Hi,
Is it possible to modify a specific aspect of a meter framework using ION setup and then apply that change to the meter without wiping the meter configuration?
Or can this only be done with Designer?
Many thanks,
Gavin
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello @Gavin_Bryson ,
Is it possible to configure specific aspects of a framework using ION Setup - Yes, Advanced configuration.
Is it possible to save just a small section of a framework (framelet) in ION Setup - No.
It is possible to have a framelet from Designer and use ION Setup to paste onto meter - Yes. The framelet is considered a lock paste, existing modules on the will be overwritten from framelet.
Regards,
Charles
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
I believe only Designer - @Anonymous user to confirm if there are any exceptions.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello @Gavin_Bryson ,
Is it possible to configure specific aspects of a framework using ION Setup - Yes, Advanced configuration.
Is it possible to save just a small section of a framework (framelet) in ION Setup - No.
It is possible to have a framelet from Designer and use ION Setup to paste onto meter - Yes. The framelet is considered a lock paste, existing modules on the will be overwritten from framelet.
Regards,
Charles
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.