Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Configure SNMP trap ports

Configuration

Detailed instructions for how to configure the EcoStruxure IT Gateway

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • Gateway
  • Configuration
  • Configure SNMP trap ports
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • File transfer status sensor on EcoStruxure IT Gate...
  • Video: Configure Gateway device file transfer sett...
  • Video: Configure device credentials in the Gateway
  • Configure Gateway device polling
  • Configure 1 minute polling in EcoStruxure IT Gatew...
  • Configure Gateway backup
  • Configure Gateway restore on Gateway 1.8+
  • Configuring Gateway backup in Gateway 1.7.0
  • Configure Gateway restore on Gateway 1.7.0
  • Configure SNMP trap ports
  • Trap receiver registration for third party devices
  • Configure SNMPv3 traps and informs in the Gateway
  • Connect PowerChute Business Edition agents (PCBE) ...
  • EcoStruxure IT Gateway logs
  • Configure Web credentials in the Gateway
  • File transfer status sensor on EcoStruxure IT Gate...
  • Video: Configure Gateway device file transfer sett...
  • Video: Configure device credentials in the Gateway
  • Configure Gateway device polling
  • Configure 1 minute polling in EcoStruxure IT Gatew...
  • Configure Gateway backup
  • Configure Gateway restore on Gateway 1.8+
  • Configuring Gateway backup in Gateway 1.7.0
  • Configure Gateway restore on Gateway 1.7.0
  • Configure SNMP trap ports
  • Trap receiver registration for third party devices
  • Configure SNMPv3 traps and informs in the Gateway
  • Connect PowerChute Business Edition agents (PCBE) ...
  • EcoStruxure IT Gateway logs
  • Configure Web credentials in the Gateway

Related Forums

  • EcoStruxure IT Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

EcoStruxure IT Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to Configuration
Start a Topic
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
5846 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Configure SNMP trap ports

Picard EcoStruxureIT
‎2021-03-31 05:49 AM

During device discovery, EcoStruxure IT Gateway automatically attempts to register itself as a trap receiver with APC and Schneider Electric SNMPv1 devices with a Network Management Card (NMC) on port 1062.

In Gateway 1.10 and newer, you can configure additional SNMP ports in the Settings > Advanced > SNMP trap ports option. 

Tip: Running an older Gateway version? See How to update your Gateway software

Allowed ports are 0 - 65535. The default system trap port 1062 cannot be changed. The configurable port list contains port 162 by default to support the default for most third party devices.

Note: Make sure you adjust firewall rules to allow for any additional ports you add in the Gateway.

You do not have to restart the Gateway after changing the list of available ports.

GW110_advanced_SNMP_ports_360018952938.pngGW110_advanced_SNMP_ports_360018952938.png

Traps and informs in the Gateway

The Gateway listens for SNMPv1 traps, and starting in Gateway 1.18, SNMPv3 traps and informs for discovered APC NMC and third party devices. See Configure SNMPv3 traps and informs in the Gateway

APC NMC devices

Discovered APC NMC SNMPv3 devices are not automatically registered as trap receivers. The SNMPv3 device must be configured for SNMPv3 traps:

SNMPv3

  • Username
  • Authentication and password: SHA, MD5, or None
  • Encryption type and password: AES256, AES192, AES128, DES3, DES, or None
  • Port:
    • Port 1062, 162, or a port you specify in the Settings > Advanced > SNMP trap ports option

Note: APC NMC devices send traps to every registered trap listener.

Need help for APC NMC devices?

Third party devices

To allow the Gateway to receive traps from third party devices, Schneider Electric devices without an NMC, or NMC SNMPv3 devices - in other words, devices where the Gateway cannot automatically register itself as a trap receiver - you must manually configure each device with these trap receiver settings:

SNMPv1

  • NMS IP address/Host name: Your EcoStruxure IT Gateway IP address
  • Port:
    • Gateway version 1.10 or later:  Port 1062, 162, or a port you specify in the Settings > Advanced > SNMP trap ports option*
  • Community string: public

SNMPv3

  • NMS IP address/Host name: Your EcoStruxure IT Gateway IP address
  • Username
  • Authentication and password: SHA, MD5, or None
  • Encryption type and password: AES256, AES192, AES128, DES3, DES, or None
  • Port:
    • Port 1062, 162, or a port you specify in the Settings > Advanced > SNMP trap ports option*

*Gateway versions 1.9 and earlier required 1062 as the trap port for third party devices.

Some devices may require additional device-specific settings for traps to be sent. Consult the user manual for the device for more information.

When EcoStruxure IT Gateway receives a trap from a device, it immediately polls the alarms that are predefined for the device. It does not process the content of the trap message. It does not poll the sensors immediately, which means that alarms created based on sensor thresholds will not be updated until the next scheduled poll.

See How often does the Gateway poll monitored devices?

 

 

Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore