Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PM5350 Modbus register 2034? "CT Location for 1 or 2 CT Metering" ?

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM5350 Modbus register 2034? "CT Location for 1 or 2 CT Metering" ?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-04-22 03:13 PM . Last Modified: ‎2024-01-30 04:44 AM

1 Like
2
2509
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-04-22 03:13 PM

PM5350 Modbus register 2034? "CT Location for 1 or 2 CT Metering" ?

Hi,

 

An old PM5350 has been setup 3ph, 4w, Wye Grounded, 3CT,VT Direct Connect. The Modbus register 2034 has been modified from default (1) to (2). After investigation (CT ratio OK), I suspect that this register give us wrong a reading.  

 

I cannot find any documentation anywhere else than in the register list : 2034 Modbus register  "CT Location for 1 or 2 CT Metering".

 

How to write on this register ? it seems like there is no access either from ION setup or the front panel...

How much this register affects the current/power/energy calculation of the meter ?

 

Thanks for your help,

Olivier

 

Description   Register Units Size
(INT16)
Data Type Access Range Default NV User Notes
CT Location for 1  or 2 CT Metering   2034 --- 1 INT16U RWC 1 – 3 1 Y If 1 CT, value is meter terminal connected
If 2 CT, value is meter terminal not connected
1 = Phase A, 2 = Phase B, 3 = Phase C
Labels
  • Labels:
  • PM5000
Tags (2)
  • Tags:
  • english
  • Modbus Register 2034 CT location
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2021-04-27 04:10 AM

1 Like
0
2483
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-04-27 04:10 AM

Hi Olivier, 

 

This register 2034 is used only in the 1 CT or 2 CT configurations.
When we select the number of CTs connected as 1 then here we need to specify in which location that CT is connected.
​When we select the number of CTs connected is 2 then here we need to specify in which location the CT is not connected and kept open.
Also these values will not be considered in 3P4W or 3P3W configuration where we have 3 CTs are connected.

 

Regards, 

Ramasamy N

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 2
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2021-04-26 11:20 AM

0 Likes
0
2494
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-04-26 11:20 AM

@Ramasamy_N any ideas to this question?

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2021-04-27 04:10 AM

1 Like
0
2483
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-04-27 04:10 AM

Hi Olivier, 

 

This register 2034 is used only in the 1 CT or 2 CT configurations.
When we select the number of CTs connected as 1 then here we need to specify in which location that CT is connected.
​When we select the number of CTs connected is 2 then here we need to specify in which location the CT is not connected and kept open.
Also these values will not be considered in 3P4W or 3P3W configuration where we have 3 CTs are connected.

 

Regards, 

Ramasamy N

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore