Configure Gateway backup

Configuration

Detailed instructions for how to configure the EcoStruxure IT Gateway

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • Gateway
  • Configuration
  • Configure Gateway backup
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • File transfer status sensor on EcoStruxure IT Gate...
  • Video: Configure Gateway device file transfer sett...
  • Video: Configure device credentials in the Gateway
  • Configure Gateway device polling
  • Configure 1 minute polling in EcoStruxure IT Gatew...
  • Configure Gateway backup
  • Configure Gateway restore on Gateway 1.8+
  • Configuring Gateway backup in Gateway 1.7.0
  • Configure Gateway restore on Gateway 1.7.0
  • Configure SNMP trap ports
  • Trap receiver registration for third party devices
  • Configure SNMPv3 traps and informs in the Gateway
  • Connect PowerChute Business Edition agents (PCBE) ...
  • EcoStruxure IT Gateway logs
  • Configure Web credentials in the Gateway
  • File transfer status sensor on EcoStruxure IT Gate...
  • Video: Configure Gateway device file transfer sett...
  • Video: Configure device credentials in the Gateway
  • Configure Gateway device polling
  • Configure 1 minute polling in EcoStruxure IT Gatew...
  • Configure Gateway backup
  • Configure Gateway restore on Gateway 1.8+
  • Configuring Gateway backup in Gateway 1.7.0
  • Configure Gateway restore on Gateway 1.7.0
  • Configure SNMP trap ports
  • Trap receiver registration for third party devices
  • Configure SNMPv3 traps and informs in the Gateway
  • Connect PowerChute Business Edition agents (PCBE) ...
  • EcoStruxure IT Gateway logs
  • Configure Web credentials in the Gateway

Related Forums

  • EcoStruxure IT Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

EcoStruxure IT Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to Configuration
Start a Topic
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
5075 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Configure Gateway backup

Picard EcoStruxureIT
‎2020-03-27 05:14 AM

Last Updated: Sisko JLehr Sisko ‎2025-06-20 08:51 AM

Gateway is automatically backed up on a weekly schedule. See Backup schedule

 

Gateway backup configuration and one time backup is performed via the command line. Local or remote terminal access is required to create and maintain Gateway backups.

 

Backup files are stored to the local file system. Backup files can be stored on a remote system of your choice, independent of the Gateway application, through the OS as a one time or recurring task.

IMPORTANT: You can restore a backup from the same version of Gateway only. 

 

Create a onetime backup

 

Note: This example is on a Windows based system. The Linux commands are identical; the install directory is slightly different. Sudo can be used to run with administrator level privileges.

 

  1. Open a command prompt as administrator on the computer where the Gateway is installed.

  2. Navigate to the bin subdirectory in Gateway install directory on the files system, for example, C:\Program Files\EcoStruxure IT Gateway\<version number>\bin.

  3. Type the command ./backup

  4. If prompted, enter a password used to encrypt and decrypt the configuration data. Be sure to save this password for later to use during restoration. After confirming the password, the backup archive will be created. When not prompted, the gateway administrator password will be used. 

  5. Upon creation, output is displayed with the Gateway backup id, name, date, and other version information.

GW18_backup_1_360007070377.pngGW18_backup_1_360007070377.png

 

Backup files are stored locally on the Gateway server file system, under the backups subdirectory in the Gateway install directory, for example, C:\Program Files\EcoStruxure IT Gateway\backups. From here, the file can be copied or configured for export to a remote file share through the operating system.

 

GW18_backup_2_360007070377.pngGW18_backup_2_360007070377.png

 

Backup config options

 

The instructions above use the default Gateway backup settings. Some aspects of the backup are configurable by adding the config parameter to the backup command.

 

View the backup configuration

 

./backup config

 

View the backup configuration settings.

 

GW18_backup_3_360007070377.pngGW18_backup_3_360007070377.png

 

Configure the backup password

 

You will be prompted for a new password to use for encrypting backups.

 

./backup config --archive-password

GW18_backup_4_360007070377.pngGW18_backup_4_360007070377.png

 

Configure the backup destination

 

Set the directory used to store backup file contents.

 

./backup config --destination <file path>

GW18_backup_5_360007070377.pngGW18_backup_5_360007070377.png

 

Configure the maximum number of backups to keep

 

Set the maximum number of backup entries to store before rotating older entries.

 

./backup config --rotation <maximum number of backups to store>

GW18_backup_6_360007070377.pngGW18_backup_6_360007070377.png

 

Backup schedule

 

Set the schedule of backups. The default settings are to backup on Sunday at midnight each week.

--repeat accepts one of the following values: monthly, weekly, daily, or hourly.

 

--on accepts one of the following values when repeat is weekly: monday, tuesday, wednesday, thursday, friday, saturday, or sunday. When repeat is monthly it accepts the day of the month instead (see examples below).

 

--at accepts time in twelve or twenty four hour format with hours separated by a colon. Valid examples: 8:00am, 14:00, 2:00pm, or 03:00pm. 

 

GW18_backup_7_360007070377.pngGW18_backup_7_360007070377.png

 

Weekly backup example

 

Backup will run every Tuesday at 14:00 (2pm).

./backup schedule --repeat weekly --on tuesday --at 14:00

 

Monthly backup example

 

Backup will run on the 15th of each month at 08:00 (8am).

./backup schedule --repeat monthly --on 15 --at 8:00am

 

Daily backup example

 

Backup will run every day at 14:00 (2pm)

./backup schedule --repeat daily --at 2:00pm

 

Hourly backup example

 

Backup will run every hour

./backup schedule --repeat hourly

 

Disabling scheduled backup

Scheduled backup will be disabled

./backup schedule false

 

Re-enabling scheduled backup

Scheduled backup will be enabled with the default backup schedule.

./backup schedule true --repeat weekly

 

 

Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore