Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Updating EcoStruxure IT Gateway to the latest version

Gateway software installation and setup

Step-by step instructions for how to download, install, and set up the EcoStruxure IT Gateway

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • Gateway
  • Gateway software installation and setup
  • Updating EcoStruxure IT Gateway to the latest version
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Installing and setting up EcoStruxure IT Gateway
  • Video: Discover devices
  • Discovering Smart-UPS in the Gateway
  • Import a device list to discover devices in EcoStr...
  • Configuring cloud connectivity in the Gateway
  • Set up redundant EcoStruxure IT Gateways
  • Installing the EcoStruxure IT mobile app
  • Updating EcoStruxure IT Gateway to the latest vers...
  • How to replace your EcoStruxure IT Gateway with a ...
  • Video: Install EcoStruxure IT Gateway on Linux
  • Installing EcoStruxure IT Gateway on CentOS no lon...
  • EcoStruxure IT Gateway installer checksums
  • Video: How to deploy EcoStruxure IT Gateway
  • Video: Install EcoStruxure IT Gateway on Windows
  • Video: How to discover Modbus devices in the Gatew...
  • Installing and setting up EcoStruxure IT Gateway
  • Video: Discover devices
  • Discovering Smart-UPS in the Gateway
  • Import a device list to discover devices in EcoStr...
  • Configuring cloud connectivity in the Gateway
  • Set up redundant EcoStruxure IT Gateways
  • Installing the EcoStruxure IT mobile app
  • Updating EcoStruxure IT Gateway to the latest vers...
  • How to replace your EcoStruxure IT Gateway with a ...
  • Video: Install EcoStruxure IT Gateway on Linux
  • Installing EcoStruxure IT Gateway on CentOS no lon...
  • EcoStruxure IT Gateway installer checksums
  • Video: How to deploy EcoStruxure IT Gateway
  • Video: Install EcoStruxure IT Gateway on Windows
  • Video: How to discover Modbus devices in the Gatew...

Related Forums

  • EcoStruxure IT Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

EcoStruxure IT Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to Gateway software installation and setup
Start a Topic
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
19125 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Updating EcoStruxure IT Gateway to the latest version

EcoStruxureIT
‎2018-11-15 10:39 AM

Last Updated: JLehr Champion ‎2026-02-01 09:33 AM

 

The EcoStruxure IT Gateway must be at a minimum of version 1.18 to update to the latest Gateway version.

If your Gateway version is older than 1.18, contact support for assistance.

 

Installing Gateway 2.1.1 on Windows

 

In June 2025, Microsoft introduced a new certificate signing authority in Windows operating system updates. This certificate must be installed on your Windows computer to install EcoStruxure IT Gateway 2.1.1.

 

See Installing Gateway 2.1.1 on Windows requires the new Microsoft certificate 

 

 

When you update the Gateway to the latest version, the software update performs a backup that is stored in the install directory.

It is important that you have a back up before you update EcoStruxure IT Gateway. 

 

  • To manually run a Gateway backup, see Configure Gateway backup
  • Take a snapshot via VM.

 

Do not uninstall the previous version of the Gateway software.

 

Update from IT Expert

 

Gateway software update is available from IT Expert.

 

  1. Log in to IT Expert.
  2. Go to Administration > Gateways.
  3. Click the Update button on each Gateway you want to update the software on. 

 

ITE update Gateway 1.png

 

 

The Gateway software update runs in the background.

 

New Gateway versions can be installed with minimal downtime, and are deployed in parallel with the currently running instance. You can actively monitor your devices while data migration and new version deployment completes.


If there is a failure to migrate data and deploy the new version, the current Gateway install will continue to run unaffected, reporting errors to our engineering team for review.

 

If a device library update is also available, it will be presented after the Gateway software is updated. The Gateway software update is always presented first.

 

Manual update and installation

 

  1. Log in to IT Expert.
  2. Go to Administration > Gateways.
  3. Click Download Gateway software.
  4. Run the installer.

 

OR

 

Download the Gateway software for Windows or Linux here.

 

You must also manually update the device library. 

Device library updates are released frequently, independent of Gateway software releases.

See How to update the Gateway device library

 

Auto-update in IT Expert

 

You can enable automatic Gateway software updates in IT Expert. When you enable auto-update on a Gateway connected to IT Expert, you allow Schneider Electric to automatically update it when a new software version is available.

 

  1. In IT Expert, go to Administration > Gateways.
  2. Click Enable auto-update on the Gateway tile(s).

 

 

ITE enable autoupdate.png

 

You can also double click a Gateway tile and check the box to enable auto-update, or uncheck the box to disable it.

 

ITE allow autoupdate checkbox.png

 

 

About the Gateway Device Library

 

Device library updates are released frequently, independent of Gateway software releases.

 

When auto-update is enabled in IT Expert, the device library is also auto-updated if an update is available. The Gateway software is always updated first.

 

If a new version of the device library is available independent of a Gateway software release, you must manually update it in IT Expert.

See How to update the Gateway device library

 

 

Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

Comments
gcastold
gcastold
Explorer
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2024-04-29 07:58 AM

This article assumes that we are using a Windows platform on an Appliance and that we're using IT Expert.

JLehr
JLehr Champion
Champion
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2024-05-01 01:14 PM

Hi @gcastold,

 

We added a link in the Manual update and installation section of this article that leads to the Gateway download page for both Windows and Linux.

 

Thanks for helping us improve!

marek.notino
marek.notino
Explorer
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2026-03-03 01:56 AM

 

Hello,

I am experiencing an issue with updating the gateway. When I attempt to update it through IT Expert, I receive an error: One or more Gateways failed to update.

 

Additionally, when I try to perform a manual update using the installer on the server, the process gets stuck on backing up the previous version.

I am trying to update from version 1.24.0.12 to version 2.1.1.18 on Windows Server 2025.

 

Could you please advise me on how to successfully update the gateway?

 

Thank you.

JLehr
JLehr Champion
Champion
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2026-03-06 08:05 AM

Hi @marek.notino,

 

Please submit a support request for the most efficient troubleshooting and fastest resolution.

marek.notino
marek.notino
Explorer
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2026-03-25 02:51 AM

Hi @JLehr 

Request created 122493863 on 9/3/2026, and I still haven't received a response. Could you please check on it for me and provide an update? We are still unable to upgrade the gateway from version 1.24.0.12 to version 2.1.1.18.

Thank you.

JLehr
JLehr Champion
Champion
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2026-03-25 08:26 AM

Hi @marek.notino,

 

I'm sorry this happened to you. I'll do what I can to facilitate a response. 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore