Gateway Device Communication Alert
Troubleshooting
How to troubleshoot and solve issues configuring the EcoStruxure IT Gateway
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
When the Gateway is unable to keep up with the polling interval for a device, a Device Communication Alert warning alarm is generated. The alarm message is <device name> is responding slowly to polling.
The Device Communication Alert alarm is generated after five consecutive polls exceed the polling interval. The alarm clears after five consecutive polls complete within the polling interval.
You can do one or more of the following:
Reduce the number of devices the Gateway is polling at 1 minute (Gateway 1.13 and newer).
Reduce the number of devices the Gateway is polling.
Add more CPU and memory to the Gateway.
Investigate network latency issues, or put the Gateway on the same local area network (LAN) as the device.