party devices
  • Configure SNMPv3 traps and informs in the Gateway
  • Connect PowerChute Business Edition agents (PCBE) ...
  • EcoStruxure IT Gateway logs
  • Configure Web credentials in the Gateway
  • File transfer status sensor on EcoStruxure IT Gate...
  • Video: Configure Gateway device file transfer sett...
  • Video: Configure device credentials in the Gateway
  • Configure Gateway device polling
  • Configure 1 minute polling in EcoStruxure IT Gatew...
  • Configure Gateway backup
  • Configure Gateway restore on Gateway 1.8+
  • Configuring Gateway backup in Gateway 1.7.0
  • Configure Gateway restore on Gateway 1.7.0
  • Configure SNMP trap ports
  • Trap receiver registration for third party devices
  • Configure SNMPv3 traps and informs in the Gateway
  • Connect PowerChute Business Edition agents (PCBE) ...
  • EcoStruxure IT Gateway logs
  • Configure Web credentials in the Gateway

Related Forums

  • EcoStruxure IT Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

EcoStruxure IT Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to Configuration
Start a Topic
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
3700 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Configure Gateway restore on Gateway 1.7.0

Picard EcoStruxureIT
‎2019-01-31 03:45 AM

For configuring restore in Gateway 1.8 and newer, see Configure Gateway restore in Gateway 1.8 

Backup files contain operating system-specific parameters. Restore a Windows system from a Windows backup, and a Linux system from a Linux backup.

IMPORTANT: You can restore a backup from the same version of Gateway only. 

The backup keeps the existing Gateway serial number.

If you are using a proxy server, run this command before you run the restore:

SET _JAVA_OPTIONS=-Dhttp.proxyHost=x.x.x.x -Dhttp.proxyPort=443

Note: x.x.x.x is the IP address of the proxy server. You might also need to change the port if the proxy server is not at 443.

Windows restore

Restore is run from a Windows command prompt.

To restore from a previously created backup:

  1. Open a command prompt as administrator on the computer where the Gateway is installed.
  2. Navigate to C:\Program Files\EcoStruxure IT Gateway\x.x.x\restore
    Type the command cd C:\Program Files\EcoStruxure IT Gateway\x.x.x\restore
  3. Type the command restore.bat
    The utility searches for backups at the location you specify, and prompts you to choose the correct backup.
    After a series of confirmations, the restore process will begin.

When you do not add arguments to the command, all the possible arguments are displayed on the screen, including examples of how to execute the restore process.

Examples

restore.bat restore -serviceName EcoStruxureITGateway-1.7.0.64 -mntType WINDOWS_SHARE -server 1.2.3.4 -share backupShare -dir backupDir -domain aa.bb.com -user admin -pw -zipPw

Note: -user and -pw  and -zipPw are required. Specify the user for the file server.

You will be prompted for the backup location and the encrypted zipfile password after the command is run. The encrypted zipfile password is the serial number of your Gateway.

restore.bat password-reset 

Note: This resets the Gateway admin user’s password. To reset the admin password, you must also go to Control Panel > Administrative Tools > Services and restart the EcoStruxure IT Gateway Server service.

Linux restore

To restore from a previously created backup:

  1. Open a command prompt on the computer where the Gateway is installed.
  2. Type the command cd /opt/EcoStruxureITGateway/x.x.x/restore

  3. Type the command ./restore.sh
    The utility searches for backups at the location you specify, and prompts you to choose the correct backup.
    After a series of confirmations, the restore process will begin.

When you do not add arguments to the command, all the possible arguments are displayed on the screen, including examples of how to execute the restore process

Examples

./restore.sh restore -serviceName EcoStruxureITGateway-1.7.0.64 -mntType WINDOWS_SHARE -server 1.2.3.4 -share backupShare -dir backupDir -domain aa.bb.com -user admin -pw -zipPw

Note: -user and -pw  and -zipPw are required. Specify the user for the file server.

You will be prompted for the backup location and the encrypted zipfile password after the command is run. The encrypted zipfile password is the serial number of your Gateway.

./restore.sh password-reset

Note: This resets the Gateway admin user’s password. To reset the admin password, you must also restart the EcoStruxure IT Gateway Server.  The command can be run from any directory by sudo users. Type systemctl restart EcoStruxureITGateway-x.x.x.service 

Possible arguments

list List database backups
Usage: list [options]
Options:
-backup
backup to restore to
* -dir
backup directory on remote server
-domain
domain of remote server
* -mntType
mountType 'WINDOWS_SHARE'|'NFS'  Note: There is an issue using NFS shares for backup. Windows shares work as expected for the gateway installed on both Linux and Windows.
-pw
prompt for password for file server
-zipPw
prompt for encrypted zipfile password
* -server
remote backup server ip or name
* -share
remote mount point
-user
username for file server

restore Restore database
Usage: restore [options]
Options:
-backup
backup to restore to
* -dir
backup directory on remote server
-domain
domain of remote server
* -mntType
mountType 'WINDOWS_SHARE'|'NFS'
-pw
prompt for password for file server
-zipPw
prompt for encrypted zipfile password
* -server
remote backup server ip or name
* -share
remote mount point
-user
username for file server

 password-reset Reset Gateway administrator password
Usage: password-reset [options]

Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore