Unable to add an Automation Server underneath an Enterprise Server
  • Unable to add an Automation Server underneath an Enterprise Server
  • RobertAndriolo
    RobertAndriolo
  • Hernan_Urueña
    Hernan_Urueña
  • Benji
    Benji
  • Cody_Failinger
    Cody_Failinger
‎2018-09-06 12:09 PM
Last Updated: Administrator CraigEl Administrator ‎2025-04-09 08:22 PM
One of the following error messages are displayed.
Internal server error
Server already part of a system
  • Building Operation WorkStation
  • Building Operation Server
  1. Version Mismatch: The Automation Server is either not the same version as the Enterprise Server or it is still connected to a different Enterprise Server. If the Automation Server is still connected to another Enterprise Server then it must be detached before it can be added underneath a new Enterprise Server.
  2. User Permissions: In some instances, the User Permissions "System Address" is not added to the user account that is attempting to add the server.
If you are given an error that states "Domain: Internal Server Error" then you need to download the same version of firmware to the AS that is installed on the ES.
Resolution #1: Detach the Automation Server
  1. Log in to the Automation Server.
  2. In the system tree pane, right-click on the automation server and go to Advanced > Detach server.
  3. The Disconnect Automation Server window will open; click yes.
  4. The Automation Server is now detached and can be added to an Enterprise Server.
Resolution #2: Verify User Permissions
  1. Check a current backup using the SBO xbk Analyzer and verify the number of servers listed under Reports>Servers
  2. Log on using the default admin account and see if these servers exist.
  3. Detach the server(s), as described above.
  4. If the secondary user still requires permission to add and see ALL servers:
    • Go to the user and select the Permissions tab
    • Ensure the ES path is selected
    • Click on the Add System button (identified with the arrow)
    • Enable all options to allow read/write, create etc.
    • Save these changes and log off and back on with this user to see the changes.
This user should now be able to add/see ALL servers.