PM5350 Modbus register 2034? "CT Location for 1 or 2 CT Metering" ?

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
Olivier-Quasar
Cadet | EcoXpert Master
Cadet | EcoXpert Master

PM5350 Modbus register 2034? "CT Location for 1 or 2 CT Metering" ?

Hi,

 

An old PM5350 has been setup 3ph, 4w, Wye Grounded, 3CT,VT Direct Connect. The Modbus register 2034 has been modified from default (1) to (2). After investigation (CT ratio OK), I suspect that this register give us wrong a reading.  

 

I cannot find any documentation anywhere else than in the register list : 2034 Modbus register  "CT Location for 1 or 2 CT Metering".

 

How to write on this register ? it seems like there is no access either from ION setup or the front panel...

How much this register affects the current/power/energy calculation of the meter ?

 

Thanks for your help,

Olivier

 

Description RegisterUnitsSize
(INT16)
Data TypeAccessRangeDefaultNVUser Notes
CT Location for 1  or 2 CT Metering 2034---1INT16URWC1 – 31YIf 1 CT, value is meter terminal connected
If 2 CT, value is meter terminal not connected
1 = Phase A, 2 = Phase B, 3 = Phase C

Accepted Solutions
Ramasamy_N
Commander Commander
Commander

Re: PM5350 Modbus register 2034? "CT Location for 1 or 2 CT Metering" ?

Hi Olivier, 

 

This register 2034 is used only in the 1 CT or 2 CT configurations.
When we select the number of CTs connected as 1 then here we need to specify in which location that CT is connected.
​When we select the number of CTs connected is 2 then here we need to specify in which location the CT is not connected and kept open.
Also these values will not be considered in 3P4W or 3P3W configuration where we have 3 CTs are connected.

 

Regards, 

Ramasamy N

See Answer In Context

Tags (1)
2 Replies 2
Charles_Murison
Picard Picard
Picard
0 Likes
0
692

Re: PM5350 Modbus register 2034? "CT Location for 1 or 2 CT Metering" ?

@Ramasamy_N any ideas to this question?

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
Ramasamy_N
Commander Commander
Commander

Re: PM5350 Modbus register 2034? "CT Location for 1 or 2 CT Metering" ?

Hi Olivier, 

 

This register 2034 is used only in the 1 CT or 2 CT configurations.
When we select the number of CTs connected as 1 then here we need to specify in which location that CT is connected.
​When we select the number of CTs connected is 2 then here we need to specify in which location the CT is not connected and kept open.
Also these values will not be considered in 3P4W or 3P3W configuration where we have 3 CTs are connected.

 

Regards, 

Ramasamy N

Tags (1)