Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

How to replace the self-signed SSL certificate in EcoStruxure IT Gateway

Troubleshooting

How to troubleshoot and solve issues configuring the EcoStruxure IT Gateway

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • Gateway
  • Troubleshooting
  • How to replace the self-signed SSL certificate in EcoStruxure IT Gateway
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Gateway configuration file edit required after inc...
  • How to troubleshoot the Gateway connection to EcoS...
  • How to troubleshoot SNMP communication issues in t...
  • How to solve the cloud connectivity untrusted SSL ...
  • How to set up the Gateway proxy settings
  • How to restart the Gateway Service
  • How to replace the self-signed SSL certificate in ...
  • How to replace a device in EcoStruxure IT Gateway
  • How to disconnect or reconnect a Gateway from EcoS...
  • How to create a device walk file for EcoStruxure I...
  • How to allow a targeted read for Device Support
  • Gathering Gateway logs for troubleshooting
  • Gateway restore fails on some non-English locales
  • Gateway appliance network problems due to bad imag...
  • Gateway Device Communication Alert
  • Galaxy UPS is offline after updating the Gateway
  • Device serial numbers and unique identifiers
  • Device is offline after replacement or RMA
  • Device discover fails - SNMP is disabled by defaul...
  • Cannot discover Redfish devices in Gateway
  • Cannot discover NetBotz devices in Gateway
  • Web server port 443 is being used by another appli...
  • Troubleshooting issues connecting your Gateway to ...
  • Troubleshooting Gateway device discovery failure
  • SNMP walks, Modbus polls, and Redfish discoveries
  • NetBotz devices appear in the list of unknown devi...
  • NetBotz 4.x discovery issue when Gateway proxy set...
  • My device name didn't update in the Gateway after ...
  • My device is not responding - Gateway 1.4.0
  • Gateway configuration file edit required after inc...
  • How to troubleshoot the Gateway connection to EcoS...
  • How to troubleshoot SNMP communication issues in t...
  • How to solve the cloud connectivity untrusted SSL ...
  • How to set up the Gateway proxy settings
  • How to restart the Gateway Service
  • How to replace the self-signed SSL certificate in ...
  • How to replace a device in EcoStruxure IT Gateway
  • How to disconnect or reconnect a Gateway from EcoS...
  • How to create a device walk file for EcoStruxure I...
  • How to allow a targeted read for Device Support
  • Gathering Gateway logs for troubleshooting
  • Gateway restore fails on some non-English locales
  • Gateway appliance network problems due to bad imag...
  • Gateway Device Communication Alert
  • Galaxy UPS is offline after updating the Gateway
  • Device serial numbers and unique identifiers
  • Device is offline after replacement or RMA
  • Device discover fails - SNMP is disabled by defaul...
  • Cannot discover Redfish devices in Gateway
  • Cannot discover NetBotz devices in Gateway
  • Web server port 443 is being used by another appli...
  • Troubleshooting issues connecting your Gateway to ...
  • Troubleshooting Gateway device discovery failure
  • SNMP walks, Modbus polls, and Redfish discoveries
  • NetBotz devices appear in the list of unknown devi...
  • NetBotz 4.x discovery issue when Gateway proxy set...
  • My device name didn't update in the Gateway after ...
  • My device is not responding - Gateway 1.4.0

Related Forums

  • EcoStruxure IT Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

EcoStruxure IT Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to Troubleshooting
Start a Topic
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
20968 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to replace the self-signed SSL certificate in EcoStruxure IT Gateway

EcoStruxureIT
‎2022-07-13 05:38 AM

Last Updated: VKaipila Explorer ‎2026-09-14 02:33 AM

 

These instructions apply to EcoStruxure IT Gateway 2.0 and newer.

 

For older versions of the Gateway, the default installation directory file path is: 

C:\Program Files\EcoStruxureITGateway\<gateway_version>\gateway\conf

 

Contact support for information about Gateway versions older than 1.16.

 

IMPORTANT: An imported SSL certificate signed by a trusted certificate authority or a CA certificate imported to the keystore will not persist through an EcoStruxure IT Gateway update.

 

You must import the certificate again after you update your Gateway software.

 

The Java keytool for Gateway can be accessed in the \EcoStruxureITGateway\<gateway_version>\jre\bin\ directory.

  • For Windows it is recommended to add this location to your Environment Variables → PATH for ease of use.
  • For Linux it is recommended to create an alias for ease of use: alias keytool=/opt/EcoStruxureITGateway/<gateway_version>/jre/bin/keytool

 

Windows

 

These command examples are formatted for use in the Windows command prompt.
Using PowerShell requires using single quotes instead of the double quotes displayed below.

 

EcoStruxure IT Gateway stores the user interface SSL certificates in two Java keystore files in the \EcoStruxureITGateway\<gateway_version>\conf\keystore\ directory:

 

dcos.keystore (PrivateKeyEntry)

dcos.truststore (trustedCertEntry)

 

 

Important: Including the SAN or Subject Alternative Name extension is required if accessing the Gateway user interface via the IP address of the Gateway server.  ex. https://10.x.x.x.

In this example the Common Name (CN) and Subject Alternative Name (SAN) should be the IP address of the Gateway server.

 

Note: If your CA provided you with a .p12 file then this can be converted to a dcos.keystore by using the following command:

keytool.exe -importkeystore -srckeystore newGWcert.p12 -srcstoretype PKCS12 -alias newGWcertAlias -destkeystore dcos.keystore -deststoretype PKCS12 -destalias dcos

** Be sure to verify and change the alias to dcos

  • -alias (the current p12 alias)

  • -destalias (where you set alias to dcos)

  • -srckeystore (your CA provided .p12 example: newGWcert.p12)

 

 

Step 1: Create a new keystore for the trusted SSL certificate

 

  1. Stop the EcoStruxureITGateway-x.x.x.x service.

  2. Open File Explorer and navigate to:

    •  \EcoStruxureITGateway\<gateway_version>\conf\keystore\ 

  3. Rename the existing dcos.keystore and dcos.truststore 

    • example: dcos.keystoreDefault

  4. Open a command prompt and change the directory to C:\Program Files\EcoStruxureITGateway\<current Gateway install version>\conf\keystore (custom Gateway installs may be in a different location)

  5. Type the following command to create a new dcos.keystore:
    "C:\Program Files\EcoStruxureITGateway\<gateway_version>\jre\bin\keytool.exe" -genkeypair -alias dcos -keyalg RSA -keysize 2048 -keystore dcos.keystore -ext SAN=ip:10.x.x.x

     

  6. You will first be prompted to enter a new password for the dcos.keystore you just created.
    • Note: Write down or remember your password, you will need it in a later step. 

  7. You will then be asked to enter the following information:
    •  Note: The following values need to match values present on the certificate signing authority (CA). Some are required by the CA, and others may be optional depending on the CA configuration.
    • The first value (CN) must match the hostname or FQDN (Fully Qualified Domain Name) of the server where EcoStruxure IT Gateway is installed

      • (CN) Common Name
      • (OU) Organizational Unit
      • (O) Organization
      • (L) City or Locality
      • (ST) State or Province 
      • (C) A two letter country code
    • Example:  CN=10.x.x.x, OU=Monitoring, O=My Organization, L=Boston, ST=Massachusetts, C=US

  8. Verify that the file dcos.keystore now exists in C:\Program Files\EcoStruxureITGateway\<gateway_version>\conf\keystore\ and that the SAN or Subject Alternative Name is present.
    keytool.exe -list -v -keystore dcos.keystore

     

    An example of the file: 
    SubjectAlternativeName [
      IPAddress: 10.x.x.x
    ]
    

     

  9. Edit the application-gateway-prod.yml file; set the key-store-password to the password you created in step 6 above.
  • Note: If your password uses any special characters you will want to use single quotes in the application-gateway-prod.yml file

 

 

Step 2: Create a certificate signing request (CSR) and new SSL certificate signed by a trusted CA


Note:
The CSR generated by the Java keytool does not always honor the SAN.  If this is the case then generate the CSR using the tool provided by your CA.  Be sure to include the SAN extension and use the same values for CN, OU, O, L, ST, C as used to create the dcos.keystore.

