We have a client that wants to use the TLL option from an ION8650 meter. using:
The client has configured the meter using the attached guide but they wonder why the load profile is stopped when the TLC is ON (Attached picture).
After this, please we ask for your support:
1. IS the client configuring the TLC correctly?
2. How to see the data that is configured in the TLC?
Thanks in advance.
https://app.box.com/s/3gpia0v44jl7d1zibtg0wtyyb5em28iq
Link copied. Please paste this link to share this article on your social media post.
Hello @mauricio_rojas_ ,
A few points, KVA rated = 0? I believe there is a calculation somewhere in the TLL calculations that takes a square root of (X-Y) if X < Y, then result is a complex number that will return N/A from Arithmetic module. This N/A will propagate until the data recorder.
To troubleshoot with newer version of ION Setup with advanced configuration, this you can start at the Data Recorder module, if you right click the input you can get a popup ("Go to X") to navigate to the module where input is coming from. This will take you to the output of the module in question, from here you can go to the input of the upstream module and repeat until you find the source of the N/A.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @mauricio_rojas_ ,
A few points, KVA rated = 0? I believe there is a calculation somewhere in the TLL calculations that takes a square root of (X-Y) if X < Y, then result is a complex number that will return N/A from Arithmetic module. This N/A will propagate until the data recorder.
To troubleshoot with newer version of ION Setup with advanced configuration, this you can start at the Data Recorder module, if you right click the input you can get a popup ("Go to X") to navigate to the module where input is coming from. This will take you to the output of the module in question, from here you can go to the input of the upstream module and repeat until you find the source of the N/A.
Regards,
Charles