System requirements for EcoStruxure IT Gateway software including operating system, CPU and RAM, disk space, firewall, and supported browsers
Search in
EcoStruxure IT Support
Submit a support request for additional assistance with EcoStruxure IT software.
Link copied. Please paste this link to share this article on your social media post.
Last Updated:
JLehr
2025-11-19
12:16 PM
RHEL 7 and CentOS are not supported on Gateway 1.23 and newer.
How to replace your EcoStruxure IT Gateway with a new installation
EcoStruxure IT Gateway 1.23 release notes
It is recommended that operating systems and browsers are kept up to date and patched regularly in accordance to vendor recommendations.
Windows
Linux
The required CPU and memory depends on the number of monitored devices and the protocol.
The following guidelines are based on our testing. Your actual results may vary due to differences in hardware, network, and device responsiveness.
The Gateway service (OpenJDK Platform binary) allocates up to half the total system memory for its use.
The number of SNMPv3 devices the Gateway can monitor is about 25% of what is possible with SNMPv1 and Modbus TCP.
SNMPv1 and Modbus TCP
| Size | Number of devices | Number of sensors | RAM | CPU |
|---|---|---|---|---|
| Small | 250 | 34,000 | 4GB | 4 |
| Medium | 2000 | 270,000 | 8GB | 8 |
| Large | 5000 | 540,000 | 16GB | 24 |
SNMPv3
| Size | Number of devices | Number of sensors | RAM | CPU |
|---|---|---|---|---|
| Small | 60 | 8,500 | 4GB | 4 |
| Medium | 500 | 65,000 | 8GB | 8 |
| Large | 1,200 | 130,000 | 16GB | 24 |
A maximum of 25 devices can be configured to poll at 1 minute.
When you use the small Gateway configuration to discover SNMPv3 devices, only about 10 out of the 60 SNMPv3 devices can be polled at 1 minute. More than 10 devices may cause the Gateway to become overloaded and not keep up with the configured poll rate.
See Configure 1 minute polling in EcoStruxure IT Gateway
If the combination of number of devices, poll rate, and protocol is more than the Gateway can handle, you may get a device communication alert alarm.
800MB of disk space is required for the application itself, plus additional space for a maximum of 8 days of sensor data.
Additional disk space required
| Size | Additional disk space | Total disk space |
| Small | 128MB per day | 2GB |
| Medium | 512MB per day | 5GB |
| Large | 1.1GB per day | 10GB |
If your firewall blocks the Gateway default ports, or any non-default ports you specified, you must add firewall exceptions for these ports. See Gateway default ports
A DNS server must be defined for the network that connects to EcoStruxure IT.
Make sure your Gateway can resolve us.ecostruxureit.com via DNS.
Make sure Gateway versions older than 1.10.0 can resolve us.struxureon.com via DNS.
Set the screen resolution to at least 1024 x 768.
Intelligent Network Management Card
Modbus TCP or SNMP V1 and V3 enabled
Gateway versions older than 1.15 do not allow discovery of SNMPv3 devices with the Authentication type and Encryption type set to None. See Discover devices
Connected to a TCP/IP network that the Gateway has access to
Note: Firmware update and mass configuration with APC NMC 4 (AP9644) devices are not yet supported.
Redfish server protocol support
HP Proliant with iLO 4, 5
Note: iLO 4 requires ManagerFirmwareVersion 2.55 or greater.
Dell PowerEdge with iDRAC 7, 8, 9
NetBotz support
Rack Monitor 570, 250, 750/755
The number of cameras and their surveillance settings can impact system performance.
For the best experience, the following limits are recommended:
Medium or higher Gateway configuration: A maximum of 32 cameras with default NetBotz camera settings (1920x1080 and 10fps)
Organization-wide: A maximum of 250 cameras with default NetBotz camera settings (1920x1080 and 10fps)
Camera limits are not enforced by the system.
Recommended camera limits are based on performance considerations such as resolution, frame rate, and overall data volume.
Staying within these limits helps maintain stability and responsiveness.
Exceeding the recommended camera limits may reslt in degraded performance, especially during activities like backups or when additional devices are monitored.
When you launch the EcoStruxure IT Gateway, the browser might display a message that the connection is not secure. Since the application is installed on the local machine, the security certificate used by localhost is a self signed certificate.
It is safe to add an exception to your browser for https://localhost.
See How to replace the self-signed SSL certificate in EcoStruxure IT Gateway