ABOUT THE PM8000 DELIVERED ENERGY VALUE

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
AYSEGUL
Ensign Ensign
Ensign
0 Likes
5
993

ABOUT THE PM8000 DELIVERED ENERGY VALUE

Dears hello ,

Energy Delivered parameters like kWh on PM8000 is return 0 after 9999 kWH value.

Is it normal? I have searched the user manual , but there is no any limitation. Can he see the delivered energy value bigger than 9999?

 

Thanks for your help.

 

Best Regards,

Ayşegül

 

Tags (1)

Accepted Solutions
N4th4n13L
Ensign Ensign
Ensign

Re: ABOUT THE PM8000 DELIVERED ENERGY VALUE

Hi Ayşegül,

 

I don't believe there's a way to edit the rollover value through the front panel display, or through the web server. You can issue resets through the display though.

 

ION Setup is a free software that can be downloaded from here; https://www.se.com/us/en/product-range-presentation/61461-ion-setup-3.0/ 

 

Regards,

Nathaniel Dunn

See Answer In Context

Tags (1)
5 Replies 5
N4th4n13L
Ensign Ensign
Ensign
0 Likes
4
974

Re: ABOUT THE PM8000 DELIVERED ENERGY VALUE

Hello Ayşegül,

 

Yes, it can be set for a value higher than 9,999 kWhs.

 

The rollover value is adjustable, and can be found in the Setup Assistant under the Metering Setup Assistant and Rollover tab for the FAC 2.2 template. 

 

These registers can be found in the integrator modules under setup registers tab if navigating using the advanced mode of ION Setup. It is recommended to use a maximum rollover value of 10,000,000. Which equates to a maximum value of 9,999,999.

 

Regards,

Nathaniel Dunn

Tags (1)
AYSEGUL
Ensign Ensign
Ensign
0 Likes
1
972

Re: ABOUT THE PM8000 DELIVERED ENERGY VALUE

Dear Nathaniel 

 

Thank you so much for your answer.

Can we make retated setting on display without using ION setup?

Where can I reach the related settings on display?

 

B&R

Ayşegül

 

Tags (1)
N4th4n13L
Ensign Ensign
Ensign

Re: ABOUT THE PM8000 DELIVERED ENERGY VALUE

Hi Ayşegül,

 

I don't believe there's a way to edit the rollover value through the front panel display, or through the web server. You can issue resets through the display though.

 

ION Setup is a free software that can be downloaded from here; https://www.se.com/us/en/product-range-presentation/61461-ion-setup-3.0/ 

 

Regards,

Nathaniel Dunn

Tags (1)
DanL
Commander Commander
Commander

Re: ABOUT THE PM8000 DELIVERED ENERGY VALUE

@AYSEGUL The default configuration for the PM8000 energy roll-over is 10 million kWh (10 000 000 kWh), and NOT 10 000 kWh.

 

  1. Did you make custom configuration changes or load a custom configuration template?
    If you do need to change the default energy rollover values, do NOT use "advanced mode of ION Setup" for this. Instead, use ION Setup's "Setup Assistant" wizard: "Metering Setup" | "Rollover" to configure all the integrator rollover setup configurations at once

  2. How are you performing the register reads to observe "return 0 after 9999 kWH value" - is it with ION protocol, Modbus, DNP, IEC61850, integrated or remote display, web pages, email, other? If you have not customized the PM8000 configuration, most likely the behavior you see is a result of software and/or protocol configuration.
Tags (1)
AYSEGUL
Ensign Ensign
Ensign
0 Likes
0
955

Re: ABOUT THE PM8000 DELIVERED ENERGY VALUE

Thank you so much for your answer. 

That is clear.