Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Enterprise Server and Automation Server Bindings show Unresolved

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Enterprise Server and Automation Server Bindings show Unresolved
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • GavinHe
    GavinHe
  • DavidFisher
    DavidFisher
  • DavidChild
    DavidChild
  • Hernan_Urueña
    Hernan_Urueña
  • Product_Support
    Product_Support
  • Tom_Poovey
    Tom_Poovey
  • Derrick_Ratliff
    Derrick_Ratliff
  • RyanSuar
    RyanSuar
  • CraigEl
    CraigEl
  • Cody_Failinger
    Cody_Failinger

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
3 Likes
19720 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Enterprise Server and Automation Server Bindings show Unresolved

Picard Product_Support
‎2018-09-11 03:18 PM

Last Updated: Admiral GavinHe Admiral ‎2023-09-27 11:41 AM

Issue

The binding between an Enterprise Server and Automation Server or between two Automation Servers shows Unresolved

Unresolved Binding.png

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Enterprise Server
  • Building Operation Automation Server
  • Binding Diagnostics

Cause

The communication between the two servers is incorrectly configured, blocked by software such as firewalls or antivirus or another application is using the port.

Resolution

For Firewall Issues:

Ensure the Windows firewall on the Enterprise Server PC is set up correctly, for example follow Creating Windows Firewall rules to allow Building Operation to communicate on the TCP port to set up inbound and outbound rules.  

Alternatively configure the Windows firewall using the Firewall Config tool on all PC's having EcoStruxure software installed.

Problems with firewall settings can arise if the Enterprise Server PC is removed during the commissioning process and the firewall settings swap between Private Networks and Public Networks.

For example

  • All the Automation Servers may appear online, but the "Unresolved" bindings issue may be seen.
  • Automation Servers cannot be restored via the Enterprise Server

If a suitable option temporarily disable the firewall to see if it fixes the issue.

 

For 1.4 or 1.5 Servers with a name containing the "&" symbol:

Ask Product Support for Hotfix R1.4.1.16201 (or later version) for version 1.4 and R1.5.0.1601 (or later version) for version 1.5. 

 

For other Causes:

Follow these troubleshooting steps in order until the issue has been resolved.

  1. Check that the ES IP address is the same as the PC IP address.  If they do not match, follow How to set the Enterprise Server IP address to change the ES IP. 
  2. All ports must be open between the ES and AS, for port numbers search "Network Ports" in the Information Technology System Planning Guide.
  3. If the address of the ES is a domain name, try using the IP address instead.
  4. If there are more than one network adaptor on the ES can, for example, take the address of a wireless adaptor, VMware virtual adaptor or VirtualBox adaptor.  The ES should be using the NIC adaptor, either follow the link in item 1 or disable the other network adaptors.
  5. Right click on the ES and select Advanced > Repair Server Communication.  This should update the Communication tables of the servers.
  6. Detach the automation servers from the ES and then add the automation servers back.  Follow Unable to add an Automation Server underneath an Enterprise Server.
  7. Select each server and click on the Communication Tab.  If communication is valid, it should list the details of every other server.
  8. Try to disable any network monitor function of anti-virus software on the computer.
  9. If a Schneider laptop is used, right click the Trellix software in the system tray and Enable Firewall Timed Groups.
    Trellix Timed Groups.png
  10. Although not a supported architecture if a user installs the Enterprise Central and Enterprise Server on the same PC with default settings the ports will conflict.  Either remove the unsupported Enterprise Central or if for testing stop the service and set appropriate usable ports.
    EC and ES Installed with Defaul Settings.png

 

 

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (7)
  • Find more articles tagged with:
  • 16547
  • ampersand
  • blue
  • DavidChild19
  • HernanUruena23
  • HernanUruena24
  • triangle
Was this article helpful? Yes No
75% helpful (6/8)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now