Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

AMT not receiving Data

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • AMT not receiving Data
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • DavidFisher
    DavidFisher
  • Chris_Asbury
    Chris_Asbury
  • Derrick_Ratliff
    Derrick_Ratliff
  • RobertAndriolo
    RobertAndriolo
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3006 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

AMT not receiving Data

Product_Support
‎2020-11-30 08:00 AM

Last Updated: CraigEl Champion ‎2022-08-07 10:28 PM

Issue

  • AMT has stopped receiving data
  • AMT is not receiving data
  • A new link added to a system, is not sending messages or transactions

Product Line

TAC INET

Environment

I/NET

Cause

AMT can stop receiving data for several reasons.

  • Connection between Remote Client with I/O and SQL is broken
  • AMT is Paused
  • Communication to the device is not functioning
  • AMT Masking is not set correctly
  • Host Masking is not set correctly
  • Point Masking is not set correctly
  • Door Editor Masking is not Set
  • The software has frozen
  • I/NET has reached its maximum online event size and FIFO is not working (very rare)
  • Other

Resolution

Connection between Remote Client with I/O and SQL PC is broken.

  1. Check that no other I/NET PCs are connected to the SQL database. This may include an instance of I/NET installed on the SQL PC
  2. Restart the I/Net Remote Client with I/O to re-establish the connection with the SQL Server
  3. Wait several minutes for data to update.
  4. If this fails, ensure that there are no firewalls or communication failures between the 2 PCs.
  5. If using I/NET v2.42 there have been instances where this version does not pass events to the SQL Server.  This is fixed in v2.43 or greater.

AMT is paused

  1. Right-click anywhere in an open Alarm/Transaction/Message window
  2. The bottom choice is either "Pause" or "Resume"
  3. If it is "Resume" click on that and AMT function will be restored

Communication to the device is not functioning

  1. Minimize AMT and open I/NET
  2. Connect to the controller
  3. Select Summary>Controller
  4. If you see values and get no error messages this is not the issue
  5. If you cannot see values or get a "No Entries in Database" error, determine why communication is down

AMT Masking is not set correctly

  1. In AMT Select Edit>Configuration
  2. Note the current settings, take a screen shot and save it if possible
  3. For troubleshooting purposes, select all of the check boxes under "Messages/Alarm"
  4. Restart the I/O server
  5. In I/NET trigger a point to go into alarm or send a message
  6. Check AMT for successful delivery

Host Masking is not set correctly (TCP/IP only)

  1. Right-click on the I/O server and select Configure
  2. Modify the Active Profile
  3. On the bottom of the screen click on "Host Masks"
  4. Select any NPR or 527
  5. Note the current settings
  6. Check all boxes
  7. Click okay
  8. Repeat 4-7 for all NPR or 527 devices
  9. Restart the I/O server
  10. In I/NET trigger a point to go into alarm or send a message
  11. Check AMT for successful delivery

Point Masking not set correctly

  1. Connect to a controller that you expect to receive messages from
  2. Select Edit>Controller>Resident I/O
  3. Modify a point you expect to receive messages from
  4. Ensure that the appropriate Mask bits are set
  5. Ensure that there is a priority set for both Messages and Alarms
  6. Click okay
  7. Go to the controller summary and attempt to trigger a message or alarm

Door Editor Masking is not Set

  1. Connect to a controller that you expect to receive messages from
  2. Select Edit>Controller>Doors
  3. Modify a door you expect to receive messages from
  4. Ensure that the appropriate Mask bits are set
  5. Ensure that there is a priority set for both Transactions and Alarms
  6. Click okay
  7. Attempt to trigger a message or alarm

The software has frozen

  1. Restart the I/O server
  2. If this does not work restart the computer

I/NET has reached its maximum online event size and FIFO is not working (very rare)

  1. Right Click on the I/O server and select Archive Configuration
  2. Enable Archiving if it is not enabled
  3. Increase the size of the maximum online events
  4. Restart the I/O server
  5. Trigger an Alarm or Event in I/NET
  6. Verify AMT 

Other troubleshooting steps

  1. Force a Lan to reconfigure by changing the station address of the Xenta 527, then changing it back

If AMT still will not function Repeat the above processes using an Event window with no filter.  It is possible messages are being received, just not to the open Window

  1. Close all open AMT windows
  2. Select System>New>Event Window
  3. Click Okay
  4. This opens an Event Window which will display all data coming into AMT
  5. Repeat the above troubleshooting processes

The Controller LAN is having communication issues

  1. Cycle power on one of the Controllers on the Controller Lan to force a Lan Reconfigure

Other solutions for this issue have been documented in these articles:

  • No door transactions coming into AMT: Quick Poll is not enabled.  Typically applies to older sites.
  • Transactions not Updating AMT Window using direct connect: For Direct Connect systems
  • No Transactions or controller Events in AMT: Reliable Tap
  • AMT messages stop after re-installing I/NET: Applies to recently upgraded sites.
Labels (1)
Labels:
  • TAC INET
Tags (3)
  • Find more articles tagged with:
  • 4585
  • AMT not receiving Data
  • ChrisAsbury20
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore