I am trying to configure the ION meter for Modbus communication. From the below video, I can see how to configure an addition register for specific data.
https://www.youtube.com/watch?v=HxIzrVXS6T0
However, I am wondering how to configure a data buffer for Modbus polling? Like how PME interacts with meters having internal memory, even if the communication between the server and meters is down for a certain time, the data will be backfilled to the PME once the communication is back. How do we achieve this function in ION meter Modbus communication? Thank
Hello @SESA648446 ,
Sounds like you are talking about the onboard logs being read by Modbus. Sadly this is not possible on ION9000 or PM8000 meters. ION protocol is required to get logs.
Regards,
Charles
Hello @SESA648446 ,
Sounds like you are talking about the onboard logs being read by Modbus. Sadly this is not possible on ION9000 or PM8000 meters. ION protocol is required to get logs.