ABOUT THE PM8000 DELIVERED ENERGY VALUE

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ABOUT THE PM8000 DELIVERED ENERGY VALUE
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Anonymous user
Not applicable

Posted: ‎2021-02-28 11:38 PM

0 Likes
9
2827
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-02-28 11:38 PM

ABOUT THE PM8000 DELIVERED ENERGY VALUE

Dears hello ,

Energy Delivered parameters like kWh on PM8000 is return 0 after 9999 kWH value.

Is it normal? I have searched the user manual , but there is no any limitation. Can he see the delivered energy value bigger than 9999?

 

Thanks for your help.

 

Best Regards,

Ayşegül

 

Labels
  • Labels:
  • PM8000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
N4th4n13L
Lieutenant JG N4th4n13L Lieutenant JG
Lieutenant JG

Posted: ‎2021-03-01 06:09 AM

1 Like
0
2804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-03-01 06:09 AM

Hi Ayşegül,

 

I don't believe there's a way to edit the rollover value through the front panel display, or through the web server. You can issue resets through the display though.

 

ION Setup is a free software that can be downloaded from here; https://www.se.com/us/en/product-range-presentation/61461-ion-setup-3.0/ 

 

Regards,

Nathaniel Dunn

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 9
N4th4n13L
Lieutenant JG N4th4n13L Lieutenant JG
Lieutenant JG

Posted: ‎2021-03-01 05:51 AM

0 Likes
4
2808
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-03-01 05:51 AM

Hello Ayşegül,

 

Yes, it can be set for a value higher than 9,999 kWhs.

 

The rollover value is adjustable, and can be found in the Setup Assistant under the Metering Setup Assistant and Rollover tab for the FAC 2.2 template. 

 

These registers can be found in the integrator modules under setup registers tab if navigating using the advanced mode of ION Setup. It is recommended to use a maximum rollover value of 10,000,000. Which equates to a maximum value of 9,999,999.

 

Regards,

Nathaniel Dunn

  • Thumbnail of PowerLogic ION7400 series
    PowerLogic
    PowerLogic ION7400 series
  • Thumbnail of PowerLogic ION8650 series
    PowerLogic
    PowerLogic ION8650 series
  • Thumbnail of PowerLogic ION9000
    Schneider Electric
    PowerLogic ION9000
View products (3)
Tags (1)
  • Tags:
  • english
Reply
Anonymous user
Not applicable

Posted: ‎2021-03-01 05:56 AM

0 Likes
1
2806
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-03-01 05:56 AM

Dear Nathaniel 

 

Thank you so much for your answer.

Can we make retated setting on display without using ION setup?

Where can I reach the related settings on display?

 

B&R

Ayşegül

 

Tags (1)
  • Tags:
  • english
Reply
N4th4n13L
Lieutenant JG N4th4n13L Lieutenant JG
Lieutenant JG

Posted: ‎2021-03-01 06:09 AM

1 Like
0
2805
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-03-01 06:09 AM

Hi Ayşegül,

 

I don't believe there's a way to edit the rollover value through the front panel display, or through the web server. You can issue resets through the display though.

 

ION Setup is a free software that can be downloaded from here; https://www.se.com/us/en/product-range-presentation/61461-ion-setup-3.0/ 

 

Regards,

Nathaniel Dunn

Tags (1)
  • Tags:
  • english
Reply
DanL
Captain DanL Captain
Captain

Posted: ‎2021-03-01 09:57 AM

2 Likes
1
2795
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-03-01 09:57 AM

@AYSEGUL The default configuration for the PM8000 energy roll-over is 10 million kWh (10 000 000 kWh), and NOT 10 000 kWh.

 

  1. Did you make custom configuration changes or load a custom configuration template?
    If you do need to change the default energy rollover values, do NOT use "advanced mode of ION Setup" for this. Instead, use ION Setup's "Setup Assistant" wizard: "Metering Setup" | "Rollover" to configure all the integrator rollover setup configurations at once

  2. How are you performing the register reads to observe "return 0 after 9999 kWH value" - is it with ION protocol, Modbus, DNP, IEC61850, integrated or remote display, web pages, email, other? If you have not customized the PM8000 configuration, most likely the behavior you see is a result of software and/or protocol configuration.
Tags (1)
  • Tags:
  • english
Reply
Anonymous user
Not applicable

Posted: ‎2021-03-02 12:28 AM

0 Likes
0
2789
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-03-02 12:28 AM

Thank you so much for your answer. 

That is clear.

Tags (1)
  • Tags:
  • english
Reply
aannas88
aannas88
Cadet

Posted: ‎2024-11-07 07:58 PM

0 Likes
1
797
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-07 07:58 PM

I have the same problem, The default rollover was 10 000 000, and I try to change to 10 000 000 000, hopefully the energy reading not reset to zero again

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2024-11-08 08:50 AM . Last Modified: ‎2024-11-08 08:51 AM

1 Like
0
767
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-08 08:50 AM

Hello @aannas88 ,

The energy values in the meter are sent over communication as 32 bit floating numbers. At the numbers get larger, the precision of the number decreases. If the customer is okay with a drop in communicated precision then they do that with informed consent. over ~16 million, the 32 format can no longer give individual kwh. See https://en.wikipedia.org/wiki/Single-precision_floating-point_format for more information.

 

Note that internal to the meter energy is calculated with 64 bit floating point numbers. Outside of the integrator module is 32 bit floating point.

 

Regards

Charles

L4 Prime for Advanced metering and Utilities
Reply
aannas88
aannas88
Cadet

Posted: ‎2024-11-08 03:46 PM

0 Likes
1
728
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-08 03:46 PM

The metering was installed for Ball Mill motor 6.5 MWH that running 24 hour/day, and suppose not to reset the energy meter. 

I will be monitoring data reading, Thanks for the advice

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2024-11-12 01:06 PM

0 Likes
0
709
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-12 01:06 PM

Hello @aannas88 ,

 

Eventually the meter will reset energy values, 6.5 MWh running 24 hours a day 7 days a week will still roll over after ~640 days. Perhaps the customer could look at having the energy roll over at specific times such as the start of each year.

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of