Video: Discover devices
Gateway software installation and setup
Step-by step instructions for how to download, install, and set up the EcoStruxure IT Gateway
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
During the initial setup of your Gateway, you specify credentials to communicate with the SNMPv1, SNMPv3, NetBotz, Redfish, or Modbus devices you want to discover. To modify these settings later, go to Settings > Device credentials.
Note: When you discover NetBotz 300, 400, and 500 devices using SNMP, they are listed as unsupported devices in the Gateway. Use the NetBotz protocol to discover these devices in the Gateway.
Your APC NMC3 devices might be configured to limit the number of failed login attempts. If the number of device file transfer credentials you provide in the Gateway exceeds the number of failed login attempts allowed on the NMC3 device, the device might be locked.
To discover devices after the initial setup of your Gateway:
Go to Discover devices.
Click Configure Credentials to select specific device file transfer credentials to use in a device discovery. Otherwise, all configured credentials will be used.
Click Manage credentials to view the credentials you have configured in the Gateway.
To comply with stricter cybersecurity requirements across various product groups, it is recommended that you review your username/password lists in EcoStruxure IT Gateway and confirm that configured credentials are both active and accurate.
Specify the IP addresses or address range of the devices, or import a device list. You cannot import a device list for serial Modbus discoveries.
idea_icon_360021184553.png Check out the on-screen device discovery tips.
Discovery results are displayed in the summary including discovered devices and unsupported devices that were not discovered. You can view details about unsupported devices, and see discovery results in the discovery log.
If you find that one or more of your devices is not supported, you can request device support.
All discovered devices are listed on the Devices page.