ION9000 sag/swell module data

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION9000 sag/swell module data
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Stuart_Cheng
Lt. Commander Stuart_Cheng Lt. Commander
Lt. Commander

Posted: ‎2024-11-07 06:53 AM . Last Modified: ‎2024-11-07 06:57 AM

0 Likes
6
775
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-07 06:53 AM

ION9000 sag/swell module data

Hi All,

 

I am using ION9000 to capture voltage sag/swell. I configured the threshold to +/- 10% and linked the data to IEC61850 module for communication.

Stuart_Cheng_0-1730990226369.jpeg

  • I noticed something unusual: during a voltage sag, the DistVmin was recorded at only 90.61%, which is within the acceptable limit and should not have triggered the capture (please note that the value shown below is raw data minus 100% for easier understanding by the end-user). However, I also checked the ION9000 webpage and found that the voltage depth is 90%. I am curious about why the data is inconsistent?

Stuart_Cheng_1-1730990354245.png

 

Stuart_Cheng_2-1730990366873.png

 

Stuart_Cheng_4-1730990396426.png

  • Another question from the same customer site, wondering why the DistVMax 89.83% was smaller than DistVMin 90.59, which also seems unusual according to the definition since DistVmin represents the minimum magnitude during the disturbance.

Stuart_Cheng_5-1730990419893.png

 

Stuart_Cheng_6-1730990611667.png

 

Appreciate it if anyone can provide any insight. Thanks

Labels
  • Labels:
  • ION9000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2024-11-12 01:03 PM

0 Likes
0
631
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-12 01:03 PM

Hello @Stuart_Cheng ,

If you are using a dead band setting in IEC61850, then that could explain the behavior observed. Glad to see that the meter is reporting the sag data correctly in the logged data. Chances are you will want to have the IEC61850 report on any value change since the inputs are only updated at the end o each event.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 6
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2024-11-07 08:59 AM

0 Likes
0
749
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-07 08:59 AM

Hello @Stuart_Cheng ,

 

Are you able to connect to the meter with ION Setup?  Are you able to download the Sag/swell logs?
The web page will do some queries to the logs and some calculations, it is possible that the calculations are rounding or some other consideration.

 

With regards to the IEC61850, would need to understand what you have setup. If you are linking the outputs of the Sag/swell module directly to input of IEC61850 module and then taking a reading from those values, you might be showing the deltas between sag events and not the actual measured amount for the sag. 

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Stuart_Cheng
Lt. Commander Stuart_Cheng Lt. Commander
Lt. Commander

Posted: ‎2024-11-07 07:02 PM . Last Modified: ‎2024-11-07 07:04 PM

0 Likes
1
732
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-07 07:02 PM

Hi @Charles_Murison 

 

Thanks for the reply. Do you mean the sag/swell data recorded in the data recorder? I will request my customer to provide it for analysis

 

Stuart_Cheng_0-1731034858204.png

 

 

Regarding communication, I connect the output register of the sag/swell module directly to the input of IEC61850 module without any further calculations. However, I am not entirely clear about the "deltas between sag events" you mentioned. Why using the IEC61850 module to collect data from the sag/swell module does not reflect the actual measured values? Does this mean that the data may vary depending on the communication protocols used, for example, ION versus IEC61850?

 

Also wondering if you have any idea about my second question. The DistVMax value is 89.83%, which is lower than the DistVMin value of 90.59%. This seems unusual based on definitions. DistVMin represents the minimum magnitude during the disturbance and should in theory be smaller than DistVMax?

 

Appreciate it if you could help elaborate more on these questions. Thank you

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2024-11-08 08:31 AM

0 Likes
0
708
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-08 08:31 AM

Hello @Stuart_Cheng ,

 

Yes the data recorder you are showing is exactly the data I am hoping to get. Hopefully with that data I can understand what is happening with DistVMax and DistVMin. The values in your screenshot from IEC61850 are negative values, I missed the statement that values were (reading - 100). The Sag/Swell module cannot give negative values so I had assumed that values were a delta between the current and previous reading. 

The data does not change depending on the protocol used to read the data (possibly some rounding/truncating occasionally).

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Stuart_Cheng
Lt. Commander Stuart_Cheng Lt. Commander
Lt. Commander

Posted: ‎2024-11-09 01:46 AM

0 Likes
1
681
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-09 01:46 AM

Hi @Charles_Murison 

 

I have attached the raw data for your reference. Upon comparison, I've noted that DistV2Max is the only value that differs (10.16 vs. 9.39). Interestingly, 9.39 corresponds exactly to the DistV2Max from the last disturbance on October 31, 2024. I am thinking whether it could be related to the deadband setting of the IEC61850 module, which may have caused the DistV2Max value to retain the previous reading?

 

From ION Setup

Stuart_Cheng_0-1731145285558.png

 

From Customer’s SCADA

Stuart_Cheng_1-1731145285562.png 

 

If the issue is related to the deadband, what adjustments do you suggest? Can I directly change the value in the CID file to modify the deadband? Thank you.

 

Stuart_Cheng_2-1731145301787.png

Attachments
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2024-11-12 01:03 PM

0 Likes
0
632
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-12 01:03 PM

Hello @Stuart_Cheng ,

If you are using a dead band setting in IEC61850, then that could explain the behavior observed. Glad to see that the meter is reporting the sag data correctly in the logged data. Chances are you will want to have the IEC61850 report on any value change since the inputs are only updated at the end o each event.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Stuart_Cheng
Lt. Commander Stuart_Cheng Lt. Commander
Lt. Commander

Posted: ‎2024-11-12 05:07 PM

0 Likes
0
621
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-12 05:07 PM

Thanks @Charles_Murison!

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of