 

  1. Open a command prompt and change the directory to C:\Program Files\EcoStruxureITGateway\<current Gateway install version>\conf\keystore and enter the following to create the newGWcert.csr in the same directory:
    "C:\Program Files\EcoStruxureITGateway\<gateway_version>\jre\bin\keytool.exe" -certreq -alias dcos -keystore dcos.keystore -file newGWcert.csr -ext SAN=ip:10.x.x.x

     

  2. Provide the certificate signing request (CSR) to your certificate signing authority (CA). This could be a CA run by your company, or it might need to be sent to a third-party Certificate Authority. You will receive a new signed certificate and the root certificate from your CA.
    • Note: You will need both the new signed certificate and root certificate for later steps.

 

 

Step 3: Import the Root certificate and Web Server SSL certificate to the EcoStruxure IT Gateway keystore

 

  1. Copy the root CA certificate (we will call this rootca.crt) and newGWcert.crt to the server where EcoStruxure IT Gateway is installed.

    • Note: Root and Web Server SSL certificates may end in .crt or .cer. If the CA issued .pem files then you will need to copy/paste from BEGIN CERTIFICATE to END CERTIFICATE into a file and save as .crt or .cer.

  2. Open a command prompt and change the directory to C:\Program Files\EcoStruxureITGateway\<gateway_version>\conf\keystore.

  3. Import the root CA certificate by typing the following command (this will create a new dcos.truststore and import the root certificate in that trust store):

    “C:\Program Files\EcoStruxureITGateway\<gateway_version>\jre\bin\keytool.exe" -importCert -trustcacerts -alias root -keyalg RSA -file rootca.crt -keystore dcos.truststore

     

  4. You will first be prompted to enter a new password for the dcos.truststore you just created.
    • Note: Write down or remember your password, you will need it in a later step. 

  5. You will be asked whether or not to trust this certificate.  Type "yes" if you trust the certificate and hit Enter.

  6. Verify that the file dcos.truststore now exists in C:\Program Files\EcoStruxureITGateway\<gateway_version>\conf\keystore\. 

  7. Edit the application-gateway-prod.yml file; set the trust-store-password to the password you created in step 4 above.
    • Note: If your password uses any special characters you will want to use single quotes in the application-gateway-prod.yml file.

  8. Import the root CA certificate into the dcos.keystore by typing the following command:
    "C:\Program Files\EcoStruxureITGateway\<gateway_version>\jre\bin\keytool.exe" -importCert -trustcacerts -alias root -file rootca.crt -keystore dcos.keystore​

     

  9. Import the Web Server SSL certificate to the dcos.keystore by typing the following command:
     "C:\Program Files\EcoStruxureITGateway\<gateway_version>\jre\bin\keytool.exe" -importCert -trustcacerts -alias dcos -file newGWcert.crt -keystore dcos.keystore​

     

  10. Make sure the CA root certificate and intermediate certificate (if applicable) is imported to local Trusted Root Certification Authorities on all computers that will be used to access the Gateway user interface.

    • Right-click on CA root certificate

    • Select Install Certificate

    • Choose Windows Local Computer

    • Select Place all certificates in the following store > Browse

    • Choose Trusted Root Certification Authorities

  11. Start the EcoStruxureITGateway-x.x.x.x service.

    • EcoStruxure IT Gateway will now use the new signed certificate. No SSL Certificate security warning will be displayed by the browser when the Gateway user interface is launched.
    • Note: If you are still seeing 'Not Secure' in your web browser try clearing your cookies, closing your browser and re-open.

 

 

Linux

 

EcoStruxure IT Gateway stores the user interface SSL certificates in two Java keystore files in the /opt/EcoStruxureITGateway/<gateway_version>/conf/keystore directory:

 

dcos.keystore (PrivateKeyEntry)

dcos.truststore (trustedCertEntry)

 

Note: All commands must be run as root or sudo

 

 

Important: Including the SAN or Subject Alternative Name extension is required if accessing the Gateway user interface via the IP address of the Gateway server.  ex. https://10.x.x.x

In this example the Common Name (CN) and Subject Alternative Name (SAN) should be the IP address of the Gateway server.

 

Note: If your CA provided you with a .p12 file then this can be converted to a dcos.keystore by using the following command:

keytool -importkeystore -srckeystore newGWcert.p12 -srcstoretype PKCS12 -alias newGWcertAlias -destkeystore dcos.keystore -deststoretype PKCS12 -destalias dcos

** Be sure to verify and change the alias to dcos

  • -alias (the current p12 alias)

  • -destalias (where you set alias to dcos)

  • -srckeystore (your CA provided .p12 example: newGWcert.p12)

 

Step 1: Create a new keystore for the trusted SSL certificate

 

  1. SSH into the Linux server and stop the EcoStruxureITGateway-x.x.x.x service.
    sudo systemctl stop EcoStruxureITGateway-x.x.x.x.service​
     
  2.  Change directory to the following:
    •  /opt/EcoStruxureITGateway/<gateway_version>/conf/keystore

  3. Rename the existing dcos.keystore and dcos.truststore 
    • example: dcos.keystoreDefault

  4. From the same directory type the following command:
    sudo '/opt/EcoStruxureITGateway/<current Gateway install version>/jre/bin/keytool' -genkeypair -alias dcos -keyalg RSA -keysize 2048 -keystore dcos.keystore -ext SAN=ip:10.x.x.x

     

  5. You will first be prompted to enter a new password for the dcos.keystore you just created.
    • Note: Write down or remember your password, you will need it in a later step. 

  6. You will then be asked to enter the following information:
    • Note: The following values may need to match values present on the certificate signing authority (CA). Some are required by the CA, and others may be optional depending on the CA configuration.
    • The first value (CN) must match the hostname or FQDN (Fully Qualified Domain Name) of the server where EcoStruxure IT Gateway is installed 
      • (CN) Common Name
      • (OU) Organizational Unit
      • (O) Organization
      • (L) City or Locality
      • (ST) State or Province 
      • (C) A two letter country code
    • Example:  CN=10.x.x.x, OU=Monitoring, O=My Organization, L=Boston, ST=Massachusetts, C=US

  7. Verify that the file dcos.keystore now exists in /opt/EcoStruxureITGateway/<gateway_version>/conf/keystore/

  8. Edit the application-gateway-prod.yml file; set the key-store-password to the password you created in step 6 above.
    • Note: If your password uses any special characters you will want to use single quotes in the application-gateway-prod.yml file

 

 

Step 2: Create a certificate signing request (CSR) and new SSL certificate signed by a trusted CA

 

  1. SSH into the Linux server and change the directory to /opt/EcoStruxureITGateway/<gateway_version>/conf/keystore and enter the following to create the newGWcert.csr in the same directory:
    sudo '/opt/EcoStruxureITGateway/<gateway_version>/jre/bin/keytool' -certreq -alias dcos -keystore dcos.keystore -file newGWcert.csr -ext SAN=ip:10.x.x.x​

     

  2. Provide the certificate signing request (CSR) to your certificate signing authority (CA). This could be a CA run by your company, or it might need to be sent to a third-party Certificate Authority. You will receive a new signed certificate and the root certificate from your CA.
    • Note: You will need both the new signed certificate and root certificate for later steps.

 

Step 3: Import the Root certificate and Web Server SSL certificate to the EcoStruxure IT Gateway keystore

 

  1. Copy the root CA certificate (we will call this rootca.crt) and newGWcert.crt to the server where EcoStruxure IT Gateway is installed.
    • Note: Root and Web Server SSL certificates may end in .crt or .cer.  If the CA issued .pem files then you will need to copy/paste from BEGIN CERTIFICATE to END CERTIFICATE into a file and save as .crt or .cer.

  2. SSH into the Linux server and change directory to /opt/EcoStruxureITGateway/<gateway_version>/conf/keystore.

  3. Import the root CA certificate by typing the following command (this will create a new dcos.truststore and import the root certificate in that trust store):
    sudo '/opt/EcoStruxureITGateway/<gateway_version>/jre/bin/keytool' -importCert -trustcacerts -alias root -keyalg RSA -file rootca.crt -keystore dcos.truststore​

     

  4. You will first be prompted to enter a new password for the dcos.truststore you just created.
    • Note: Write down or remember your password, you will need it in a later step. 

  5. You will be asked whether or not to trust this certificate. Type yes if you trust the certificate and hit Enter.

  6. Verify that the file dcos.truststore now exists in /opt/EcoStruxureITGateway/<gateway_version>/conf/keystore.

  7. Edit the application-gateway-prod.yml file; set the trust-store-password to the password you created in step 4 above.
    • Note: If your password uses any special characters you will want to use single quotes in the application-gateway-prod.yml file.

  8. Import the root CA certificate into the dcos.keystore by typing the following command:
    sudo ‘/opt/EcoStruxureITGateway/<gateway_version>/jre/bin/keytool’ -importCert -trustcacerts -alias intermediate -file intermediateca.crt -keystore dcos.keystore​

    IMPORTANT: Repeat this step for the intermediate certificate using -alias intermediate if your CA provided one.

  9. Import the Web Server SSL certificate to the dcos.keystore by typing the following command:
    sudo ‘/opt/EcoStruxureITGateway/<gateway_version>/jre/bin/keytool’ -importCert -trustcacerts -alias root -file rootca.crt -keystore dcos.keystore​

     

  10. Make sure the root CA certificate is imported to the internet browser on all the computers/browsers that will be used to access the Gateway user interface.


    Mac Local Computer:

    • Open Keychain Access

    • Select System

    • Go to the top menu and click File > Import Items

    • Choose your CA root certificate file (.cer, .crt, or .pem) and click Open

    • Enter your Mac user password to allow the change

    • Double click on CA root certificate

    • Click the dropdown next to Trust

    • Change When using this certificate to Always Trust

    • Enter your Mac user password again to allow the change

  11. Start the EcoStruxureITGateway-x.x.x.x service.
    sudo systemctl start  EcoStruxureITGateway-x.x.x.x.service​
     
    • EcoStruxure IT Gateway will now use the new signed certificate. No SSL Certificate security warning will be displayed by the browser when the Gateway user interface is launched.

 

 

Was this article helpful? Yes No
0% helpful (0/2)

Link copied. Please paste this link to share this article on your social media post.

Comments
JMollica
JMollica Explorer
Explorer
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2024-04-17 06:26 AM

Hello,

I would recommend under the Create a new keystore for the trusted SSL certificate for Step 4 to add argument '-validity 365' or any number, to set the number of days the certificate will be valid for, otherwise the default will be 3 months' time.

ex: 

'/opt/EcoStruxureITGateway/<current Gateway install version>/jre/bin/keytool' -genkey -alias dcos -keyalg RSA -keystore dcos.keystore -keysize 2048 -validity 365

 

HWeser
HWeser
Explorer
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2025-05-23 06:43 AM

Hello,

I'm struggeliung now with this instruction to setup a EcoStruxure IT Gateway for almost a week. But got is solved. Could you please review on the points below and advise?

 

  1. The instruction always is refering to 2 keystore files (the "dcos.keystore" and "dcos.truststore"). No explaination why the RootCA should be loaded into a file "root.truststore". If you follow this instruction, the dialog ask you to create a container password. To allow the application to access the container, its password and filename need to get added to the "application-installer.yaml" file, same as the entries for the other 2 containers.
  2. The instruction does not advise how to install intermediate certificates if your CA requires to do so. If you skip this step, you cant add the server certificate itself getting an error in "keytool error: java.lang.Exception: Failed to establish chain from reply".

My findings in short:

 

  1. verify Java keystore content
  2. stop Gateway service
  3. stop Gateway database service
  4. delete the dcos.keystore AND the dcos.truststore
  5. generate a new dcos.keystore and provide the requested information as necessary. The values entered will be issued for the CSR with next step:
    1. CN - FQDN of the server
    2. OU - e.g. company name
    3. O - e.g. department name
    4. S - state
    5. C - country
    6. confirm the summary with "yes" or "no" to walk thru steps again.
  6. Create CSR file and handover to your CA.
  7. Your CA may provide you ideally with indidividual CRT files. If you receive PEM - that file can be opened with a plain texteditor and each section starting with "----BEGIN CERTIFICATE----" and ending with "----END CERTIFICATE----" can be saved in separate files. Usually the first section is the server cert, the second section an Intermediate and the last section the root certificate. Then rename files extension into CRT and check the content.
  8. Upload the certificates provided by your CA to server.
  9. Load the RootCA.CRT to your dcos.truststore and use alias "root". Because you deleted the dcos.truststore in step 3 you will be prompted to set a password. Check the password value in file "application-installer.yaml" and use same there.
  10. If your CA requires an intermediate certificate to install, load the Intermediate.CRT to your dcos.truststore and use alias "intermediate". If your CA didn't provide, goto next step.
  11. Load the Server.CRT into your dcos.keystore and use alias "dcos". (Here I couldn't get further with the following error message:

keytool error: java.lang.Exception: Failed to establish chain from reply

 

Solution to establish the chain:

  1. Load the provided RootCA.crt into the "dcos.keystore" and use alias "root".
  2. Load the provided Intermediate.crt into the "dcos.keystore" and use alias "intermediate".
  3. Load the provided Server.crt into the "dcos.keystore" and use alias "dcos". You shouldn't get an error anymore.
  4. Verify the content of "dcos.keystore". There should be now 3 entries separated with double lines of stars "*********" :
    1. PrivateKeyEntry with key and 3 certificates ending section with separators ********
    2. TrustedCertEntry "root" ending section with separators *********
    3. TrustedCertEntry "intermediate" ending section with separators *********
  5. Now you need to remove the TrustedCertEntries 2+3 from keystore by using command "keytool.exe -delete -alias root -keystore dcos.keystore" and "keytool.exe -delete -alias intermediate -keystore dcos.keystore".
    (Note: This step was required otherwise the webserver is still seen with a certificate not verified issuer.)
  6. One more time verify the content of "dcos.keystore". There should now only 1 PrivateKeyEntry with Key and 3 subrecords with certificates.
  7. start Gateway database service
  8. start Gateway service

 

Many thanks and happy about a response

wavecomas
wavecomas
Explorer
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2025-06-21 01:31 AM

 

All this is useless.

After gateway update our certs are replaced with self signed certs agan!!!!!

jchiglo
jchiglo
Explorer
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2025-06-26 09:02 AM

Our development team notices the same exact problem as what wavecoma's comment says. The linux procedure needs to be reviewed to reflect any new changes to the directory when there's a new gateway version. 

IMDEASoftware
IMDEASoftware
Explorer
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2025-09-02 07:42 AM

The certificate generated will not be trusted without a "Subject Alternate Name". For that you need to add one when generating the CSR (change fqdn.hostname and put your gateway IP instead of 10.1.2.3):

 

/opt/EcoStruxureITGateway/2.0.1.3/jre/bin/keytool -certreq -alias dcos -ext san=dns:fqdn.hostname,ip:10.1.2.3 -keystore dcos.keystore -file newGWcert.csr

wavecomas
wavecomas
Explorer
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2025-12-02 02:17 AM

How many years we need to wait our time  for repeating pocedures after each gateway upgrade when all previous certs are gone ?? SHAME!!

HWeser
HWeser
Explorer
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2026-10-13 07:54 AM

Hello

 

I just installed the new 2.3.0.10 and confirm the updated instructions for SSL certificate replacement much better now. Many thanks ... 

 

3 suggestions:

  • Consider (optional) to install an intermediate certificate if your CA require it. It needs to be installed in keystore between steps 8 and 9 to establish the secure chain.
  • Our company security scanners claim few days after release 10 vulnerabilities related to SSL crypto implementation and Python version. Probably the RSA is not best choice to secure the keystores?
    • Can we have a modern crypto algorithm curve to use like ed25519 for keystores encryption?
    • Any instructions/ideas how to update parts of the gateway?
  • What about the update procedure which currently require to re-run the certificate excercise?
    • For my knowledge the keystore is static as long you dont update the certificates or keystore password. Can we not just backup and restore the keystores folder after update?

Greetings and happy computing

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore